Replacement of Satchwell "VG" combined Actuator 2-port Valve Body assembly due to obsolescence.
  • Replacement of Satchwell "VG" combined Actuator 2-port Valve Body assembly due to obsolescence.
  • CraigEl
    CraigEl
‎2018-09-10 05:10 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-15 07:28 PM
Satchwell “VG” combined Actuator & 2-port Valve Body assembly requires replacement.
  • Stand alone Satchwell “VG” combined Actuator & 2-port Valve Body assembly
  • VG
  • Actuator
  • 2-port
  • Valve Body
Obsolescence of Satchwell “VG” combined Actuator & 2-port Valve Body assembly.
Replace Satchwell “VG” combined Actuator & 2-port Valve Body assembly with Schneider Electric MD10B Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size.
N.B.
The MB 3-port Valve Body may be converted to a 2-port Valve Body by installing a plug in Port 3
Details of the original Satchwell “VG” combined Actuator & 2-port Valve Body assembly may be viewed here.
Details of the replacement Schneider Electric MD10B Actuator may be viewed here.
Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here.
Details of the replacement Satchwell MB 3-port Valve Body may be viewed here.
N.B.
It is possible that the "VG" Actuator may have been fitted with an Auxiliary Switch.
If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B Actuator if required.
Details of the MD-S1 Auxiliary Switch may be viewed here.
  • Field Devices
  • 6627