Zigbee Driver Error Codes

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Zigbee Driver Error Codes
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • SaidSawan
    SaidSawan
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4751 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Zigbee Driver Error Codes

Picard Product_Support
‎2018-09-06 09:02 AM

Issue

Need a description of Zigbee error codes

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager

Cause

No list of error codes available

Resolution

Here is a list of all possible error codes

Error Code (HEX) Error Code (Decimal) Error Description

 

-2 Device offline (communication initialization after changing Ext. Network ID in ZVC)

 

-1 Device not bound
0x00 0 Success. Operation was successful.
0x01 1 Failure. Operation was not successful.
0x02 - 0x7d 2 - 125 Reserved by Ember
0x7e 126 Not authorized. The sender of the command does not have authorization to carry out this command.
0x7f 127 A reserved field/subfield/bit contains a nonzero value.
0x80 128 Malformed command. The command appears to contain the wrong fields or invalid field.
0x81 129 Unsupported cluster command. The specified cluster command is not supported on the device. Command not carried out.
0x82 130 Unsupported general command. The specified general command is not supported on the device.
0x83 131 Unsupported manufacturer cluster command. A manufacturer specific unicast, cluster specific command was received with an unknown manufacturer code, or manufacturer code was recognized but command is not supported.
0x84 132 Unsupported manufacturer general command. A manufacturer specific unicast, ZCL command was received with an unknown manufacturer code, or the manufacturer code was recognized but the command is not supported.
0x85 133 Invalid field. At least one field of the command contains an incorrect value, according to the specification.
0x86 134 Unsupported attribute. The specified attribute does not exist on the device. ( Zigbee Module not fully compatible with Room controller and FW of MPM)
0x87 135 Invalid value. Out of range error, or set to a reserved value.
0x88 136 Read only. Attempt to write a read only attribute.
0x89 137 Insufficient space. An operation failed due to an insufficient amount of free space available.
0x8a 138 Duplicate exists. An attempt to create an entry in a table failed due to a duplicate entry already being present in the table.
0x8b 139 Not found. The requested information could not be found.
0x8c 140 Unreportable attribute. Periodic reports cannot be issued for this attribute.
0x8d 141 Invalid data type. The data type given for an attribute is incorrect. Command not carried out.
0x8e 142 Invalid selector. The selector for an attribute is incorrect.
0x8f 143 Write only. A request has been made to read an attribute that the requester is not authorized to read. No action taken.
0x90 144 Inconsistent startup state. Setting the requested values would put the device in an inconsistent state on startup. No action taken.
0x91 145 Defined out of band. An attempt has been made to write an attribute that is present but is defined using an out-of-band method and not over the air.
0x92 - 0xbf 146 - 191 Reserved by Ember
0xc0 192 Hardware failure. An operation was unsuccessful due to a hardware failure.
0xc1 193 Software failure. An operation was unsuccessful due to a software failure.
0xc2 194 Calibration error. An error occurred during calibration.
0xc3 - 0xff 195 - 255 Reserved by Ember

 

256 Device offline

 

257 Device profile does not match selected device widget in Building Expert
Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (1)
  • Find more articles tagged with:
  • 17863
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore