Issue
Having difficulties determining which firmware/hardware version supports which feature. Some of main questions are:
- Is an SE8000 compatible with an MPM's firmware
- Can zigbee NYCE sensors be paired with MPMs
Product Line
EcoStruxure Building Expert
Environment
- SmartStruxure Lite Multi-Purpose Manager
- SE8xxx Room controller
- SE8000 Series
- SER8300, SE8300, SE8350, SE8600
- Ex. Viconics branding VT8000 Series
Cause
Firmware versions are frequently updated to introduce new features
Resolution
|
|
Room Controller Firmware |
Zigbee-Module Application |
MPM's Firmware |
Comments |
|
Lua4RC |
1.0.7 |
N/A |
2.13.4 and up |
A script must be uploaded via BACnet or USB cable in order to view the "LUA" Menu. |
|
ZigBee NYCE Sensors |
1.0.6/1.0.7 |
051 - 0131R05 and up |
2.13.4 and up |
|
|
SE8650
|
1.2.0 |
051 - 0131R06 and up |
2.17 and up |
|
|
SE8600
|
1.0.7 |
051 - 0131R05 and up |
2.13.4 and up |
|
|
SE8300/ SER8300 |
1.0.7 |
051 - 0131R02 and up |
2.12.4 and up |
No label on ZigBee Module |
|
1.0.6 |
051 - 0131R02 and up |
2.7.2 and up |
No label on ZigBee Module |