CSC 5252 / 5352 - Controller does not switch off.
  • CSC 5252 / 5352 - Controller does not switch off.
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-10 01:52 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-15 09:23 PM
The controller does not follow the programmed on/off times.
Field Devices
CSC
5252
5352
Discrete
Compensators
The flow temperature sensor has failed and is causing the controller to remain on.
As part of it's "Out of Hours" operation, the controller will monitor the flow temperature and if it falls below 5'C, the controller will act to remove the risk of frost by starting the pump and opening the control valve.
For a full description of this function, please refer to the CSC User Guide.
  • Field Devices
  • 6126