Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 163
    • 164
    • 165
    • …
    • 509
  • Next »

How to adjust the temperature Display on an ETR100 (1xx)

Issue Displayed temperature on the ETR is offset from the actual temperature reading of the controller. Environment ETR Thermostat Cause Factory calibration is offset from actual temperature. Resolution Click here to download the Installation and Operating Instructions Temperature Display Adjustments Temperature display may be adjusted by adjusting the ZERO or OFFSET Potentiometer (P2) as shown on the diagram.  Adjust P2 until the LCD Display reading, matches your controllers temperature reading if necessary. Note that all LCD Displays, are factory calibrated using an NIST Certified Glass Thermometer.
View full article
Picard Product_Support
‎2018-09-07 03:42 AM

Labels:
  • Andover Continuum
  • Field Devices
  • TAC IA Series
  • TAC INET
  • TAC Vista
1450 Views

Transactions/messages showing up in double, triple, in I/NET with remote clients

Issue Why are transactions/messages showing up in double, triple, etc in I/NET Product Line TAC INET Environment I/Net revisions 2.xx Cause The table linking for each of the reports and establishing a link between RptIndividualHistorz.TenantNdx and the RptCards.TenantNDX Resolution In versions of I/NET when using the I/NET client as a remote client, you must uncheck all the Host Masks on each remote client, otherwise, the Messages and transactions show up multiple times. If not using a Remote Client, the following solution may help you. Refer to the TCON301.
View full article
Picard Product_Support
‎2018-09-07 12:46 AM

Last Updated: Guinan RandyDavis Guinan ‎2021-08-24 12:25 PM

Labels:
  • TAC INET
1492 Views

National characters does not look right on the OP.

Issue National characters do not look right on the TAC Xenta Operator Panel (OP). Instead of Swedish (Danish, German, Spanish) characters, I get other characters in my OP. Product Line TAC Vista Environment TAC Menta TAC Vista TAC Xenta OP Cause You need to specify what character-set to use. You do this in the OP Configuration Tool. Resolution Open OP Configuration Tool from the Menta application Go to Format, - Character set file Pick the file for your language. Save and generate
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

Last Updated: Guinan RandyDavis Guinan ‎2021-08-24 12:11 PM

Labels:
  • TAC Vista
1295 Views

I/NET Pocket Guide in PDF Format

Issue Reference of I/NET Guide Product Line TAC INET Environment I/NET Seven Cause Combination of various TCON documents showing most common used functions for easy reference.  Note that this document is not maintained.  Please refer to documentation available on Exchange Resolution Download the INET Pocket Reference Guide PDF
View full article
Picard Product_Support
‎2018-09-10 02:42 AM

Last Updated: Lt. Commander mroche1 Lt. Commander ‎2021-08-23 02:35 PM

Labels:
  • TAC INET
4031 Views

Modbus basics

Issue Understanding and Troubleshooting Modbus Product Line EcoStruxure Building Operation, TAC IA Series, Other  Environment All Modbus environments. Cause Modicon first introduced Modbus in 1979. Modbus is an open standard,and it is the most widely used in the industrial environment. Modbus is publicly available and,due to its simplicity, many manufacturers use Modbus as a solution for integration in their own products. Many commercial products and systems support the Modbus RTU and Modbus TCP protocols. For further information, visit the Modbus website at http://www.modbus.org. Resolution For a brief understanding on Modbus and how to troubleshoot Modbus, refer to the Modbus Troubleshooting PDF
View full article
Picard Product_Support
‎2018-09-10 05:07 AM

Last Updated: Lt. Commander mroche1 Lt. Commander ‎2021-08-23 02:28 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC Vista
7439 Views

No users exist in Vista Workstation even though logged in as System Manager

Issue When logged in to TAC Vista Workstation it is not possible to see any users. Product Line TAC Vista Environment Vista Workstation Cause Only a user who has Authority level "System manager" has permission to see users.   Resolution If logged in with the system user, make sure that this user has the Authority level "System Manager". If not, try to log in with another System Manager level user. If you do not have one, contact your local Support who will then need a copy of your Vista Database in order to give you a list of all System Manager Users. There must always be ONE System Manager in a Vista system.
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-08-19 04:22 PM

Labels:
  • TAC Vista
1153 Views

Use a demo license when both TAC Vista and EcoStruxure Building Operation are installed on the computer

Issue It is not clear which part of the license system handles the end-user license and which part handles the demo license. Having both TAC Vista and EcoStruxure Building Operation(EBO) installed on the same PC can cause conflicts in the license system. Product Line EcoStruxure Building Operation   Environment Building Operation Enterprise Server   Cause If an EcoStruxure installation is only used for engineering and therefore will only have demo licenses activated, you don't need to install the license server. The service "FLEXnet Licensing Service" is installed by any EcoStruxure software package, and that is the service that will handle the activation of demo licenses. Resolution If you will only use demo licenses on a PC and/or also have TAC Vista installed on the same PC, only install the license administrator and not the license server.   It is also possible to run TAC Vista and EBO using the same License server, please see Lesson Learned SmartStruxure license and TAC Vista license on the same PC
View full article
Picard Product_Support
‎2018-09-11 01:40 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-08-19 04:11 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1808 Views

WebReports installer crashes when attempting connection to the Enterprise Server

Issue During the installation of WebReports, the installer crashes when clicking "Continue" in the "Reporting Agent" step. "StruxureWare Building Operation has stopped working" Product Line EcoStruxure Building Operation Environment WebReports Cause There is an issue with the installer when FIPS (Federal Information Processing Standards) algorithms are enforced. Resolution Open the local group policy editor (Start > run > gpedit.msc) Navigate to "Local Computer Policy > Computer Configuration > Windows Settings > Security Settings > Local Policies > Security Options" Locate the following item in the list on the right: "System cryptography: Use FIPS compliant algorithms for encryption, hashing, and signing" Edit the item, and select "Disabled" Install WebReports Example of FIPS being enabled
View full article
Picard Product_Support
‎2018-09-10 01:45 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-08-17 12:26 AM

Labels:
  • EcoStruxure Building Operation
1650 Views

Creating a Door for Read In/Out

Issue How to set up a Door on a controller for use as Read In/Out Access Environment Access Expert Windows 7 Server2012 R2 Server 2014 Cause There is no documentation on how to do this in Access Expert Resolution In order to do this, the following steps need to be followed: 1. Open up the site instance from IE 2. Log on to the system and Select the View All Hardware Icon 3. Select  the Interface that the door will be configured on 4. Uncheck the box  for Card In/ Free Out on Door Behavior 5. Click on the Save button on the bottom of the screen 6. Add a Reader to the interface and name accordingly for the IN Reader 7. Click on the Strike Button and verify that the Strike Relay is set to (Relay 1) 8. Click on the Door Switch button and select the proper setting for the Door Contact Tab 9. Click on Save and Close on the bottom 10. Click on the interface again and add a secondary Reader and make it a Slave Reader 11. Name accordingly as the Out Reader 12. If you notice this does not have any REX or Door Status Buttons to select from. 12. Click on Save 13. Restart the controller
View full article
Picard Product_Support
‎2018-09-10 10:54 AM

Labels:
  • EcoStruxure Access Expert
1313 Views

Multical 602 - No pulse output detected for cooling energy from top module 602-0C

Issue Multical 602 - No pulse output detected for cooling energy from top module 602-0C Environment Kamstrup Multical 602 heating/cooling meter with 602-0C top module (part number MAPULSETOP-C) Cause The 602-0C top module was purchased separately from the Multical 602 meter. The 602-0C top module is factory configured for a heat meter. Output C (terminals 16 and 17) is associated with heat energy CE+ which is stored in the calculator at register E1. The cooling energy CE- is stored in a separate memory location of the calculator at register E3.  Resolution Configure output C to cooling energy E3 using the METERTOOL HCW software and USB optical eye tool. Contact Product Support for the METERTOOL HCW software and the USB drivers for the USB optical eye tool The USB optical eye part number is MAOPTICUSB Procedure to configure output C to cooling energy: 1. Run the METERTOOL HCW software  2. Place the optical eye over the small window on the front of the calculator 3. Make sure that the optical tool is held in place magnetically and is resting on the lower pins 4. Press the connect button in METERTOOL HCW 5. Select Modules from the menu on the left-hand side 6. Select Configure Top Module from the next screen 7. The configure button will be inactive and in order to make any changes, you must read current configuration. Press the Read button 8. Output C is set to CE+ and that Output D is set to CV+ and the Configure button is now active 9. Using drop down box for Output C, select the option CE- to specify that this output will connect to the Cooling Energy register E3 10. Press the Configure button to write the new setting to the 602-0C top module and wait for this write process to complete It is recommended that the meter be cold started to ensure the changes takes effect. The procedure to cold start the meter is as follows.    Remove the calculator top piece from its base Click front buttons a few times to use up power (drains super-cap) Once display goes blank, wait for 30 seconds Replace the calculator top piece onto its base Display should come on and meter initialises it is best to cold start the meter to ensure changes takes effect, maybe we should mention that here, to do this...   a) remove the calculator top piece from its base b) click front buttons a few times to use up power (drains super-cap) c) once display goes blank, wait for 30 seconds d) replace the calculator top piece onto its base e) display should come on and meter initialises it is best to cold start the meter to ensure changes takes effect, maybe we should mention that here, to do this...   a) remove the calculator top piece from its base b) click front buttons a few times to use up power (drains super-cap) c) once display goes blank, wait for 30 seconds d) replace the calculator top piece onto its base e) display should come on and meter initialises
View full article
Picard Product_Support
‎2018-09-11 07:48 AM

Labels:
  • Field Devices
1855 Views

I/NET Station Conflict

Issue Error Message pop up reading: Station Conflict - [Link: 95] Station 00 at site 61 - Xenta527 conflicts with site 63 - xenta737-97. Station Conflict - [Link: 1000] Station 00 at site 03 - Host 3 conflicts with site 90 - Host 9. Product Line TAC INET Environment I/NET Cause Station conflicts occur when multiple devices share the same address. This is always the cause, but Identifying the possible addresses can be confusing. Host Address - The I/NET Configuration unique identifier for each host workstation.  1-250 Link address - The system segment in question. Contains multiple Stations and in DLA multiple sites. 0-99 It is generally advised that you do not use Link 0. The Link will typically define an NPR or Xenta 527. Such as the Link 4 Xenta 527 functions as the bridge between TCP/IP and the Link 4 Controller LAN segment. Site Address - Only used in DLA architecture.(1-63) 0 is only used in non-DLA NPR devices. The site allows for multiple Controller LAN segments to use the same Link address. This changes the description of a Xenta 527-NPR from Link 6, to Link 6 Site 1 and allows Link 6 Site 2, Site 3 and so on. In DLA architecture, the NPR devices will typically all use the same Station Address.  If link 6 Site 1 uses Station 0, Link 6 Site 2 may also use Station 0. Station Address - This is the unique identifier for addresses on a physical controller LAN wire.  You may use 0-63, but one must be reserved for the NPR device. Station level controllers are typically referred to in messaging by a 4 digit address.  Link 4 station 12 may be shorted to 0412.  All controllers in an I/NET system must have a unique for digit label of LLSS. The only exception to this is the NPR device as it function as a gateway and can have a site address to make it unique.  Controller LAN level controller do not show a site label. Resolution Change the address on one of the offending controllers In DLA situations, you can only duplicate the Station address used by the Xenta 527 If a 913 is used on the Controller LAN, it must also have a unique station ID Ensure all Host workstations have unique host ID's Ensure all devices in a DLA architecture have unique Link/Station combinations.  There cannot be 2 Link 4 Station 3s, even if they both have a unique site number.
View full article
Picard Product_Support
‎2018-09-07 02:02 AM

Labels:
  • TAC INET
1749 Views

Field Devices - DC1100/1400 "Set Back" operation.

Issue DC1100/1400, how does the "Set Back" operation work? Environment DC1100 DC1400 Drayton Set Back Cause The Set Back operation has been enabled, but does not appear to work. Resolution There are two modes of operation when using the Set Back function. 1 - Set Back Enabled - Space Night Setpoint - Disabled. - Do not use this option. Expected result At the end of occupancy, the plant will continue to operate, and the compensated setpoint temperature will reduce by the "Flow Night Setpoint" value. The display will show "Set Back". Actual result Controller switches off and displays "Outside Occupation". 2 - Set Back Enabled - Space Night Setpoint - Enabled. Space temperature above "Space Night Setpoint" setting. Controller acts as expected, it switches off and displays "Outside Occupation". Space temperature below "Space Night Setpoint" setting. The plant will switch on, and the compensated setpoint temperature will reduce by the "Flow Night Setpoint" value. The display shows "Set Back". The image below shows the appropriate section of the programming menu structure.  
View full article
Picard Product_Support
‎2018-09-10 11:07 PM

Labels:
  • Field Devices
1815 Views

VisiSat - Version 2.1 Build 196, installed with Visio 2010 / Visio 2016.

Issue Installing VisiSat 2.1 Build 196, when using Visio 2010, or Visio 2016. Product Line Satchwell MicroNet Environment Visio 2010 Visio 2016 VisiSat 2.1 Build 196 Cause Having installed VisiSat 2.1 Build 196, the customer cannot see any of the VisiSat tools. Visio 2010 is unlikely to be available Visio 2016 may be. Resolution To install VisiSat 2.1 Build 185, when Visio 2010 is being used, please carry out the following; Install Visio 2010. Start Visio 2010. Select the "Options" menu Select the "Trust Centre" menu Select the "Trust Centre Settings" menu Select the "Macro Settings" menu Choose "Enable All Macros" and save the changes. PLEASE NOTE - Visio 2016 is not supported by VisiSat 2.1 Build 196, and therefore has not been tested. Install Visio 2016 Start Visio 2016 Select the "Options" menu Select the "Trust Centre" menu Select the "Trust Centre Settings" menu Select the "Macro Settings" menu Choose "Enable All Macros" and save the changes. Select the "File Block Settings" menu Uncheck the boxes of the files you wish to open/save. Shutdown Visio and restart Windows. Restart Windows. Install Visisat. When opening Visisat you should now see the VisiSat tab in Visio 2010/2016 Please note, an occasional error has been seen when selecting the VisiSat "Options" menu, this error does not appear to cause any problems.
View full article
Picard Product_Support
‎2018-09-10 12:07 PM

Labels:
  • Satchwell MicroNet
1950 Views

What does the "| n" mean when viewing the properties of an OPC variable in Vista workstation?

Issue What does the "| n" mean when viewing the properties of an OPC variable in Vista workstation? Problems have been encountered with OPC variables Error messages such as "The object is no longer available in the servers address space", Also, canonical data type or OPC data types. Environment Vista 5.1.X TAC Vista OPC client Cause The "|n" is a reference to the data type or canonical data type as it's called in the OPC standard. In the world of OPC, the client application can be created in on one of many diverse programming languages. To resolve potential issues all OPC data types are assigned a specific Canonical Data Type. When a client application adds an OPC Item to an OPC Group it can use the default data type for the item or it can request the item with a specific canonical data type. If the OPC tool is used then the canonical is added automatically by checking with the server. It's only if variables are added manually that this information is required. Resolution The method used for addressing OPC variables is Folder.Variable_Name|Data_Type  The table below details the data types:  Data Type Canonical Type Size Data Range Boolean 11 1 Bit True or False Byte 17 1 Byte 0-255 Byte Array∗ 8209 1 Byte times Array Size 0-255 Short 2 2 bytes -32768 – 32767 Short Array∗ 8194 2 bytes times Array Size -32768 – 32767 BCD 18+ 2 bytes 0 - 9999 BCD Array∗ 8210 2 bytes times Array Size 0 - 9999 Word 18 2 bytes 0 – 65535 Word Array∗ 8210 2 bytes times Array Size 0 – 65535 Long 3 4 bytes -2,147,483,648 to 2,147,483,647 Long Array∗ 8195 4 bytes times Array Size -2,147,483,648 to 2,147,483,647 LBCD 19+ 4 bytes 0 - 99999999 LBCD Array∗ 8211 4 bytes times Array Size 0 - 99999999 Dword 19 4 bytes 0 – 4,294,967,295 Dword Array∗ 8211 4 bytes times Array Size 0 – 4,294,967,295 Float 4 4 bytes -(3.40 E38 – 1.40 E-45) to (1.40 E-45 – 3.40 E38) Float Array∗ 8196 4 bytes times Array Size -(3.40 E38 – 1.40 E-45) to (1.40 E-45 – 3.40 E38) Double 5 8 bytes -(1.798 E308 – 4.941 E-324) to 4.941 E-324 – 1.798 E308) Double Array∗ 8197 8 bytes times Array Size -(1.798 E308 – 4.941 E-324) to 4.941 E-324 – 1.798 E308) Char 16 1 Byte All Characters supported in the standard ASCII table String 8 1 – n Bytes All Characters supported in the standard ASCII table
View full article
Picard Product_Support
‎2018-09-06 03:31 PM

Labels:
  • TAC Vista
1306 Views

WebStation kiosk mode - Automatic logon, Full Screen, TGML Graphics without toolbars

Issue Is it possible when starting Internet Explorer: To log on automatically. To start in Full Screen mode. To show a TGML graphic (without system tree) and without entering a user name and password by a shortcut. Is it possible to hide the 2 toolbars as described below? Product Line EcoStruxure Building Operation Environment Building Operation WebStation Kiosk Mode Cause For some applications such as Kiosk screens, these features are needed Resolution Automatic logon This can be accomplished either by using the "Remember me" checkbox on the logon screen, or by using the guest logon feature. To make WebStation bypass the logon screen, create a user with a username of GUEST and a password of GUEST, give this user limited permissions. For 1.7 and later, the password for the GUEST account when used for WebStation automatic logon, is not compatible with the default password policies. Automatic logon will only happen if the GUEST account password is exactly "GUEST". If policies are not changed the automatic logon will stop working after 90 days. Full Screen mode To make Internet Explorer go directly to full screen mode, you can use the "kiosk mode" switch. Create a shortcut with the command  iexplore.exe -k [insert your URL here] Display TGML Graphic without toolbars Open the graphic you require, using the "Open in a new window" right-click command. Copy the URL and create a shortcut with it. When you open this URL the user is taken directly to the graphic, without toolbars or menus.
View full article
Picard Product_Support
‎2018-09-10 05:31 AM

Labels:
  • EcoStruxure Building Operation
4161 Views

Echelon LonMaker Turbo crashes repeatedly along with Microsoft Visio 2010

Issue Visio 2010 crashes whether or not LonMaker is running and both LonMaker and Visio 2010 crash together often when LonMaker is running. Echelon LonMaker An unexpected error occurred. Please save your drawing and exit Visio/LonMaker. Environment LonMaker Turbo Edition Visio 2010, possibly Visio 2007 Cause The "Send to Bluetooth" Add-In in Visio 2010 has been known to cause Visio to crash thus bringing LonMaker down with it. This often occurs when Bluetooth is disabled on the computer. When Visio is not able to access the bluetooth, the program crashes. Another possible cause is that the Add-In is not compatible with DEP. Resolution Steps to remove the Bluetooth add-in The simplest resolution to this problem is to disable the Send to Bluetooth add-in in Visio by following these steps: In Visio 2010 click File and select Options near the bottom of the left-hand pane. Select Add-Ins from left-hand pane then find and highlight the Send to Bluetooth add-in. In the Manage drop down box select COM Add-ins and click Go. Uncheck Send to Bluetooth and click OK. Shut down Visio and start LonMaker.     Steps to disable DEP in Visio In Visio 2010 click File and select Options near the bottom of the left-hand pane. Select "Trust Center" and click "Trust Center Settings" Click "DEP Settings" and remove the tick mark in "Enable Data Execution Prevention Mode" Shut down Visio and start LonMaker.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC Vista
1002 Views

Disallow Xenta Server web users or operators from changing their own password

Issue It may be desirable to the building management to remove web users and operators' privileges to change their own password. Environment Xenta Server Cause By default all users are able to change their own passwords. Resolution While the privilege that each user has to be able to change their password cannot be removed through standard configuration methods, it can, nevertheless, be removed through the FTP server of the Xenta controller. However, these changes will apply to all web users or to all operators rather than just specific users. Connect to the FTP of the Xenta 5/7/9xx controller by typing FTP://x.x.x.x (where x.x.x.x is the IP address of the controller) in the Windows Explorer address bar. Login with the root username and root password. Browse to the ftp://x.x.x.x/www/config/ folder and copy the either the file named operatormenu.xml or webusermenu.xml (depending on which type of user needs to be edited) and copy it to the desktop of the local machine. Open the ftp.cfg file with notepad on the local machine. If you are editing the web user file then delete the following lines: <MENU name="User Administration" value="/wm/useradmin" type="CFGDIR"> <MENU name="Change Password" value="/wm/useradmin/change_password" type="CFGPAGE"/> </MENU> If you are editing the operator file then only delete the following lines: <MENU name="Change Password" value="/wm/useradmin/change_password" type="CFGPAGE"/> </MENU> Save the file to the desktop without changing the name. In the FTP rename the original file by adding a "1" to the end of the name. For example webusermenu.xml would now be named webusermenu1.xml. This way you can keep the original file in the FTP if you ever need to revert back to it. Copy the newly edited file from the desktop to the FTP folder. If you are already logged into the Xenta server then log out and log back in. The menu should no longer be available. Important Note: If the system program is reloaded in the Xenta Server, these changes will be over-written and will need to be re-done.
View full article
Picard Product_Support
‎2018-09-10 12:30 AM

Labels:
  • TAC Vista
867 Views

Xenta webserver trendlogs - Server is busy error

Issue Trendlog Server is busy. Please try viewing the page again later Diagram The error looks like a java popup with error "Server is busy. Please try viewing the page again later" Environment Xenta webserver Cause It may take up to 15 minutes before a trendlogs actually starts (Depending on how many trendlogs that are available in the Xenta) after a restart of a Xenta webserver. During this time a Java error might appear if you try to call something including values from a trendlog i.e. Diagram Resolution The server is trying to startup all the trendlogs so please wait up to 15 minutes and try to view the page again.
View full article
Picard Product_Support
‎2018-09-06 01:59 PM

Labels:
  • TAC Vista
941 Views

Inactivation of Remote Alarm Manager alarm message

Issue The Remote Alarm Manager sends a message to the recipient indicating that an alarm has been inactivated. The screen shot below shows how a typical message will appear on the receiving mobile phone. Product Line Other, Satchwell MicroNet, Satchwell Sigma, TAC Vista Environment Remote Alarm Manager version 1.2 Cause An alarm message is generated, and the Remote Alarm Manager processes it in the normal way. After three days and at midnight, the Remote Alarm Manager will send a inactivation message to the on-call recipient, indicating that this alarm has been inactivated. Resolution This is not a fault with the system, it is operating as designed. When a new alarm is received by the Remote Alarm Manager, it is acted on in the way the configuration dictates. If the alarm remains on the system, without being retransmitted, then after three days the inactivation takes place. The 3 days is the default setting and can be changed if required.
View full article
Picard Product_Support
‎2018-09-07 06:17 AM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
1114 Views

Xenta 121 occupancy behaves differently when using an occupancy sensor

Issue Confusion over behavior of the Xenta 121 when using a occupancy sensor. Environment Xenta 121-FC Xenta 121-HP Cause When an occupancy sensor is not defined in the configuration of a Xenta 121 controller the effective occupancy will follow the command given by nviOccManCmd. However, when an occupancy sensor is defined, either as a network bound point or a hardwired sensor, the effective occupancy of a Xenta 121 will behave differently. Resolution The Xenta 121 operates as follows when using an occupancy sensor: The most notable difference in how the Xenta operates are: When nviOccManCmd is in either the OC_UNOCCUPIED or the OC_STANDBY modes then the Xenta 121 will ignore the state of the occupancy sensor. When nviOccManCmd is in the OC_OCCUPIED mode the Xenta 121 will follow the state of the occupancy sensor. Note that this means that the controller could actually enter the unoccupied mode even though nviOccManCmd is set to be occupied. When nviOccManCmd is in the Oc_Nul mode the effective occupancy of the Xenta 121 will Oc_Standby until a signal is received from the occupancy sensor at which time it will change to be Oc_Occupied. This behavior should be taken into consideration when deciding on how to implement an occupancy sensor. It may be desirable to set the nviOccManCmd to Oc_Nul whenever the occupancy sensor should be considered and to set it to Oc_Unoccupied when the occupancy sensor should be ignored. This effectively utilizes the occupied, unoccupied and standby modes as three distinct modes of operation to maximize comfort and efficiency.
View full article
Picard Product_Support
‎2018-09-07 04:03 AM

Labels:
  • TAC Vista
1034 Views
  • « Previous
    • 1
    • …
    • 163
    • 164
    • 165
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of