Multical 602 - No pulse output detected for cooling energy from top module 602-0C

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Multical 602 - No pulse output detected for cooling energy from top module 602-0C
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2060 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Multical 602 - No pulse output detected for cooling energy from top module 602-0C

Picard Product_Support
‎2018-09-11 07:48 AM

Issue

Multical 602 - No pulse output detected for cooling energy from top module 602-0C

Environment

Kamstrup Multical 602 heating/cooling meter with 602-0C top module (part number MAPULSETOP-C)

Cause

The 602-0C top module was purchased separately from the Multical 602 meter.
The 602-0C top module is factory configured for a heat meter. Output C (terminals 16 and 17) is associated with heat energy CE+ which is stored in the calculator at register E1. The cooling energy CE- is stored in a separate memory location of the calculator at register E3. 

Resolution

Configure output C to cooling energy E3 using the METERTOOL HCW software and USB optical eye tool.

  • Contact Product Support for the METERTOOL HCW software and the USB drivers for the USB optical eye tool
  • The USB optical eye part number is MAOPTICUSB

Procedure to configure output C to cooling energy:

1. Run the METERTOOL HCW software 

2. Place the optical eye over the small window on the front of the calculator

3. Make sure that the optical tool is held in place magnetically and is resting on the lower pins

4. Press the connect button in METERTOOL HCW

5. Select Modules from the menu on the left-hand side

6. Select Configure Top Module from the next screen

7. The configure button will be inactive and in order to make any changes, you must read current configuration. Press the Read button

8. Output C is set to CE+ and that Output D is set to CV+ and the Configure button is now active

9. Using drop down box for Output C, select the option CE- to specify that this output will connect to the Cooling Energy register E3

10. Press the Configure button to write the new setting to the 602-0C top module and wait for this write process to complete


It is recommended that the meter be cold started to ensure the changes takes effect. The procedure to cold start the meter is as follows. 
 
  • Remove the calculator top piece from its base
  • Click front buttons a few times to use up power (drains super-cap)
  • Once display goes blank, wait for 30 seconds
  • Replace the calculator top piece onto its base
  • Display should come on and meter initialises
it is best to cold start the meter to ensure changes takes effect, maybe we should mention that here, to do this...
 
a) remove the calculator top piece from its base
b) click front buttons a few times to use up power (drains super-cap)
c) once display goes blank, wait for 30 seconds
d) replace the calculator top piece onto its base
e) display should come on and meter initialises
it is best to cold start the meter to ensure changes takes effect, maybe we should mention that here, to do this...
 
a) remove the calculator top piece from its base
b) click front buttons a few times to use up power (drains super-cap)
c) once display goes blank, wait for 30 seconds
d) replace the calculator top piece onto its base
e) display should come on and meter initialises
Labels (1)
Labels:
  • Field Devices
Tags (2)
  • Find more articles tagged with:
  • 18088
  • 20096226
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore