Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 23
    • 24
    • 25
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

Error message window appears when installing TAC Vista 5.1.6

Issue Error message window appears when installing TAC Vista 5.1.6 as below. It says that "XXX.dll file is an invalid Win32 application". But the installation could be finished without any other error messages. However if trying to run TACOS.exe after installation. Another error message window appears as below. It said, "MSVCR100.dll is an invalid Windows image, please check your installation disk". If you try to uninstall TAC Vista 5.1.6 which you just installed. You would get another error message window appears as below. It says "XXX.dll file is an invalid Win32 application". User can not run TAC Vista 5.1.6 in your computer finally. Product Line TAC Vista Environment Windows XP SP3 TAC Vista 5.1.6 Cause It may cause by the msvcr100.dll file is damaged.  Resolution Uninstall TAC Vista 5.1.6. Refer to How to uninstall and completely remove TAC Vista 5 for detail In the %system root%\WINDOWS\system32, copy "msvcr100.dll" file from someone who has installed TAC Vista 5.1.6 Rename the msvcr100.dll file which existed in the folder in your computer, user can rename the file such as msvcr100.dllx Copy the file from other computer and paste it into your computer folder Run TAC Vista 5.1.6 installation file again
View full article
Picard Product_Support
‎2018-09-10 06:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:49 PM

Labels:
  • TAC Vista
1337 Views

Unable to Run WebStation on Windows Server 2008

Issue Unable to Run WebStation on Windows Server 2008 Product Line TAC Vista Environment Vista Webstation 5.1.6 IIS ASP.net Cause IIS 7 and ASP.net must be installed before Vista Server in order for Webstation to function Resolution Uninstall Vista Server as outlined in How to uninstall and completely remove TAC Vista 5 Install IIS 7 and ASP.net Start the Server Manager Right-click Roles Click Add roles Select Web Server (IIS) In the following dialog click Add Required Features Click Next (twice) Select ASP.net In the following dialog click Add Required Role Services Click Next Click Install Install TAC Vista Server Install TAC Vista Webstation As administrator, Run the ASP.NET IIS Registration Tool (Aspnet_regiis.exe) for ASP.NET version 4.0 %SystemRoot%\Microsoft.NET\Framework\v4.0.30319\aspnet_regiis.exe -i -enable 64-bit OS: %SystemRoot%\Microsoft.NET\Framework64\v4.0.30319\aspnet_regiis.exe -i -enable
View full article
Picard Product_Support
‎2018-09-10 12:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:46 PM

Labels:
  • TAC Vista
1264 Views

Menta modifications are not saved into the Vista Database

Issue When you make a change to the Menta file and save that file back into Vista the changes are not available in Vista. An alarm appears stating ("Object does already exist " when expanding file in database) Product Line TAC Vista Environment Vista 5.1.7 Cause In some earlier versions of Vista, illegal characters were allowed to be entered in the Menta program specification name. Illegal characters in the program specification of a Menta file describes more on that problem. Resolution Rename the Menta program specification name. No more than 12 character and no spaces or illegal characters. Refer to Menta Warning: Syntax error for illegal characters which can not be used. Then generate the OP tree for the Menta application and save into the Vista database.
View full article
Picard Product_Support
‎2018-09-10 10:31 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:44 PM

Labels:
  • TAC Vista
1645 Views

Is it recommended to modify TGML Graphics from Remote Workstation?

Issue Is it recommended to modify TGML Graphics from Remote Workstation? Product Line TAC Vista Environment TAC Remote Workstation TAC Graphics Editor Cause Remote Workstation should not be used as an engineering tool. It is used only to access the system. Resolution Remote Workstation's recommended use is to access the system.  Its function is not meant to be used as an engineering tool. It is possible to access the TGML Graphic pages from remote workstation to monitor and modify the objects not for editing Graphic Pages. You can prevent the access for TGML Graphics from Remote Workstation. For settings, please refer to Prevent a graphic page from being edited.
View full article
Picard Product_Support
‎2018-09-10 04:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:42 PM

Labels:
  • TAC Vista
1226 Views

Error: The installed TAC Vista version is not compatible with XBuilder 5.1.8

Issue Version incompatibility of Vista and Xbuilder generates an error. TAC XBuilder The installed TAC Vista version is not compatible with XBuilder 5.1.8 The XBuilder projects created will not be possible to use with the installed TAC Vista. Do you want to start XBuilder? Product Line TAC Vista Environment XBuilder versions compatible with Vista 5 Xenta 913 Xenta 527 Xenta 511 Cause Incompatibility of versions when XBuilder checks installed version of Vista 5. Resolution This error message is generated when launching XBuilder. XBuilder checks the installed version of Vista against its version and will generate an error if it is not the same. However, this is only an issue when the XBuilder is to be loaded into a Xenta Server. When using a NON-Xenta server i.e. a stand alone device that is simple passing values, this message can be ignored. Please refer to Xenta Server firmware versus Vista Server versions for the Xenta Server compatibility matrix with Vista Server.
View full article
Picard Product_Support
‎2018-09-11 01:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:29 AM

Labels:
  • TAC Vista
1333 Views

Error when commissioning I/A MNL800 controller in LonMaker

Issue When commissioning I/A MNL800 controller in LonMaker LNS network management tool, an error will happen: One or more devices failed to update successfully, due to the following problem: "A device encountered an operational or messaging error while its configuration was being updated. (Subsystem: NS, #4031)" Product Line TAC IA Series, TAC Vista Environment Vista I/A MNL800 LonMaker Cause The issue is possibly due to more than one MNL800 controllers in the LonWorks network have the same Program ID defined in the WPT that causes the commissioning failed. Resolution Open the program of the MNL800 in WPT, right click in the blank place and choose Hardware Wizard. Click Next and modify the Program ID so that each MNL800 has unique program ID. Then it will be fine to commission them in LonMaker. There is also another method to deal with this issue. Please refer to Error: NS #4031 lcaErrNsUpdateFuncError A device encountered an operational or messaging error while its configuration was being updated (Subsystem: NS, #4031).
View full article
Picard Product_Support
‎2018-09-06 12:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:28 AM

Labels:
  • TAC IA Series
  • TAC Vista
1549 Views

Adding Webstation to an Existing Network

Issue After purchasing Webstation for a site, it still will not work even though the license is being read by LM Tools Product Line TAC Vista Environment Vista 5 Webstation Licensing LM Tools Cause When adding Webstation to an existing network it important to know if this was a Vista 5 "Stand-Alone" license or a "Full" version. Stand-Alone Vista will not allow any connectivity via IP. The needed license feature that comes in the Full version is "Vista.Server.Network". This can be verified by opening the site license in a text editor such as Notepad. Resolution Upgrade the site to a Full Vista license that contains the needed Vista.Server.Network feature. This will allow the Webstation to connect to Vista Server. A Demo license can be used in the interim until a Vista Upgrade License can be purchased, entitled and installed on the site. More information can be found in The Vista.Server.WebApps.Access license is missing.
View full article
Picard Product_Support
‎2018-09-10 10:35 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:26 AM

Labels:
  • TAC Vista
1238 Views

SNVT not updating Menta inputs in a 731

Issue SNVTs that have been directly connected to a Menta application are not being updated. The value of the SNVT is not the same as the value in the corresponding Menta application. Product Line TAC Vista Environment Vista 5.1.7 Xenta 700 series Cause The Menta application is running too fast and sending to many requests out to the LonWorks network. You can see that the LonWorks network is running at very high levels if you use a LonWorks protocol analyzer. For example. 20 SNVTs are directly connected to RI in a Menta application running at Medium/Fast (500ms cycle) This would mean that every 500 ms 20 request would be processed to the LonWorks network. The 731 can only process around 15 request per second. The above example would be requesting 40 samples per second.  Resolution The best solution for this problem is to use the connection object to connect SNVTs into Menta. Here is a link to User friendly way to make connections in Xbuilder for connection objects. The transfer rate can then be modified to slow down the LonWorks request through the 731. In the default setting for a connection object the transfer period is 10 seconds. To help with network request this time can be modified to prime numbers or realistic values for you application.
View full article
Picard Product_Support
‎2018-09-10 10:13 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:16 AM

Labels:
  • TAC Vista
1370 Views

Xenta Server Trend log has estimated values for a constant period of time

Issue When opening a Xenta Server (Xenta 5/7/913) trend log, it will display estimated value for a constant period of time. For example: A trend log trends room temperature every 30 minutes. An operator opens the trend log at 9AM, the trend log displays all the trend log values fine till 8AM. All values after 8AM before 9AM display as estimated value. Open the trend log again at 9:30AM, estimated values start at 8:30AM. Product Line TAC Vista Environment Xenta Server (Xenta 511, Xenta 527, Xenta 701, Xenta 711, Xenta 913) Cause Estimated value in trend log can have various causes. If it is always a constant period of time, it could be caused by the wrong time setting in Xenta Servers (most likely is the wrong day light saving minutes setting). Daylight saying time in a Xenta Server is set to 60 minutes by default. If Vista Server PC is set to not using daylight saying, then Xenta trend will not display the last hour trend since it believe the time is not reached yet. Resolution Please refer to Xenta Servers and Time Synchronization for step by step guide of manually setting up the Xenta Server's time. After the time setting change has been made, Xenta Server will reboot itself. When the reboot finishes, reopen the trend log and the issue should be solved.
View full article
Picard Product_Support
‎2018-09-06 01:32 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:12 AM

Labels:
  • TAC Vista
1424 Views

Privilege software version 2.01 crashes during installation on Windows XP

Issue Privilege software version 2.01 crashes during installation on Windows XP. Product Line TAC Vista Environment Aladdin Privilege Administrator 2.01 Vista IV Licensing Cause Privilege Administrator Incompatibility with XP Resolution Uninstall any previous Privilege Administrator (Please see How to uninstall Privilege Administrator 2.01 software for details on uninstalling the software) Download "Privilege Windows XP crash hotfix" (PS202.zip) Install PS202 by running setup.bat. Install Privilege Administrator 2.01 again.
View full article
Picard Product_Support
‎2018-09-07 03:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:11 AM

Labels:
  • TAC Vista
1533 Views

Periodic report will not run when Vista Server is running as a service

Issue Errors in Vista Workstation alarm window: "Failed to execute report XXXXX-YYYY, Error in "DDE Execute" command[27]" "Warning logged in B0WARLOG.TXT on node XXXXXX" Contents of B0WARLOG.TXT: "Could not open report XXXXX-YYYY, hRes=[-2147467261]Invalid pointer" Product Line TAC Vista Environment Vista Server Microsoft Windows 7 Microsoft Windows Server 2008 Cause Vista Server does not support running as a service under the local system or interactive user account. A PC account that has local administrator rights must be used to run Vista Server. Resolution Follow the registration instructions for Vista Server in Registering/Unregistering TAC Vista Server as a Windows service when registering TACOS.exe as a service.
View full article
Picard Product_Support
‎2018-09-10 12:55 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:06 AM

Labels:
  • TAC Vista
1396 Views

Launching Menta by opening an MTA file causes a Buffer Overrun Error

Issue Launching Menta by opening an MTA file causes a Buffer Overrun Error The error message: "Buffer overrun detected ... A buffer overrun has been detected which has corrupted the program's internal state. The program cannot safely continue execution and must now be terminated." Product Line TAC Vista Environment Menta Cause Menta's buffer for opening files is limited; if the file you are trying to open by double-clicking has a very long path (of 142+ characters), you will receive the Microsoft Visual C++ Runtime Library Buffer Overrun error message. Resolution Work arounds: Shorten the path to the Menta file. If it is possible to decrease the number of subdirectories or the length of the directory names to make the total path length less than 142 characters, this will correct the problem. Note: Never modify a Menta file name within Windows; only change Menta file names using the Menta application by using "Save As..." from the File menu. (See "Cannot open file" error when opening a Menta file for resolution if this occurs.)   If it is not possible or practical to change the path to the file, files with long paths can still be opened by launching Menta using the Start Menu or a desktop icon. Select File > Open and browse to the Menta file, then click "Open". Opening the file via this method will expand the path length limitation to over 200 characters.
View full article
Picard Product_Support
‎2018-09-07 12:12 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:57 AM

Labels:
  • TAC Vista
1920 Views

Installing I/NET and Vista on the Same PC Using I/NET with MSDE for File Equalization

Issue Installing I/NET and Vista on the Same PC Using I/NET with MSDE for File Equalization Product Line TAC INET, TAC Vista Environment I/NET 2.31 with MSDE Vista 5.1.4 with SQL2005 Express Windows XP Cause When Installing I/NET and Vista on the same PC and MSDE is desired for use with I/NET, I/NET must be installed first. If you are not using MSDE, please see Installation guidelines for installing I/NET and Vista on the same PC. Resolution Completely Remove I/NET, Vista and all versions of SQL and MSDE from the system. See Verify in Windows Registry all items are deleted after uninstall of I/NET Seven and MS SQL and How to uninstall and completely remove TAC Vista 5 for more details. Begin the I/NET Installation Select MSDE for the database installation. Complete I/NET and MSDE installation Install Vista Start Vista Server Start I/NET Configure I/NET as a Filemaster Build Database or restore from a backup.
View full article
Picard Product_Support
‎2018-09-10 03:17 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:54 AM

Labels:
  • TAC INET
  • TAC Vista
1752 Views

Xenta 102-AX temperature sensors reading incorrectly, very high

Issue Xenta 102-AX temperature sensors reading in the range of 130°F (54.4°C) when they should be closer to room temperature. Wiring has been checked and everything appears correct. What kind of temp sensor do I use for a 102-AX? Product Line EcoStruxure Building Operation, TAC Vista Environment Xenta 102-AX ETD-1xx duct temperature sensors ETR-1xx room temperature sensors STR-1xx room thermostats Cause Every other Xenta controller uses a 1.8k-ohm thermistor as a standard. Because the Xenta 102-AX is a modified version of the I/NET MR-VAV-AX, it still uses the 10k-ohm thermistors native to the I/NET product line. Resolution The Xenta 102-AX uses 10k-ohm thermistors. See 10k Thermistor compatibility with Xenta controllers for detailed information on the thermistor curve that is acceptable. Approved sensors are: ETD-2xx duct temperature sensors ETR-2xx room temperature sensors STR-2xx room thermostats STD-2xx duct temperature sensors
View full article
Picard Product_Support
‎2018-09-10 03:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:52 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2181 Views

"Read-only because object refers to a standard file" when editing Menta from Workstation

Issue "Read-only because object refers to a standard file" when trying to change Menta application (.mta file) from TAC workstation. "File object is locked by another application" when trying to edit a Menta application (.mta file) (file is not marked as reserved) Product Line TAC Vista Environment Menta Workstation Cause If a standard file is used, it is not possible to edit the "local" Menta file. Other causes are explained in "File object is locked by another application" error when trying to edit Menta file. Resolution If the referenced file is supposed to be a standard file, locate and edit the file referenced. If the referenced file is not supposed to be a standard file: Click on the more button under the MTA tab in the properties for the device. Uncheck "Reference standard file object.
View full article
Picard Product_Support
‎2018-09-07 06:57 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:44 AM

Labels:
  • TAC Vista
1718 Views

The system is not open. (Subsystem: LNS, #67)

Issue A service that requires the system to be open has been accessed prior to successfully opening the System object. TAC Vista System Plug-In The system is not open. (Subsystem: LNS, #67) Error: LNS #67 lcaErrSystemNotOpen Product Line TAC Vista Environment LonMaker Vista LNS Cause There are many circumstances that could cause this. For example, if you call the Validate method to validate a network database before opening the system, or if you call the Backup method to copy a network database before opening the system, this exception will be thrown. Resolution If registering or launching the TAC System Plug-in results in the error "System is not open, LNS #67" followed by "TACOSSysPin.Document launch failure Exception occurred," and "lnsplugin.api launch failure," then your LNS credits may be corrupted despite indications that they are not.  First reboot and try again.  If still fails, replacement credits have to be reordered from Echelon.  See description of LNS #147 in Error message in Vista System Plug-in: LNS System access failure, (Subsystem: NS,#147). It is also possible to get LNS #67 without having corrupted credits.  This has been seen a couple of times on databases that are upgraded from LNS 3.1 to LNS Turbo.  It seems to be hit or miss whether the upgrade will cause this issue or not.  The Licensing Upgrade 2006 discussed in LNS #147 should be installed.  Defragmenting the computer can also cause this corrupted credits with no indication and a TACOSSysPin error. Replacement credits will fix the issue even though there is no indication that they are corrupted.
View full article
Picard Product_Support
‎2018-09-07 04:06 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:38 AM

Labels:
  • TAC Vista
1343 Views

Adding a Xenta Programmable Controller to an NL220 System

Issue Adding a Xenta Programmable Controller to an NL220 System Product Line TAC Vista Environment NL220 Cause Commissioning a Xenta programmable controller in NL220 needs to follow a certain procedure in order to prevent various issues from occurring, such as controllers not showing online in Vista Workstation, etc. Resolution Adding a Xenta Programmable Controller to an NL220 LNS system. Preparation: Create the Menta File Install the Controller Adding the Device to the LNS database NL220:Create a Template for the device type. See NL220 Useful Functions and Shortcuts on how to create a template. NL220:Add a node using the correct device Template System plug-in: Assign Neuron ID and Menta file Add and match I/Os if applicable Bring the Device to the Vista Database System plug-in: Update TAC Network Drag controller to an existing group if desired, and delete the now empty group  Create group bindings Assign Neuron ID for the I/O modules Update the TAC Network again Check TAC Network Update Vista Database Check that your network is attached and OnNet  Download Application and Parameters Bring Vista Db online NL220: Commission and download the device (ignore I/O modules.) System plug-in: Commence Communication (if needed) NOTE:  It is very important that you Download Application and Parameters in the Vista system plug in THEN Commission the device in NL220. 
View full article
Picard Product_Support
‎2018-09-07 07:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:19 AM

Labels:
  • TAC Vista
2035 Views

Xenta 102-ES configuration and wiring for 2 position (on/off) heating control

Issue Xenta 102-ES configuration and wiring for 2 position (on / off) heating actuators or other digital heating control Product Line TAC Vista Environment Vista Xenta 102-ES Cause Wiring for 2 position heating control on the Xenta 102-ES is different than increase / decrease type actuators. Resolution The Xenta 102-ES documentation refers to two position heating control as thermal actuators, thermo or TAO and can be somewhat confusing. The same info applies whether using a two position hot water valve, any on / off type electrical heat (such as baseboard heaters or electric heating strips. Here's what you need to know: If using only one stage of heat: Select Thermo for Primary Heating in the Xenta 102-ES plugin or if configuring from Vista Workstation or the OP set nciAppOptions bit 5 to 1 and leave bit 6 as 0.   From the Xenta 102-ES plugin choose either Normally Closed (NC) or Normally Open (NO) from the box in between the Primary and Secondary Heating fields. Additionally, this can be configured from Vista Workstation or the OP by setting nciAppOptions bit 11 to 0 for normally closed (NC) operation or set bit 11 to 1 for normally open (NO) operation. Both terminals V3 and V4 will be switched when the first stage of heat is activated. These terminals operate in parallel in this configuration and either one can be used.   If using two stages of heat: Select Thermo for Primary Heating in the Xenta 102-ES plugin and select Enable for Secondary Heating. If configuring the device from Vista Workstation or the OP set nciAppOptions bit 5 and bit 6 to 1. From the Xenta 102-ES plugin choose either Normally Closed (NC) or Normally Open (NO) from the box in between the Primary and Secondary Heating fields. Additionally, this can be configured from Vista Workstation or the OP by setting nciAppOptions bit 11 to 0 for normally closed (NC) operation or set bit 11 to 1 for normally open (NO) operation. Both terminals V3 and V4 will be switched when the first stage of heat is activated. These terminals operate in parallel in this configuration and either one can be used. Only terminal V6 will be switched for second stage of heat. Note: The triac outputs of the Xenta 102-ES are ground sourcing and should be wired accordingly. See Digital outputs (V) on most Xenta 100 series controllers are ground sourcing (voltage sinking) for additional information.
View full article
Picard Product_Support
‎2018-09-10 10:46 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:36 PM

Labels:
  • TAC Vista
1588 Views

"PSU device driver failed, It may be missing or disabled!" or "An External installation failed : Hasp"

Issue "PSU device driver failed, It may be missing or disabled!” error or “An External installation failed : Hasp" error error when attempting to install Privilege Administrator. Product Line TAC Vista Environment Aladdin Privilege Administrator 2.01 Vista IV Licensing Cause Incompatibility with Windows Server 2003 Resolution Uninstall any previous installation attempts (Please see How to uninstall Privilege Administrator 2.01 software for instructions on uninstalling the software) Download HDD32.zip from Exchange Online located at Previous Vista Software \ TAC Vista IV License System Unzip and run HDD32.exe Install Privilege Administrator again. Only Vista version 4.20 and later is supported for use in Windows 2003 Server. Please observe that HDD32 may also solve some problems when installing Privilege License on Windows XP Note: Beginning 2012, PSS will no longer support the Privilege License System. The Tamfs26 Server will be retired along with TAC License Server software. It would be wise to inform the customer of this important information to plan for future upgrade in the event that their site license has issues.
View full article
Picard Product_Support
‎2018-09-07 03:38 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:31 PM

Labels:
  • TAC Vista
1513 Views

Echelon PCC-10 card does not fit in new Laptop PC Card slots

Issue New laptops do not support hardware for Echelon PCC-10 cards Product Line TAC Vista Environment Laptop Computers without PC Card slots or with ExpressCard Slots Cause Some new Laptops do not come with a PC Card slot or have an ExpressCard Slot that does not fit the PCC-10 card Resolution If the PC does not have a PC or express card slot then use NIC-709 USB Lon Talk adaptor. These are available from Loytec. See the procedure for changing from a PCC-10 LTA to a NIC-709 LTA. If the PC has a express card slot, see Can a LON PCC-10 PCMCIA card work in a laptop with an express card slot? for a solution.
View full article
Picard Product_Support
‎2018-09-10 02:56 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:30 PM

Labels:
  • TAC Vista
1884 Views
  • « Previous
    • 1
    • …
    • 23
    • 24
    • 25
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore