Cannot establish CANbus communication between MPM controllers.
  • Cannot establish CANbus communication between MPM controllers.
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 09:07 AM
MPM controllers, any version
The CANbus trunk is missing the end of line resistors on the two end MPM controllers.  Each of the MPM controllers which are at the end of the CANbus trunk must have an 120 ohm resistor installed.
Install a 120 ohm resistor at both ends of the CANbus trunk.
  • EcoStruxure Building Expert
  • 17594