Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Expert
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building expert"

View in: "Building Automation Knowledge Base" | Community

222 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 10
    • 11
    • 12
  • Next »
Label: "EcoStruxure Building Expert" Show all articles

Enabling SNTP and time sync

Issue Unable to determine whether the time on the MPM is synchronized with the server after enabling the SNTP functionality Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause Time synchronization confirmation not available on MPM. Resolution To enable the SNTP functionality on the MPM, follow the below steps: Make sure the MPM has outbound activity; meaning that the MPM should be connected to the internet via a "hub or a "switch" (versus being connected directly to the computer) From the SNTP1 object, tick the Enable box Note: In object SNTP1, Server 2 will be used when Server 1 is unavailable only if Server 1 is a domain name. Server 2 will not be used if Server 1 is an IP address. In the ETH1 object, make sure that sure that the settings on the MPM matches those of the network, especially the DNS, Gateway and the Netmask (Subnet Mask) fields. These parameters can be found by typing "ipconfig /all" in command prompt or by contacting your IT personnel. Navigate to the CFG1 object, then using the "Date Configuration" box, set the date to today and the time to within 15 minutes before or after the actual current time. click save. Wait a few seconds and watch how the "current time" gets synced with the server's clock. Note: If SNTP was already active before changing the time manually, the clock will not be synced to the server unless you perform the following steps: Navigate to SNTP object. Uncheck the "Enable Box", then click save. Check the "Enable box", then click save again. Navigate to CFG object to verify that the time has been synced.
View full article
Picard Product_Support
‎2018-09-10 02:24 PM

Labels:
  • EcoStruxure Building Expert
2087 Views

Integrating a SE7200F5045E to Niagara G3 / AX. Which snvt can be used to display the current setpoint?

Issue Integrating a SE7200F5045E to Niagara G3 / AX. The tenant can change the occupied heating or cooling setpoint locally.  Which snvt can be used to display the current setpoint? Environment Niagara G3 Niagara R2 SE7200 series Cause Application question - wants to plot the proper setpoint on the graphic Resolution The nciSetpts snvt displays the current setpoints used by the SE7200 for heating and cooling in both occupied and unoccupied modes. Note:  The tenant can only change the occupied heating and cooling setpoints from the local keypad / display.
View full article
Picard Product_Support
‎2018-09-06 09:10 AM

Labels:
  • EcoStruxure Building Expert
  • TAC IA Series
1625 Views

Is the SE7200 compatible with the SED-WIN-P-5045 wireless window switch ?

Issue Datasheets indicate that the SE7200F5545P is compatible with the SED-WIN-P-5045 but changes in the switch are not being recognized by the SE7200.  Environment SE7200 wireless version Cause The SED-WIN wireless window switch was confirmed, as of the date of this article, as NOT compatible with the SE7200 controller model. Compatibility will be available at a later date. Resolution If necessary, use the VT7200F5014P-2624 controller with the SED-WIN-P-5045.  This controller has a Honeywell cover but it's functionally equivalent to the SE7200F5545P.  Just swap covers.
View full article
Picard Product_Support
‎2018-09-06 09:09 AM

Labels:
  • EcoStruxure Building Expert
1420 Views

Do any of the SmartStruxure Lite room controllers come with a morning warm-up cycle?

Issue Do any of the SmartStruxure Lite room controllers come with a morning warm-up cycle? Environment SmartStruxure Lite SE8x000 SE7x00 Cause Spec requirement Resolution None of the room controllers come with morning warm-up.  It would have to be provided at the network level (i.e. Automation Server).
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • EcoStruxure Building Expert
983 Views

How to download a copy of the log file from an MPM

Issue Cannot download the log file through Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause Feature not implemented Resolution To download a copy of the log file, you can type the following in the address bar of your browser, given that the MPM is powered up and accessible. 10.50.80.3/root/log.dat     (assuming the MPM's IP address is set to default 10.50.80.3)
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • EcoStruxure Building Expert
1341 Views

Cannot establish CANbus communication between MPM controllers.

Issue Cannot establish CANbus communication between MPM controllers.   Environment MPM controllers, any version Cause The CANbus trunk is missing the end of line resistors on the two end MPM controllers.  Each of the MPM controllers which are at the end of the CANbus trunk must have an 120 ohm resistor installed. Resolution Install a 120 ohm resistor at both ends of the CANbus trunk.
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • EcoStruxure Building Expert
1095 Views

Cannot discover wireless devices in MPM controller.

Issue Cannot discover wireless devices in MPM controller. Environment MPM controllers, any version Cause The Pan ID was set correct under the ZigBee Configuration property.  However when viewing the Pan ID setting under ZigBee Configuration, the Pan ID entered in the Settings box does not match the one displayed in the Current Configuration box.  The Zigbee Configuration Pan ID has somehow become corrupted. Resolution Reboot the MPM controller.  If a reboot does not clear the issue then the controller will have to be restored to factory default settings.  - Backup the MPM controller and then restore the MPM back to its original factory setting.
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • EcoStruxure Building Expert
1435 Views

Commisioning, Troubleshooting and FAQ's for SEZ7000 in BACnet and ZigBe networks

Issue Having trouble getting the stand-alone system to start-up Environment SmartStruxure Lite Multi-Purpose Manager Cause Communication between the SEZ7656 (Master) and one or multiple SEZ7260 (Slave) cannot be established Resolution 1 - SEZ7000 BACnet network commissioning (quick start-up) :   SEZ7656(E,F,H,R)1000B                       Rooftop controller: 1.  Press & hold (MENU) key until you see "Pswrd Set" 2.  Press (NO) to go to next parameter 3.  Leave "RTC MAC" to (4) 4.  Change "RTC Baud" to (38400) then press (YES) 5.  Press (NO), press (MENU), "Exit Menu" press (YES) 6. Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the rooftop controller   Reference manuals:            II-SE7000-SEZ7656E-A4.EN.4.2013.v1               II-SE7000-SEZ7656F1045B-A4.EN.4.2013.v1               II-SE7000-BNETRTU-A4.EN.4.2013.v1     SEZ72(60)x5000B                                 Zone thermostats: 1.  Press & hold (Override) key until you see "Pswrd Set" 2.  Press (Override) to go to next parameter 3.  Set “Zone MAC” to 11 on the 1 st thermostat, then 12, 13, … 4.  Change "Zone Baud" to (38400) on all thermostats 5.  Leave Get From at (255) 6.  Leave "RTC MAC" to (4) on all thermostats 7.  Let the thermostat reset 8.  Within a minute the thermostat will display the outside air temperature, this confirms communication with RTU controller (OAT sensor must be connected to the RTU controller) 9.  Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the zone controller   Reference manual:              II-SE7000-SEZ7260X-A4.EN.4.2013.vi   ----------------------------------------------------------------------------------------------------------------------------------------------   SEZ7000 ZigBee network commissioning (quick start-up) :   SEZ7656(E,F,H,R)1000W                      Rooftop controller: 1.    Press & hold (MENU) key until you see "Pswrd Set" 2.    Press (NO) to go to next parameter 3.    Leave "RTC MAC" to (4) 4.    Set “PAN ID” to (1) 5.    Change "Channel" to (15) 6.    Press (NO), press (MENU), "Exit Menu" press (YES) 7.    Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the rooftop controller   Reference manuals:            II-SE7000-SEZ7656E1045W-A4.EN.1.2013.v1                II-SE7000-SEZ7656F1045W-A4.EN.4.2013.v1                II-SE7000-WRTU-A4.EN.4.2013.v1     SEZ72(60)x5000W                    Zone thermostats: 1.    Press & hold (Override) key until you see "Pswrd Set" 2.    Press (Override) to go to next parameter 3.    Set “Zone MAC” to 11 on the 1 st thermostat, then 12, 13, … 4.    Set “PAN ID” to (1) on all thermostats 5.    Change "Channel" to (15) on all thermostats 6.    Leave “Get From” at (255) 7.    Leave "RTC MAC" to (4) on all thermostats 8.    Let the thermostat reset 9.    Within a minute the thermostat will display the outside air temperature, this confirms communication with RTU controller (OAT sensor must be connected to the RTU controller) 10.   Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the zone controller   Reference manual:              II-SE7000-SEZ7260X5x45W-US.EN.4.2013.v1   ----------------------------------------------------------------------------------------------------------------------------------------------   2 - SEZ7000 Troubleshooting :   Com Lost:       BACnet/ZigBee:                        Ensure RTU and Zone thermostats are compatible:             - Old models:                            SEZ7656(B)1000x only work with SEZ72(00)x5000x             - Current models:                      SEZ7656(E,F,H,R)1000x only work with SEZ72(60)x5000x   Ensure all thermostats have a unique MAC address.  If "RTC MAC" = 4, none of the Zone thermostats can use Zone MAC = 4     BACnet network wiring: -Daisy-chain only, no "T" connections -Use (+) and (-) terminals only, never use (REF) terminal -Use 2-22 low-capacitance shielded communication cable, attach shield at every junctions, tape and push back in the wall, only ground one side of the network -Install End-Of-Line, 1/4 watt, 120 Ohm resistor on both ends of network, install across (+) & (-) terminals)     3 - SEZ7260         FAQ's Q.   I only have access to the first few configuration parameters in the SEZ7260 zone thermostats. A.    Set "Get From" parameter to 255.   Q.   Some SEZ7200 don’t display outside air temperature. A.    If the thermostat display doesn’t scroll then set “Menu Scro” parameter to (On). The thermostat should scroll “Room Temp”, “Occupied”, “Out Temp” if Out Temp is missing then this thermostat doesn’t communicate with the RTU controller.  Verify the wiring and the network parameters.   Q.   Some SEZ7200 display outside air temperature at 0°F and this is not the right temperature. A.    This thermostat is randomly loosing communication with the RTU controller. Verify the wiring and the network parameters.   Q.   Floating damper does not open or close A.    This is probably cause the Common of the damper actuator is wired to Zone thermostat “24 Com” terminal, it should be wired to “24 Hot” since BO1 & BO2 terminals are switching Common.   Q.   BO5 reheat baseboard output doesn’t work. A.    Look at parameter “BO5 OALK” if outside air temperature is warmer than 32°F (default) then the output is disabled.  Look at “RehtConf” parameter.  Using a short wire, jump the BO5 – BO5 terminals, if the baseboard still don’t work then it’s something else, not thermostat related (wiring, relay …)   Q.    Can I use 24 Vac from another transformer (duct heater, baseboard relay …) on BO5 output? A.    Yes BO5-BO5 is an isolated triac contact, it can switch 24 Vac from another transformer.
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • EcoStruxure Building Expert
1633 Views

BACnet COM Address of Room Controller SE7000 and SE8000

Issue When installing SE7000/SE8000 Room Controllers to connect them to a BACnet MS/TP network, multiple issues can arise: Leaving the Room Controller's COM address at 254 (default value out of the box) will make the room controller undiscoverable by the front end. Choosing a Com address value between 128 to 253 will cause the front end system to convert the com address to 127, causing duplicates when working with multiple Room Controllers. Room controllers with COM address set to 0 will prevent the front end from discovering any devices Product Line EcoStruxure Building Expert, EcoStruxure Building Operation, Other Environment SE8xxx Room controller SE8000 Series SER8300, SE8300, SE8350, SE8600 Viconics branding VT8000 Series SE7000 Series Controllers, VT7000 Series Controllers, 7600, 7300, 7200 Cause Master devices, those who participate in the token-passing protocol, must be addressed from 1 to 127. Addresses from 128 to 253 are reserved for slaves who do not participate in the token passing; however, they can occupy lower addresses as well. Resolution COM address must be changed to a value in the range of 1-127.
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
2509 Views

SSL Compatibility Table

Issue Having difficulties determining which firmware/hardware version supports which feature. Some of main questions are: Is an SE8000 compatible with an MPM's firmware Can zigbee NYCE sensors be paired with MPMs Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager SE8xxx Room controller SE8000 Series SER8300, SE8300, SE8350, SE8600 Ex. Viconics branding VT8000 Series Cause Firmware versions are frequently updated to introduce new features Resolution   Room Controller Firmware Zigbee-Module Application MPM's Firmware Comments Lua4RC 1.0.7 N/A 2.13.4 and up A script must be uploaded via BACnet or USB cable in order to view the "LUA" Menu. ZigBee NYCE Sensors 1.0.6/1.0.7 051 - 0131R05 and up 2.13.4 and up   SE8650   1.2.0 051 - 0131R06 and up 2.17 and up   SE8600   1.0.7 051 - 0131R05 and up 2.13.4 and up   SE8300/ SER8300 1.0.7 051 - 0131R02 and up 2.12.4 and up No label on ZigBee Module 1.0.6 051 - 0131R02 and up 2.7.2 and up No label on ZigBee Module
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Labels:
  • EcoStruxure Building Expert
2092 Views

SmartStruxure Lite Demo Case

Issue SmartStruxure Lite Demo Case SSSB-SK1 and SSSB-SK2 Environment SmartStruxure Lite Demo Case Cause The part numbers SSSB-SK1 and SSSB-SK2 are no longer available for sale.  Resolution There are currently no demo cases available for sale for the SmartStruxure Lite product range. You can purchase the products and build a demo case/kit. Contact you local Schneider Electric sales offices for assistance. 
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Labels:
  • EcoStruxure Building Expert
1590 Views

Pairing SED-WIN and SED-Dor (wireless window/door contacts) with a SE8000, SE7000, and a MPM.

Issue Pairing SED-WIN and SED-Dor (wireless window/door contacts) with a SE8000, SE7000, and a MPM. Environment MPM SE7000 series SE8000 series Cause Quick reference / clarification Resolution The SE8000 can be paired to the wireless contacts with or without being networked to a MPM. The SE7000 must be networked to a MPM prior to being paired to wireless contacts. Always ensure the latest firmware is installed in the MPM.
View full article
Picard Product_Support
‎2018-09-06 09:04 AM

Labels:
  • EcoStruxure Building Expert
1360 Views

Read-only or Read/Write status of AVs in Room Controller device created in MPM

Issue When a Room Controller device is created under an MPM using one of the predefined devices in Building Expert, a number of its BACnet objects are mapped to AVs in the MPM. It is not possible to tell from the AV properties if the BACnet objects are read-only or read/write. Product Line EcoStruxure Building Expert Environment MPM SmartStruxure Lite Cause When a Room Controller device is added under an MPM using one of the predefined devices in Building Expert, a number of its BACnet objects are mapped to AVs in the MPM.  The BACnet objects made visible to the MPM are a small subset of the total number of BACnet objects in the device and consist of several different BACnet types, some of which are read-only and others are read/write.  Regardless of the BACnet type, they are all mapped to AVs whose properties do not distinguish between read-only and read/write objects. Resolution There is little documentation available on the predefined devices found in Building Expert. The best source of information is in PIC Statements and BACnet - Integration Guides. As an example I will use the SE8600UxB room controller. The "SE8600 Series BACnet - Integration Guide" is available on Exchange Download Center. In the MPM we have created a Lua script which monitors the occupancy status of the SE8600 and under certain conditions sets it to UnOccupied then turns it off after a delay. For this to work we need to know which AVs we can monitor and write to. Among the AVs mapped to the MPM for this device are "Occupancy Command", "Effective Occupancy" and "System Mode", which would seem to be suitable. The "SE8600 Series BACnet - Integration Guide" lists hundreds of BACnet properties of various object types, only 12 of which are mapped to the MPM. These 12 properties all appear as AVs in the MPM, regardless of their original BACnet object type. Also, although the object tables in the document list the read/write status of most of the objects, they do not list it for the objects mapped to the MPM. The only way to find out is to scan through the various tables of objects until you find one whose name matches one of the AVs in our example. Make a note of which table it is in. In our example: "Occupancy Command" and "System Mode" are in the MV table "Effective Occupancy" is in the MI table On page 35, under "Summary for Integrators", there is this line: "AI’s, BI’s & MI’s are not writable and are typically only used for status". "Effective Occupancy" appears in the MI object table, so it is read-only. As "Occupancy Command" and "System Mode" are in the MV table they are read/write. This procedure is applicable to all the Room Controllers available via the "Add Devices" command in Building Expert.
View full article
Picard Product_Support
‎2018-09-06 09:02 AM

Labels:
  • EcoStruxure Building Expert
2181 Views

Zigbee Driver Error Codes

Issue Need a description of Zigbee error codes Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause No list of error codes available Resolution Here is a list of all possible error codes Error Code (HEX) Error Code (Decimal) Error Description   -2 Device offline (communication initialization after changing Ext. Network ID in ZVC)   -1 Device not bound 0x00 0 Success. Operation was successful. 0x01 1 Failure. Operation was not successful. 0x02 - 0x7d 2 - 125 Reserved by Ember 0x7e 126 Not authorized. The sender of the command does not have authorization to carry out this command. 0x7f 127 A reserved field/subfield/bit contains a nonzero value. 0x80 128 Malformed command. The command appears to contain the wrong fields or invalid field. 0x81 129 Unsupported cluster command. The specified cluster command is not supported on the device. Command not carried out. 0x82 130 Unsupported general command. The specified general command is not supported on the device. 0x83 131 Unsupported manufacturer cluster command. A manufacturer specific unicast, cluster specific command was received with an unknown manufacturer code, or manufacturer code was recognized but command is not supported. 0x84 132 Unsupported manufacturer general command. A manufacturer specific unicast, ZCL command was received with an unknown manufacturer code, or the manufacturer code was recognized but the command is not supported. 0x85 133 Invalid field. At least one field of the command contains an incorrect value, according to the specification. 0x86 134 Unsupported attribute. The specified attribute does not exist on the device. ( Zigbee Module not fully compatible with Room controller and FW of MPM) 0x87 135 Invalid value. Out of range error, or set to a reserved value. 0x88 136 Read only. Attempt to write a read only attribute. 0x89 137 Insufficient space. An operation failed due to an insufficient amount of free space available. 0x8a 138 Duplicate exists. An attempt to create an entry in a table failed due to a duplicate entry already being present in the table. 0x8b 139 Not found. The requested information could not be found. 0x8c 140 Unreportable attribute. Periodic reports cannot be issued for this attribute. 0x8d 141 Invalid data type. The data type given for an attribute is incorrect. Command not carried out. 0x8e 142 Invalid selector. The selector for an attribute is incorrect. 0x8f 143 Write only. A request has been made to read an attribute that the requester is not authorized to read. No action taken. 0x90 144 Inconsistent startup state. Setting the requested values would put the device in an inconsistent state on startup. No action taken. 0x91 145 Defined out of band. An attempt has been made to write an attribute that is present but is defined using an out-of-band method and not over the air. 0x92 - 0xbf 146 - 191 Reserved by Ember 0xc0 192 Hardware failure. An operation was unsuccessful due to a hardware failure. 0xc1 193 Software failure. An operation was unsuccessful due to a software failure. 0xc2 194 Calibration error. An error occurred during calibration. 0xc3 - 0xff 195 - 255 Reserved by Ember   256 Device offline   257 Device profile does not match selected device widget in Building Expert
View full article
Picard Product_Support
‎2018-09-06 09:02 AM

Labels:
  • EcoStruxure Building Expert
4752 Views

How to tell the difference between a Wireless Window Switch (SED-WIN-P-5045) and a Wireless Door Switch (SED-DOR-P-5045).

Issue How to tell the difference between a Wireless Window Switch (SED-WIN-P-5045) and a Wireless Door Switch (SED-DOR-P-5045).  They are physically identical. Environment SSL window and door switch Cause Identical physical features Resolution Power cycle the switch (remove the battery for 60 seconds and then insert again) and verify the LED blinking pattern to confirm if it is a window switch or door switch  (2 blinks for window, 3 blinks for door). Or read the identification label on the printed circuit board. See page 3 of the installation guide.
View full article
Picard Product_Support
‎2018-09-06 09:01 AM

Labels:
  • EcoStruxure Building Expert
1247 Views

Can the SEC-TE communicate directly to SE8600?

Issue I have package units with point count that exceeds the SE78600 capacity, can I simply add the SEC-TE in order to complete I/O points requirements? Environment SEC_TE MPM SE8600 Cause Unfortunately, the SEC– TE can’t be used as extended I/O modules with the SE8600 however; you may use SEC-TE with the MPM-UN. Resolution SEC – TE can not communicate directly with the SE8600. However you can use the SEC-TE with the MPM-UN.
View full article
Picard Product_Support
‎2018-09-06 08:45 AM

Labels:
  • EcoStruxure Building Expert
1884 Views

Using the pulse counter in SEC-TE (TE2)

Issue Having issues configuring the pulse counter on the SEC-TE (TE2) Environment SmartStruxure Lite Multi-Purpose Manager SEC-TE (TE2) Cause N/A Resolution Navigate to the ZVC object of the SEC-TE and change "Analog Input 3 Mode" to "pulse counting". The value in AI3 (the counter) will then be incremented every time the pulse goes from 1 to 0 regardless of how long that takes. However, to convert the value of the counter to a more meaningful reading (e.g. water flow), you would need to use a Lua script in the MPM.   To reset the counter, click on the "Reset" button   Possible issues while testing: Using the Binary outputs of the TE2 for testing purposes will cause the counter to display unreliable readings. In fact, any binary output that induces voltage in AI3 will in inaccurate readings due to the noise induced. Instead, The binary outputs of the MPM can be used for testing before deploying the equipment on site.
View full article
Picard Product_Support
‎2018-09-10 02:26 PM

Labels:
  • EcoStruxure Building Expert
1712 Views

Multi Purpose Manager Daylight Savings Time for Australia

Issue Daylight savings do not take effect when it starts on 4th October Environment Multi Purpose Manager 2.15 and 2.16.    Cause Australia starts DST in October and ends in April of the following year. In North America and Europe, DST starts In March and ends in October or November in the same year. The built in DST feature in the MPM assumes that the "DST_Start_month" must be before the "DST_End_Month".  This issue will also applies to countries where the start of DST is towards the end of the year and DST ends the following year.  Resolution This issue has been reported to R&D. The following workaround can be used before this issue is fixed in a future MPM firmware.  1. Configure DST in the MPM to start in April and set DST to end in October. 2. Set the DST offset to -1 hour using the following Lua script in the MPM (add a Lua object and enter the following code)         if not init then            ME.CFG1_Time_Dst_Offset.value = -3600            init = 1         end     if not init then ME.CFG1_Time_Dst_Offset.value = -3600 init = 1 end
View full article
Picard Product_Support
‎2018-09-06 08:42 AM

Labels:
  • EcoStruxure Building Expert
1797 Views

IP rating on SE7000/SE8000

Issue It is required to know the IP rating on the SE7000 and SE8000 range devices, but this is not written in the datasheet. Product Line EcoStruxure Building Expert Environment SE7000 SE8000 Cause The information was not available at the time where the datasheets were created. Resolution The IP rating on the devices is IP30. At the time of writing, tests are ongoing for IP31 rating.
View full article
Picard Product_Support
‎2018-09-06 08:41 AM

Labels:
  • EcoStruxure Building Expert
1710 Views

Forcing a value from the BACnet front-end will be overridden by the Lua script

Issue When Forcing a value from SBO, it is just overwritten by the Lua script all the time. Product Line EcoStruxure Building Expert Environment MPM SE8000 Cause By default, the MPM executes the program once every second, so if written simply like: Output_1 = Off the output will be turned Off every second. Resolution Declare a few variables in the Lua script that will help you implement the logic you need, here is an example: var("Override_Status","ME.BV1") var("Override_Value","ME.BV2") if changed.Override_Status and Override_Status == 1 then ME.BO1 = Override_Value elseif changed.Override_Status and Override_Status == 0 then ME.BO1 = ME.BI1 end Basically, an override status points will act as a "Override button", and when it is active, The output will be equal to override value specified in SBO. Else, if it is disabled, the output will be set to what ever you currently have in your script. In the example above, the output will be equal to the input.
View full article
Picard Product_Support
‎2018-09-06 08:36 AM

Labels:
  • EcoStruxure Building Expert
2366 Views
  • « Previous
    • 1
    • …
    • 10
    • 11
    • 12
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore