Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/NET Station Conflict

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Station Conflict
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2034 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Station Conflict

Picard Product_Support
‎2018-09-07 02:02 AM

Issue

Error Message pop up reading:

Station Conflict - [Link: 95]
Station 00 at site 61 - Xenta527 conflicts with site 63 - xenta737-97.

Station Conflict - [Link: 1000]
Station 00 at site 03 - Host 3 conflicts with site 90 - Host 9.

Product Line

TAC INET

Environment

I/NET

Cause

Station conflicts occur when multiple devices share the same address. This is always the cause, but Identifying the possible addresses can be confusing.

  • Host Address - The I/NET Configuration unique identifier for each host workstation.  1-250
  • Link address - The system segment in question. Contains multiple Stations and in DLA multiple sites. 0-99 It is generally advised that you do not use Link 0. The Link will typically define an NPR or Xenta 527. Such as the Link 4 Xenta 527 functions as the bridge between TCP/IP and the Link 4 Controller LAN segment.
  • Site Address - Only used in DLA architecture.(1-63) 0 is only used in non-DLA NPR devices. The site allows for multiple Controller LAN segments to use the same Link address. This changes the description of a Xenta 527-NPR from Link 6, to Link 6 Site 1 and allows Link 6 Site 2, Site 3 and so on. In DLA architecture, the NPR devices will typically all use the same Station Address.  If link 6 Site 1 uses Station 0, Link 6 Site 2 may also use Station 0.
  • Station Address - This is the unique identifier for addresses on a physical controller LAN wire.  You may use 0-63, but one must be reserved for the NPR device. Station level controllers are typically referred to in messaging by a 4 digit address.  Link 4 station 12 may be shorted to 0412.  All controllers in an I/NET system must have a unique for digit label of LLSS. The only exception to this is the NPR device as it function as a gateway and can have a site address to make it unique.  Controller LAN level controller do not show a site label.

Resolution

  • Change the address on one of the offending controllers
  • In DLA situations, you can only duplicate the Station address used by the Xenta 527
  • If a 913 is used on the Controller LAN, it must also have a unique station ID
  • Ensure all Host workstations have unique host ID's
  • Ensure all devices in a DLA architecture have unique Link/Station combinations.  There cannot be 2 Link 4 Station 3s, even if they both have a unique site number.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 12351
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore