Issue
Integrating a SE7200F5045E to Niagara G3 / AX. The tenant can change the occupied heating or cooling setpoint locally. Which snvt can be used to display the current setpoint?
Environment
Niagara G3
Niagara R2
SE7200 series
Cause
Application question - wants to plot the proper setpoint on the graphic
Resolution
The nciSetpts snvt displays the current setpoints used by the SE7200 for heating and cooling in both occupied and unoccupied modes.