Commisioning, Troubleshooting and FAQ's for SEZ7000 in BACnet and ZigBe networks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Commisioning, Troubleshooting and FAQ's for SEZ7000 in BACnet and ZigBe networks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • SaidSawan
    SaidSawan
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1631 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Commisioning, Troubleshooting and FAQ's for SEZ7000 in BACnet and ZigBe networks

Picard Product_Support
‎2018-09-06 09:07 AM

Issue

Having trouble getting the stand-alone system to start-up

Environment

SmartStruxure Lite Multi-Purpose Manager

Cause

Communication between the SEZ7656 (Master) and one or multiple SEZ7260 (Slave) cannot be established

Resolution

1 - SEZ7000 BACnet network commissioning (quick start-up) :

 

SEZ7656(E,F,H,R)1000B                       Rooftop controller:

1.  Press & hold (MENU) key until you see "Pswrd Set"

2.  Press (NO) to go to next parameter

3.  Leave "RTC MAC" to (4)

4.  Change "RTC Baud" to (38400) then press (YES)

5.  Press (NO), press (MENU), "Exit Menu" press (YES)

6. Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the rooftop controller

 

Reference manuals:            II-SE7000-SEZ7656E-A4.EN.4.2013.v1

              II-SE7000-SEZ7656F1045B-A4.EN.4.2013.v1

              II-SE7000-BNETRTU-A4.EN.4.2013.v1

 

 

SEZ72(60)x5000B                                 Zone thermostats:

1.  Press & hold (Override) key until you see "Pswrd Set"

2.  Press (Override) to go to next parameter

3.  Set “Zone MAC” to 11 on the 1st thermostat, then 12, 13, …

4.  Change "Zone Baud" to (38400) on all thermostats

5.  Leave Get From at (255)

6.  Leave "RTC MAC" to (4) on all thermostats

7.  Let the thermostat reset

8.  Within a minute the thermostat will display the outside air temperature, this confirms communication with RTU controller (OAT sensor must be connected to the RTU controller)

9.  Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the zone controller

 

Reference manual:              II-SE7000-SEZ7260X-A4.EN.4.2013.vi

 

----------------------------------------------------------------------------------------------------------------------------------------------

 

SEZ7000 ZigBee network commissioning (quick start-up) :

 

SEZ7656(E,F,H,R)1000W                      Rooftop controller:

1.    Press & hold (MENU) key until you see "Pswrd Set"

2.    Press (NO) to go to next parameter

3.    Leave "RTC MAC" to (4)

4.    Set “PAN ID” to (1)

5.    Change "Channel" to (15)

6.    Press (NO), press (MENU), "Exit Menu" press (YES)

7.    Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the rooftop controller

 

Reference manuals:            II-SE7000-SEZ7656E1045W-A4.EN.1.2013.v1

               II-SE7000-SEZ7656F1045W-A4.EN.4.2013.v1

               II-SE7000-WRTU-A4.EN.4.2013.v1

 

 

SEZ72(60)x5000W                    Zone thermostats:

1.    Press & hold (Override) key until you see "Pswrd Set"

2.    Press (Override) to go to next parameter

3.    Set “Zone MAC” to 11 on the 1st thermostat, then 12, 13, …

4.    Set “PAN ID” to (1) on all thermostats

5.    Change "Channel" to (15) on all thermostats

6.    Leave “Get From” at (255)

7.    Leave "RTC MAC" to (4) on all thermostats

8.    Let the thermostat reset

9.    Within a minute the thermostat will display the outside air temperature, this confirms communication with RTU controller (OAT sensor must be connected to the RTU controller)

10.   Get the installation manual, go through all the configuration parameters, take note of the required parameters per your application then repeat steps 1. and 2. enter your configuration parameters in the zone controller

 

Reference manual:              II-SE7000-SEZ7260X5x45W-US.EN.4.2013.v1

 

----------------------------------------------------------------------------------------------------------------------------------------------

 

2 - SEZ7000 Troubleshooting :

 

Com Lost:       BACnet/ZigBee:                        Ensure RTU and Zone thermostats are compatible:

            - Old models:                            SEZ7656(B)1000x only work with SEZ72(00)x5000x

            - Current models:                      SEZ7656(E,F,H,R)1000x only work with SEZ72(60)x5000x

 

Ensure all thermostats have a unique MAC address.  If "RTC MAC" = 4, none of the Zone thermostats can use Zone MAC = 4

 

 

BACnet network wiring:

-Daisy-chain only, no "T" connections

-Use (+) and (-) terminals only, never use (REF) terminal

-Use 2-22 low-capacitance shielded communication cable, attach shield at every junctions, tape and push back in the wall, only ground one side of the network

-Install End-Of-Line, 1/4 watt, 120 Ohm resistor on both ends of network, install across (+) & (-) terminals)

 

 

3 - SEZ7260         FAQ's

Q.   I only have access to the first few configuration parameters in the SEZ7260 zone thermostats.

A.    Set "Get From" parameter to 255.

 

Q.   Some SEZ7200 don’t display outside air temperature.

A.    If the thermostat display doesn’t scroll then set “Menu Scro” parameter to (On). The thermostat should scroll “Room Temp”, “Occupied”, “Out Temp” if Out Temp is missing then this thermostat doesn’t communicate with the RTU controller.  Verify the wiring and the network parameters.

 

Q.   Some SEZ7200 display outside air temperature at 0°F and this is not the right temperature.

A.    This thermostat is randomly loosing communication with the RTU controller. Verify the wiring and the network parameters.

 

Q.   Floating damper does not open or close

A.    This is probably cause the Common of the damper actuator is wired to Zone thermostat “24 Com” terminal, it should be wired to “24 Hot” since BO1 & BO2 terminals are switching Common.

 

Q.   BO5 reheat baseboard output doesn’t work.

A.    Look at parameter “BO5 OALK” if outside air temperature is warmer than 32°F (default) then the output is disabled.  Look at “RehtConf” parameter.  Using a short wire, jump the BO5 – BO5 terminals, if the baseboard still don’t work then it’s something else, not thermostat related (wiring, relay …)

 

Q.    Can I use 24 Vac from another transformer (duct heater, baseboard relay …) on BO5 output?

A.    Yes BO5-BO5 is an isolated triac contact, it can switch 24 Vac from another transformer.

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (3)
  • Find more articles tagged with:
  • 17608
  • sez7600
  • zoning
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore