Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 266
    • 267
    • 268
    • …
    • 509
  • Next »

Keep others from using local TAC Vista IV licenses

Issue How do you keep others from using my TAC Vista IV licenses? Environment Vista IV Licensing Cause Networked PCs will look for licenses outside of their local drives. On a shared engineering drive, this can cause problems. Resolution In order to have your PC set up so that it does not share its license over a network: Go to Start > Run > Type in regedit Click OK Go to HKEY_LOCAL_MACHINE > SOFTWARE > Aladdin Knowledge Systems > Privilege Licenser > Applications Click on PLServe Double click on Network Change the 1 to a 0
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1169 Views

Disable TAC Vista IV license sharing over a network

Issue Disable TAC Vista IV license sharing over a network Environment TAC Vista IV Licensing Vista Server on an open network Cause Sharing licenses across a network can be a cost effective mechanism to enable several users to use a pool of seats. However, if yours is the only license on the network, it can accidentally be "stolen" by someone else running Vista Server on the same network and you will be unable to connect, or will have to wait a long time for your PC to find an available license elsewhere on the network. Especially in an engineering setting, it is better to disable this feature. Resolution In order to have your PC set up so that it does not share its license over a network: Go to Start > Run Type in regedit, Click OK Go to HKEY_LOCAL_MACHINE > SOFTWARE > Aladdin Knowledge Systems > Privilege Licenser > Server Addresses Enter the computer name in the TCP/IP Change Broadcast to NO.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1140 Views

In Vista, alarms are not appearing in the alarm handling window.

Issue In Vista, alarms are not appearing in the alarm handling window. Environment Vista Workstation Alarm Queue Cause If the alarm is set up for a priority of Zero the alarms will not shown in Vista alarm window. Resolution If you are online in Vista, you can change the priority directly in Vista. The changes will be done in your MTA file when you export the file. Go back into Menta change the priority level in the alarm block Redownload the Menta file. Go into Vista Open the object selection box Double click on the alarm object Click on the button Status button Change the priority level Click OK
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1543 Views

Preserve Configuration Parameters when recommissioning a device in LonMaker

Issue Recommission a device in LonMaker causes the loss of Configuration Parameter setting that were changed in the browser. Environment Echelon LonMaker Cause These values exist in the device, but not in the database. Resolution When recommissioning, select use Current Values in Device instead of Default. After you have Made all the changes to the CPs in the browser that you want: Close the browser Right click on the device Go to Resynch CPs Select the Option – Upload values from the device Click OK. This will upload the Value that you just sent to the device and insert those values a CP defaults into Lon Maker’s browser. This way every time you recommission a device it will not lose any of these changes.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1192 Views

Procedure for uninstalling I/NET Seven on a stand-alone host

Issue Procedure for uninstalling I/NET Seven on a stand-alone host Product Line TAC INET Environment I/NET Seven Cause This is the procedure for uninstalling I/NET Seven and removing trace files on a stand-alone host. Resolution Go to Control Panel > Add & Remove Programs Remove I/NET Seven Remove Microsoft SQL Desk Top Engine (MSDE) Go to Windows Explorer > Program Files Delete any remaining I/NET Seven files and any remaining MS SQL files
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
1666 Views

Reference for more information about Belden wire

Issue Some TCONs mention specific Belden wire products for LAN and Sub-LAN installation. Where can more information about Belden wire be found? Environment I/NET LAN and Sub-LAN Cause Wiring standards dictate certain communication wires to be run for proper comms. Resolution Go to the Belden website for more information: http://www.belden.com.
View full article
Picard Product_Support
‎2018-09-06 11:36 PM

Labels:
  • TAC INET
945 Views

Generate I/NET Seven Reports automatically by time of day

Issue Can I/NET Seven Reports be generated automatically by time of day? Environment I/NET Seven Reports Cause Desire to generate reports automatically by schedules. Resolution I/NET Seven can schedule reports using Auto Report Generation.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
984 Views

Replace the default I/NET splash screen image that appears at boot-up

Issue Replace the default I/NET splash screen image that appears at boot-up Environment I/NET Site Cause How to replace the default I/NET splash screen image that appears at boot-up Resolution Find the location of the image file “inetw.bmp” Replace it with the new file. I/NET will be looking for “inetw.bmp” when the I/O driver is restarted; so the new image must use the original name “inetw.bmp” in the bitmap format.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
1347 Views

Will restoring a controller following an upgrade of a PCU reset consumption data?

Issue After an upgrade of a PCU, if the controller is restored, will that reset the consumption data? Environment PCU Cause A restoration of the controller will delete existing consumption data. Resolution Yes. Refer to TCON 237, page 7-17.
View full article
Picard Product_Support
‎2018-09-06 10:32 PM

Labels:
  • TAC INET
915 Views

missing the first entry in ACTrans table

Issue In I/NET Seven, I’m missing the first entry in ACTrans table. I am in the process of upgrading the site from I/NET 2000. The Site is now running I/NET Seven revision 1.00 or 1.01. Environment I/NET Site Cause In I/NET Seven, I’m missing the first entry in ACTrans table. I am in the process of upgrading the site from I/NET 2000. The Site is now running I/NET Seven revision 1.00 or 1.01. Resolution This is a reported bug that has been fix in I/NET Seven rev 1.02 (Track Record #3436). DbCreate (which is a TAC product) was failing to import the first entry in the ACTrans table. Now, when an I/NET 2000 database is migrated, all entries will be brought to I/NET Seven. Subsequent edits can be performed and the list will remain intact.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
1121 Views

Add card access information to I/NET Seven at any time from the Video Badging host.

Issue Add card access information to I/NET Seven at any time from the Video Badging host. Product Line TAC INET Environment I/NET Site Cause Add card access information to I/NET Seven at any time from the Video Badging host. Resolution I/NET Seven Revision 1.02, (Track Record #3507 - ID Works) has been changed so information can be added to a card and saved to I/NET at any time. Check your INET’s readme and upgrade notes for details.
View full article
Picard Product_Support
‎2018-09-06 10:40 PM

Labels:
  • TAC INET
1270 Views

"no lines available" messages

Issue My customer’s I/NET Seven site is getting “no lines available” messages when the host attempts to dial the 06 tap that sent AMT information. Has this been fixed? Environment I/NET site Cause My customer’s I/NET Seven site is getting “no lines available” messages when the host attempts to dial the 06 tap that sent AMT information Resolution (I/NET Seven rev 1.02, Track Record #3422 -) A change has been made in the way calls are handled so the line is not dropped until I/O Server is shut down. This eliminates the failure to answer incoming calls after the first call and clears the problem of “no lines available” when the Host attempts to dial out.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
1016 Views

Set the Peripherals section of the Configuration Profile in I/NET Seven for Access Control

Issue How should I set the Peripherals section of the Configuration Profile in I/NET Seven for Access Control? I am not using I/DISKs; and I do not have any access control hardware on these comm ports. Environment I/NET Site Cause How should I set the Peripherals section of the Configuration Profile in I/NET Seven for Access Control? I am not using I/DISKs; and I do not have any access control hardware on these comm ports. Resolution Leave the ports at the default settings. Make sure you enable the Access Control option in the Workstation Options of the configuration profile.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
1236 Views

What database format does I/NET use?

Issue What is the name of the database format I/NET uses within its environment? Environment I/NET database Cause Building specifications may require the database format for design or as-built documents. Resolution The I/NET database format is proprietary and does not have a name. It is a "Closed system." As a matter of baseline security, it would be unwise to share ANY such information outside of the company. The distribution of such sensitive information increases risk to all of our customers, not just the requesting customer. As a provider of security/access control products, our priority is to protect all of our customers; one way we do that is by protecting engineering details.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
959 Views

File equalization is not available on the workstation if the link type is NetPlus Router, Integrated Dial, or Integrated NPR dial.

Issue Although site operation appears normal, there are problems with file equalization when the desktop PC is direct connected to the NPR. Active Configuration Profile, Link type is NetPlus Router. Environment I/NET Seven NetPlus Router Integrated Dial Integrated NPR dial Cause File equalization is not available on the workstation if your link type is NetPlus Router, Integrated Dial, or Integrated NPR dial. Resolution File equalization is not available on the workstation if your link type is NetPlus Router, Integrated Dial, or Integrated NPR dial. Refer to TCON 298, 3-13 for more information.
View full article
Picard Product_Support
‎2018-09-06 10:41 PM

Labels:
  • TAC INET
1167 Views

Grant momentary release on a door without ability to modify points

Issue Grant momentary release on a door without ability to modify points Environment I/NET DPU Cause One application would be security guards. You want to grant the guards the ability to momentary - release any door, but do not want to give them the ability to modify points. Resolution Give them access to only graphic pages. These pages should have internal DOs or internal DIs . Since these discrete points are two state, they can be used to trigger event sequences that will only open the doors for brief periods. Last and of course not least, go to the guards host passwords (not your host password), and remove any function you do not want them to have. You will need "Live Graphic Page" and probably several other functions, so you will have to customize this set up to fit your situation.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC INET
864 Views

Third party software on my I/NET PC

Issue Can I run third party software on my I/NET PC Environment I/NET Site Cause Third party software on same pc as I/NET Resolution TAC software is delivered for use on IBM and compatible PCs. While your PC is capable of running other third party software while running I/NET, trying to do so may present general operational difficulties. This is particularly true if the other third party software is memory resident. When used as it is intended, the TAC software is also memory resident. The use of more than one memory resident program at the same time may impose unresolvable PC system parameter conflicts and may cause one or more of the memory resident programs to fail. Refer to TCON 300.
View full article
Picard Product_Support
‎2018-09-06 10:53 PM

Labels:
  • TAC INET
1444 Views

Maximum size the SQL database using MSDE?

Issue What is the recommended maximum size the SQL database can be using MSDE? Environment I/NET Cause What is the maximum size the SQL database using MSDE? Resolution The MSDE server software distributed with I/NET Seven imposes a 2GB restriction on database size. Larger facilities, particularly those using image verification and/or AMT archiving, could potentially encounter data storage problems due to this restriction, and should consider upgrading to SQL Server 2000. Refer to TCON 300.
View full article
Picard Product_Support
‎2018-09-06 10:55 PM

Labels:
  • TAC INET
1242 Views

Accommodating Individual numbers greater than 24000

Issue Accommodating Individual numbers greater than 24000 Environment I/NET site Cause How do older I/NET systems accommodate Individual numbers that are greater than 24000? Resolution Traditionally, I/NET has required that the key/card numbers assigned to individuals fall within the range of 1 to 24,000. This range supports the maximum limit of 24000 individuals that can be defined for a single tenant. However, it is not uncommon to find that the actual number preprogrammed on a key/card is greater than 24,000. In order to accommodate these higher key/card numbers, I/NET provides a Key/Card Translation table for each tenant. Using the translation table, you can define up to 128 ranges of high key/card numbers and the starting target number. Refer to TCON 300 for more information.
View full article
Picard Product_Support
‎2018-09-06 10:56 PM

Labels:
  • TAC INET
1136 Views

Translating "large" key/card numbers (i.e., numbers greater than 24,000) directly to a lower number

Issue Is I/NET capable of translating “large” key/card numbers (i.e., numbers greater than 24,000) directly to a lower number? Environment I/NET site with access control Cause I/NET capable of translating “large” key/card numbers (i.e., numbers greater than 24,000) directly to a lower number? Resolution The I/NET system is capable of translating “large” key/card numbers (i.e., numbers greater than 24,000) directly to a lower number, without the use of the Key/Card Translation table. However, this functionality requires that the SLI and DPU binary loads are I/NET 2000 revision 2.x or I/NET Seven revision 1.x (or later) compatible, and that DIP switch 7 at the DPU is ON. For DPUs with earlier firmware versions, the use of the Key/Card Translation table is still required when key/card numbers are greater than 24,000. Refer to TCON300 for more details.
View full article
Picard Product_Support
‎2018-09-06 11:01 PM

Labels:
  • TAC INET
1390 Views
  • « Previous
    • 1
    • …
    • 266
    • 267
    • 268
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of