Default NRE Memory Pool Configuration Changes In N4.10

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Default NRE Memory Pool Configuration Changes In N4.10
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1586 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Default NRE Memory Pool Configuration Changes In N4.10

Guinan RandyDavis Guinan
‎2021-04-20 10:36 AM

on ‎2021-04-20 10:36 AM

Issue

The following error occurs on startup following upgrading of Niagara Station to  4.10.

 

SEVERE [20:42:01 23-Oct-20 UTC][nreconfig] invalid nre memory configuration values, 832 > 816

 

Product Line

TAC IA Series

Environment

I/A Jace 8000 N4.10

Cause

The default NRE memory pool settings are incorrect after an N4.10 upgrade and need configuration to function correctly.

Resolution

Niagara 4.10 and Default NRE Memory Pool Changes

The increased size of some core libraries in Niagara 4.10 required changes to the default NRE Memory Pool settings for use on a JACE-8000. MetaSpace memory needed to be increased to allow applications to run without issue.

 

Note: Any previous custom memory configuration applied to the JACE-8000 will be reset upon upgrade to 4.10.

The overall size of the pool of memory available to the NRE installation has decreased.  T

As the overall size of the pool has decreased, customizations based on the old total pool size are invalid and cannot be maintained.

 

If a custom memory configuration is required, the user will need to manually adjust the platform administration menu after a device is upgraded. A longer-term approach to address this issue is in development and should be available with the Niagara 4.11 release.

 

NRE Memory pool default settings for Niagara 4.9:

Ills_1.png

Changes to the default configuration:

Heap Space size

  • 4.9 value: 384 MB
  • 4.10 value: 360 MB

Meta Space size

  • 4.9 value: 48 MB
  • 4.10 value: 56 MB

System reserve

  • 4.10: allocated additional 16MB

NRE Memory pool default settings for Niagara 4.10:

Ills_2.png

Labels (1)
Labels:
  • TAC IA Series
Tags (3)
  • Find more articles tagged with:
  • default NRE Memory Pool
  • Niagara 4.10
  • RandyDavis21
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore