Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

720 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 9
    • 10
    • 11
    • …
    • 36
  • Next »
Label: "Field Devices" Show all articles

Replacement of VTR Valve Body by VTRE or MB/MBF Valve Body due to obsolescence.

Issue VTR Valve Body requires replacement due to obsolescence. Product Line Field Devices Environment VTR VTRE MB MBF Cause Obsolescence of VTR Valve Body. Resolution VTR Valve Bodies are obsolete and have been for many years.  VTR Valve Bodies were available with either Flanged or Screwed connections.   REPLACEMENT OF VTR FLANGED CONNECTION VALVE BODY  A replacement for the VTR Flanged Valve Body (20-150mm only) may be selected from the VTRE range of flanged valve bodies, N.B. It should be noted that the VTRE Valve Body is rated PN6 whereas the VTR was rated PN10. The VTRE Flanged Valve Body may be operated by the EM9 Actuator. Alternatively the VTRE Flanged Valve Body may be operated by the M9B actuator. No Linkage Kit is required to mount the EM9 or M9B Actuator on the VTRE Flanged Valve Body. Alternatively a replacement for the VTR Flanged Valve Body (65-100mm only) may be selected from the MBF range of Flanged Valve Bodies. N.B. It should be noted that the MBF Valve Body is rated PN6 whereas the VTR was rated PN10. The MBF Flanged Valve Body may be operated by the MD20B series actuator. Alternatively the MBF Flanged Valve Body may be operated by the MD20A actuator. A Linkage Kit (914-1070-000) will also be required.   REPLACEMENT OF VTR SCREWED CONNECTION VALVE BODY  A replacement for the VTR Screwed Valve Body (15-50mm) may be selected from the MB range of screwed valve bodies. The MB Screwed Valve Body may be operated by the MD10B series actuator. Alternatively the MB Screwed Valve Body may be operated by the MD10A actuator. A Linkage Kit (914-1071-000) will also be required.   The datasheets concerning all the above options are available for download.
View full article
Picard Product_Support
‎2018-09-10 05:45 AM

Last Updated: Sisko DavidChild Sisko ‎2022-03-03 08:38 AM

Labels:
  • Field Devices
2011 Views

EP Series Pressure Sensor Power Consumption

Issue EP series information not available in documentation Product Line Field Devices Environment EP Series Pressure Sensor Cause Required information for planning installation. Resolution The EP 3x series consumes maximum 20mA input power as determined in loop powered mode (4-20mA).  When in three-wire voltage output mode, up to 2 mA of additional current may be drawn from the load. Further information is available on the Schneider Electric Exchange - EP Series Pressure Sensors.
View full article
Gary Schneider Alumni (Retired)
‎2022-02-18 05:07 AM

Last Updated: Sisko DavidChild Sisko ‎2022-02-18 05:53 AM

Labels:
  • Field Devices
764 Views

Controlli VSB valve to Forta actuator linkage kit

Issue When replacing a brand x valve with a Forta M800, a linkage kit may be necessary. Product Line Field Devices Environment Forta M800 VSB VSB4F VSB F AG52 8800129000 Cause Linkage kit requirement for application. Resolution Linkage kit required between Controlli VSB valve and Forta M800 is the AG52, part no 8800129000.
View full article
Picard Product_Support
‎2018-09-06 10:08 AM

Last Updated: Sisko DavidChild Sisko ‎2022-01-27 03:26 AM

Labels:
  • Field Devices
1188 Views

VSB, VSB..F, VMB, VMB..F Schneider Electric replacement valves

Issue VSB valves have been substituted by the Schneider Electric V211T valve VSB..F valves have been substituted by the Schneider Electric V211 valve VMB valves have been substituted by the Schneider Electric V311T valve VMB..F valves have been substituted by the Schneider Electric V311 valve Product Line Field Device Environment VMB VSB Cause The existing actuator is not compatible with the replacement valve as it is a different type. Resolution Schneider Electric  are no longer supplying VSB and VMB valves. They are replaced by a Schneider Electric Venta valve. Note: VSB and VMB valves are still manufactured by Controlli. VSB 2 ports are replaced by the V211T, VSB..F is replaced by the V211. VMB 3 ports are replaced by the V311T, VMB..F is replaced by the V311. The existing actuator will no longer fit on the new valve and needs to be replaced as well. If the actuator was a Controlli MVB22, MVB26 or MVB28, then replace with MV15B-230 actuator. If the actuator was a Controlli MVB46, then replace with MV15B-24 actuator. If the actuator was a Controlli MVB36, MVB52 or MVB56 then replace with M800 actuator. For compatibility: V211, V211T, V311 and V311T Venta valves are directly compatible with the Forta range of actuators e.g. M310, M400, M800, M1500, M3000, M700, MG900 and the MV15B-24/230 and no linkage kits are required.
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Last Updated: Sisko DavidChild Sisko ‎2022-01-27 03:23 AM

Labels:
  • Field Devices
2431 Views

How to configure a schedule in an SE8000

Issue Unable to configure the schedule in SE8000 series thermostat. Product Line EcoStruxure Building Expert, Field Devices Environment SE8000 Cause The system is not following building occupancy and operation as needed Resolution Tap and hold the top middle of the screen and tap on lower right arrow of page 1/2 setup. There are seven different schedule setting screens, one for each day of the week. Each day can have different scheduled events. Options The options settings allow the Room Controller to function in Occupied or Unoccupied. Occupancy Command Local occupancy: occupancy is determined by local PIR or schedule, as configured under Occ. Source from the configuration menu. Schedule Type 7 days: Independent scheduling for each day 5+1+1 days: Weekdays scheduling and Independent Weekend scheduling for Saturday and Sunday 5+2 days: Weekdays scheduling and Weekend scheduling
View full article
Picard Product_Support
‎2018-09-10 09:49 AM

Last Updated: Administrator CraigEl Administrator ‎2021-12-21 01:25 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
2288 Views

PIBCV Valve

  Issue PIBCV valves, stem up or stem down for valve open. Product Line Field Devices Environment PIBCV Valves VP220, VP221, VP222, VP228 Cause Further information required as to whether stem up or stem down for valve open position. Resolution When the stem is up (retracted into the actuator) the valve is open.   Example:
View full article
Sisko DavidChild Sisko
‎2021-12-07 07:41 AM

on ‎2021-12-07 07:41 AM

Labels:
  • Field Devices
829 Views

CSC - Help with checking the operation of this controller.

Issue Checking operation of CSC. Product Line Field Devices Environment CSC5252 CSC5352 Cause The operation of the CSC compensator explanation. Resolution The operation of a compensator is to adjust the system flow temperature, in relation to changes in the outside air temperature. The system flow temperature can be further adjusted by the addition of a room temperature sensor, which will provide room influence. The CSC 5252/5352 controller is programmed with a complete set of "Default" settings, these settings will allow the controller to operate as soon as its powered up. Although the controller has a complete range of adjustable settings, accessed through the "Fine Tune Mode", for a basic installation the "Quick Set Mode" can be used. The screen shot below explains how to enter the Quick Set Mode and the settings available. Controller data sheet Controller User guide   Compensated Flow Temperature Set-point: The compensated flow temperature set-point is automatically adjusted based on a ratio for set-point adjustments against the outside temperature changes. A consistent ratio across the entire outside temperature range, may not provide suitable control. For example: with radiator type systems, radiators are less efficient at lower water flow temperatures and need to be provided with a higher temperature to compensate for this initially. The “Set compensator ratio 1”and the “Set Ratio 2” settings provide the ratio of the change to the flow temperature set-point for changes in the outside air temperature, the ratio used is based on the “Set Change-over Value”, with the compensated slope starting from the “Set Flow Origin”. The “Set Flow Temperature Set-up Value” and “Set Night Set Back Value” provide a constant adjustment of the flow temperature set-point to a given building control requirement. The default settings would give a resultant flow temperature as shown follows:     The CSC5352 Calculator presents these settings in a graphical and listed format, making it easier to visually confirm the effects any changes to these settings would make.    
View full article
Picard Product_Support
‎2018-09-10 03:34 AM

Last Updated: Sisko DavidChild Sisko ‎2021-11-19 07:33 AM

Labels:
  • Field Devices
2026 Views

SpaceLogic SLA CO2 sensors field calibration

Issue SpaceLogic SLA CO2 units prior to date code 2138 cannot be field calibrated and ABC (Auto Baseline Calibration) is not set to ON by default. Product Line Field Devices Environment Veris Models – Cost Down version: CWE2, CWE2C, CWE2D, CWE2H, CWE2K, CWE2M, CWE2N, CWV2 Firmware prior to REV1.05.23 Prior to 2138 DC   Schneider Electric + Veris Models: CW2LA2A, CW2LA2AV, CW2LAXA, CW2LAXAV SLABLC2, SLABLCV2, SLABLCVX, SLABLCX, SLASLC2, SLASLCV2, SLASLCVX, SLASLCX, SLAWLC2, SLAWLCV2, SLAWLCVX, SLAWLCX Firmware prior to REV2.08.41 Prior to 2138 DC Cause The CO2 sensors are calibrated during manufacture, but can develop an offset during shipment or storage. Units cannot be field calibrated other than by the Auto Baseline Calibration (ABC) algorithm.  The offsets can be greater than 200PPM.  The ABC only calibrates at 30PPM a week.  That would require wait times of greater than 6 weeks. Resolution Replace with a unit with a date code of 2138 or higher or make sure ABC is enabled and wait the necessary time for ABC to correct.
View full article
Ensign Brandon_Brouwer Ensign
‎2021-11-15 04:48 PM

on ‎2021-11-15 04:48 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
1676 Views

Registers 35 and 36 in the TC900

  Issue What is the purpose of modbus registers 35 and 36 in the TC900. Product Line Field Devices Environment TC900 Cause Further detail required for registers 35 and 36 and how they interact.   Resolution The TC900 allows either the onboard sensor or an external sensor or a value e.g. a temperature value binded to a modbus (16bit unsigned) value be written to the TC900 and be used.   Register 24 determines if the in-built sensor (00) or the external sensor (01) is displayed on the screen If register 35 = 00, then the sensor set in register 24 is displayed.   Register 36 has the ability to be the binded sensor and be written to (FC06) with a value x10. e.g 23.5 should be writte as 235. If register 35 = 01, then the value in register 36 is displayed on the screen.   However, if register 23 = 01, then the setpoint is displayed on the screen.   Note, in the TC900, registers start at 0000, therefore in EBO add '1'.  
View full article
Sisko DavidChild Sisko
‎2021-11-11 07:13 AM

Labels:
  • Field Devices
1449 Views

Using Windows Problem Steps Recorder

Issue Need to capture steps taken to reproduce a problem or a solution Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices, OTHER, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Windows 7 Windows 10 Windows Server 2008, 2012, 2016 Cause A series of screen captures will help to demonstrate the steps needed to reproduce a problem or a solution. You can use this tool to capture the steps you take as a problem occurs and send the output to someone so they can see a screenshot of each step. Resolution In Windows click on the Start menu button  Type "PSR" Windows 7Windows 7 Windows 10, 2012, 2016Windows 10, 2012, 2016 Open the Problem Steps Recorder Windows 7Windows 7 Windows 10. 2012, 2016Windows 10. 2012, 2016 Click Start Perform the desired tasks Click Stop Choose a location to save the file output The .zip file will contain a .mht file which can be opened in a web browser The screenshots will appear in order  This will be followed by a detailed output of keystrokes and mouse movements. For additional information please refer to Microsoft webpage on this topic: Record steps to reproduce a problem 
View full article
Picard Product_Support
‎2018-09-10 06:54 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-10-14 06:38 PM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2138 Views

Revised part numbers V321

Issue V321 had a design revision in 2007 that made the original part numbers obsolete. And again in 2020, valve sizes DN65, 80 and 100 were also revised. Product Line Field Devices Environment V321, DN65:  7312153000 (2007), 7312153010 (2020) V321, DN80:  7312157000 (2007), 7312157010 (2020) V321, DN100:  7312161000 (2007), 7312161010 (2020) V321, DN125:  7312165000 (2007) V321, DN150:  7312169000 (2007) Cause Revision in part numbers. Resolution In 2007, stems were changed from brass to stainless steel. In 2020, on sizes DN65, 80 and 100 the bonnet profile was changed, see PA-00790 New Valve Part nos V222, V292, V321.    Please use the latest available revision in part number when ordering, See your local price list, or product data sheet, or contact your Orders Dept for details.   At 2021 part no's are: V321, DN65:    7312153020 V321, DN80:    7312157020 V321, DN100:  7312161020 V321, DN125:  7312165010 V321, DN150:  7312169010  
View full article
Picard Product_Support
‎2018-09-06 10:36 AM

Last Updated: Sisko DavidChild Sisko ‎2021-10-08 08:19 AM

Labels:
  • Field Devices
2304 Views

Fan command does not turn of on the SE7300 or SE8000 controllers

Issue SE7300 and SE8000 room controller fan speeds do not turn off when fan mode is set to auto. When cooling and / or heating is no longer needed, the fan speed remains at low speed. Product Line EcoStruxure Building Expert, Field Devices Environment SE7000 series room controller SE8000 series room controller Cause It is required that the fan be turned off when no demand for cooling or heating is needed. Resolution SE7300 controllers Enter the configuration mode of the room controller. Refer to page 19 of the SE7300 Series Installation Guide for the procedure to enter the configuration mode. In configuration mode, there is a parameter 'AutoFan'. The default mode for this parameter is 'AS'. In order for the fan to stop when there is no demand, the mode should be set to 'AS AD'. AS (Default) = Auto Speed during occupied periods. Fan is always on during occupied periods. Low, medium and high speeds operate on temperature offset from set point. AS AD = Auto Speed / Auto Demand during occupied periods. - Medium and high speeds operate on temperature offset from set point. Low speed operates on demand and will shut down when no demand is present. SE8000 controllers On the room controller, select the fan mode parameter from the home screen. The fan mode must be set to Smart in order for the fan output to function as expected. In Smart mode the fan will turn off when there is no demand for cooling or heating. For SmartStruxure applications of the SE8000 controller This issue can also be seen when binding to the "Value field of the Occupancy Command of the SE8000 controller. Make sure to bind to a priority, not to Value otherwise the fan command will not turn off.
View full article
Picard Product_Support
‎2018-09-10 11:22 PM

Last Updated: Sisko DavidChild Sisko ‎2021-09-13 06:52 AM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
7209 Views

MF41 SmartX Damper Actuator Replacement

Issue Replacements for Schneider Electric SmartX MF41 Damper Actuator Product Line Field Devices Environment SmartX MF41 Cause Replacement of SmartX MF41 Damper Actuators within the Schneider-Electric range Resolution Outgoing Actuator Model         Replacement Model (Part Number)        MF41-6083-G00                         MD10B-24 (875 1015 000)      MF41-6083-G02                         MD10B-24 (875 1015 000) + Aux Switch (914 1061 000)      MF41-6153-G00                         MD20B-24 (875 1025 000)      MF41-6153-G02                         MD20B-24 (875 1025 000) + Aux Switch (914 1061 000)
View full article
Admiral David_Kendrick Admiral
‎2021-09-10 01:07 AM

Last Updated: Sisko DavidChild Sisko ‎2021-09-10 01:07 AM

Labels:
  • Field Devices
874 Views

MS41 SmartX Damper Actuator Replacement

Issue Replacements for Schneider-Electric SmartX MS41 Damper Actuator Product Line Field Devices Environment SmartX MS41 Cause Replacement of SmartX MS41 Damper Actuators within the Schneider-Electric range Resolution Outgoing Actuator Model          Replacement Model (Part Number)       MS41-6083-G00                        MD10A-24 (875 1019 000)       MS41-6153-G00                        MD20A-24 (875 1029 000)       MS41-6153-G10                        MD20A-24 (875 1029 000)       MS41-6153-G12                        MD20A-24 (875 1029 000) + Aux Switch (914 1061 000)
View full article
Admiral David_Kendrick Admiral
‎2021-09-10 12:58 AM

Last Updated: Sisko DavidChild Sisko ‎2021-09-10 01:04 AM

Labels:
  • Field Devices
1009 Views

Replacement of Satchwell ZKM series Rotary Actuator due to obsolescence.

Issue Satchwell ZKM series Rotary Actuator requires replacement due to obsolescence. Environment Satchwell ZKM Rotary Actuator installed on Satchwell MBF series Rotary Shoe Valve Body. Satchwell ZKM Rotary Actuator installed on Satchwell MZF series Plug and Seat Valve Body. Cause Obsolescence of Satchwell ZKM series Rotary Actuator Resolution OVERVIEW The Satchwell ZKM Actuator was compatible with both Satchwell MBF series Flanged Rotary Shoe Valve Bodies and Satchwell MZF series Flanged Plug and Seat Valve Bodies, subject to the installation of an appropriate Linkage Kit. Various models of the ZKM Actuator were available, each differing in the number and type of electrical interface provided, enabling the Actuator to be installed in a range of control applications. Interfaces included Transfer Switches, Auxiliary Switches and Feedback Potentiometers, thus resulting in differing wiring connection options between the ZKM Actuator and its associated Controller and other peripherals. Details of the numerous ZKM Actuator variations available may be viewed here. In view of the differing wiring connection options that may be found on site, it is intended to deal only with the most common 6-wire connection option here. Please therefore check the number of wires connected to the ZKM Actuator before proceeding, as this will assist in confirming the suitability of the ZKM Actuator 6-wire connection option replacement suggestion described here.   1. ACTUATOR REPLACEMENT The Actuator comprising a 6 wire electrical connection enabled it to be operated from a Satchwell Z Monotronic or CZT Climatronic Proportional Controller as follows :- Terminal 1 – Open signal Terminal 2 – Close signal Terminal 3 – Common Terminal A – 135 ohm Feedback Potentiometer – winding Terminal B – 135 ohm Feedback Potentiometer – wiper Terminal C – 135 ohm Feedback Potentiometer – winding If all 6 wires are connected then the ZKM Actuator may be replaced either by the Schneider Electric MD20A Actuator or the M800 Actuator, depending on the type of Valve Body to be controlled :- MBF ROTARY SHOE VALVE BODY APPLICATIONS :- MD20A-24 + Linkage Kit LMD-MBF (914-1070-000) Details of the MD20A Actuator may be viewed here Details of the LMD-MBF Linkage Kit may be viewed here N.B. Should the Satchwell ZKM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E MD20A Actuator as appropriate :- MD-S2 - Two independent SPDT 1mA -- 3(0.5)A, 250 V AC Auxiliary Switches. (914-1061-000) Should the Satchwell ZKM series Actuator include a wired Transfer Switch then the following Accessory should also be installed on the S-E MD20A Actuator as appropriate :- MD-S2 - Two independent SPDT 1mA -- 3(0.5)A, 250 V AC Auxiliary Switches. (914-1061-000) Details of the MD-S2 Auxiliary Switch Kit may be viewed here MZF PLUG AND SEAT VALVE BODY APPLICATIONS :- M800 + Linkage Kit L2SV (880-0124-000) Details of the M800 Actuator may be viewed here Details of the L2SV Linkage Kit may be viewed here N.B. Should the Satchwell ZKM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :- S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000) Should the Satchwell ZKM series Actuator include a wired Transfer Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :- S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000) Particular care should be taken when selecting an S-E Forta M800 Actuator to replace an existing Satchwell ZKM series Actuator. The S-E Forta M800 Actuator may be used to replace an existing Satchwell ZKM series Actuator but it should be noted that where this is to be connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single S-E Forta M800 Actuator (50VA) compared to that available at the CZT Controller (10VA) will also be required. (e.g. S-E Transformer Type TR60) Details of the Schneider Electric TR60 Transformer may be viewed here In such installations not only will the ZKM need to be replaced but the associated Proportional Controller will also need to be replaced.   2. PROPORTIONAL CONTROLLER REPLACEMENT The ZKM Actuator was compatible with a number of Satchwell Proportional Controller types including Z Monotronic, CZT Series 1 and CZT Series 3 Z MONTRONIC CONTROLLER APPLICATIONS :- If the Proportional Controller is a Z Monotronic type then this should be replaced by the Satchwell CZT5305 Proportional Controller. The associated Satchwell 3 wire Sensor will also need to be replaced by a S-E 2 wire Sensor compatible with the CZT5305 Details of a compatible Room Temperature Sensor may be viewed here. Details of a compatible Duct Temperature Sensor may be viewed here. Details of a compatible Immersion Temperature Sensor may be viewed here. The replacement Immersion Temperature Sensor may be installed in the existing Immersion Temperature Sensor Pocket with the aid of an Adaptor DWA0001. Details of the DWA0001 Adaptor may be viewed here. Details of the CZT5305 may be viewed here.   CZT CONTROLLER APPLICATIONS :- If the Proportional Controller is a CZT Series 1 or CZT Series 3 type then this should be replaced by the Satchwell CZT5305 Proportional Controller. The associated Satchwell 2 wire Sensor may be retained if desired. Details of the CZT5305 may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 01:48 AM

Labels:
  • Field Devices
5619 Views

MF20-24L XIF and LON files

Issue .xif file not available for download. Product Line Field Devices, Other, TAC Vista Environment MF20-24M 1M54 00 MF20-24L actuator Cause When configuring the MF20-24L in LonWorks, .xif file is necessary.  Resolution All necessary files for LON connectivity are available here: lon_actuator_v3.0 (1).zip
View full article
Picard Product_Support
‎2018-09-11 01:27 AM

Labels:
  • Field Devices
  • TAC Vista
1452 Views

Sensor characteristics for the Satchwell controller type sensors.

Issue Resistance readings Environment Sensor Resistance Chart Type T Cause Resistance Resolution SENSOR CHARACTERISTICS   DRT DOT   DD 1401 DW 1202   DW 1204 DWS 1202   DO 2202 -40 to+40'c     DDT DWT   DR 2253 DWS 1301                 DST DOS                                                 Sontay Type SAT 1   Sontay Type SAT 2   Sontay Type SAT 3   Sontay Type SAT 4                               °C Ohms   °C Ohms   °C Ohms   °C Ohms                               -40 9711   0 2094   20 2708   -40 2317     -35 9604   1 2079   25 2592   -35 2246     -30 9465   2 2063   30 2474   -30 2163     -25 9288   3 2046   35 2346   -25 2067     -20 9067   4 2027   40 2216   -20 1962     -15 8796   5 2010   45 2086   -15 1849     -10 8472   6 1992   50 1950   -10 1733     -5 8093   7 1973   55 1818   -5 1617     0 7661   8 1953   56 1792   0 1504     5 7182   9 1934   57 1766   5 1397     10 6667   10 1911   58 1741   10 1298     15 6126   11 1892   59 1718   15 1208     20 5573   12 1872   60 1694   20 1128     25 5025   13 1851   61 1669   25 1057     30 4492   14 1830   62 1646   30 996     35 3987   15 1809   63 1622   35 942     40 3518   16 1787   64 1600   40 897     45 3089   17 1764   65 1578           50 2702   18 1740   66 1553           55 2358   19 1716   67 1530           60 2056   20 1690   68 1508           65 1792   21 1667   69 1484           70 1563   22 1644   70 1461           75 1364   23 1621   71 1439           80 1193   24 1596   72 1417           85 1047   25 1574   73 1396           90 921   26 1549   74 1375           95 815   27 1524   75 1353           100 722   28 1500   76 1333           105 643   29 1476   77 1312           110 575   30 1452   78 1293           115 517   31 1430   79 1276           120 466   32 1406   80 1258           125 423   33 1383   81 1240           130 386   34 1359   82 1222           135 353   35 1336   83 1205           140 324   36 1312   84 1188           145 300   37 1289   85 1171           150 278   38 1267   86 1154                 39 1243   87 1138                 40 1219   88 1122                 41 1198   89 1107                 42 1176   90 1089                 43 1155   91 1075                 44 1134   92 1061                 45 1113   93 1047                 46 1092   94 1033                 47 1072   95 1020                 48 1052   96 1004                 49 1033   97 991                 50 1013   98 978                       99 964                       100 950                                   Click here to download a pdf with this information.
View full article
Picard Product_Support
‎2018-09-10 05:05 AM

Labels:
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
2732 Views

TC100, TC300 series thermostats models guide

Issue TC series thermostats which one support Modbus protocol? TC series thermostats which one support time schedules? Environment TC100 (TC103) TC300 (TC303, TC353) TC500 (TC503, TC553) Cause Due to different TC thermostats models support different features, customers need to double check the selection guide to make sure the selected model can support all features which are required. Resolution Click here  to view a matrix which contains all TC series thermostats and their supported features. Additional information can be found on the Buildings Business Extranet website (Products > Field Devices Asia Pacific > Thermostats).
View full article
Picard Product_Support
‎2018-09-06 11:34 AM

Labels:
  • Field Devices
2700 Views

Adjusting a Venturi pipe to the correct size

Issue The calectro smoke detektor has too long pipe to fit Environment Calectro Smoke detektor Venturi pipe Cause The Venturi pipe is long, but also possible to cut Resolution You can cut the Venturi pipe to size but you must only cut it from the end that does not have the sleeve. See Installation instruction for more information.  
View full article
Picard Product_Support
‎2018-09-10 01:49 PM

Labels:
  • Field Devices
2593 Views

How is Magnetic Stripe ABA data formatted on a card?

Issue What track is used for ABA data? Environment ABA Magnetic stripe cards and readers. Cause Card format information required. Resolution ABA data is usually stored on Track 2 and requires a track 2 reader to decode the data. ABA Magnetic Stripe Format.
View full article
Picard Product_Support
‎2018-09-11 12:50 PM

Labels:
  • Andover Continuum
  • Field Devices
  • TAC INET
2260 Views
  • « Previous
    • 1
    • …
    • 9
    • 10
    • 11
    • …
    • 36
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore