Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 171
    • 172
    • 173
    • …
    • 509
  • Next »

Vista 5 multiple license files in license folder

Issue When using TAC Vista 5 Demo License and Site License at the same time, Vista returns “Your application was not able to obtain a license because the FLEXnet license server manager could not determine where to find the licensing data it needs. Please choose one of the following: Specify the License Server System Specify the License File Product Line TAC Vista Environment Vista 5.X.X with Site License and Demo License Cause Using Vista 5 Demo License concurrently with Site Licenses, or having an expired Demo License in the License File folder with Site License may cause Vista ignore the Site License or not fully read the Site License. Resolution Remove Demo License from the License File folder. Restart the computer. If the issue still exists, follow Switching from the Demo license to the site License in Vista 5.1.7 or older.
View full article
Picard Product_Support
‎2018-09-10 12:52 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:11 AM

Labels:
  • TAC Vista
1696 Views

I/A Series BACnet (MNB) UL 864 Listing

Issue What I/A Series BACnet hardware (MNB) is officially UL 864 listed? Environment MNB UL 864 Cause Many consulting engineers would like documented proof that the hardware within a smoke control system is UL 864 tested and approved. Resolution The Schneider Electric MicroNet BACnet UL 864 case file, outlining exactly what I/A Series BACnet hardware is approved for UL 864 systems can be obtained at: www.UL.com Navigate to the bottom of the home page under Useful links and click on Online Certifications Directory Find the UL File Number field and type s5381 The Schneider Electric MNB file will show up and click the link UUKL.S5381 under the link to file column. This will show you all of the I/A Series hardware that is UL 864 certified, and can be installed in an official smoke control system. Also refer to the I/A Series MicroNet BACnet Smoke Control Systems Manual (F-27419) for further information related UL 864 Smoke Control applications.
View full article
Picard Product_Support
‎2018-09-10 12:41 AM

Labels:
  • TAC IA Series
1695 Views

"Access Denied" errors are reported during the re-installation of the Niagara R2 software.

Issue "Access Denied" errors are reported during the re-installation of the Niagara R2 software. Environment Niagara R2 software Cause The files installed in the nre\modules folder are write protected. Resolution If an attempt is made to reinstall Niagara R2 software on a computer, an installation error frequently occurs. The Niagara installer (second installation program) progresses one tick on the progress bar then displays a "Module Install Error" window containing the message "Access is Denied". Clicking the OK button to acknowledge the error results in the message window reappearing multiple times. This occurs because the files installed in the nre\modules folder are write protected when installed. To prevent this problem before attempting to reinstall any release of the Niagara R2 software, Open Windows Explorer ("My Computer") Select all files in the niagara\nre\modules folder Right-click on the selected files Select "properties" from the displayed menu. The Properties window appears.  Clear the mark in the "Read-only" box Click the OK button.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1696 Views

Changing the IP Address in Cyberstation

Issue Site needs to change the IP address in Cyberstation Environment Continuum Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause There is a need to be able to change the IP address in Cyberstation Resolution Shut down Cyberstation Go to the PC's network/LAN/TCPIP connection properties and enter the new static IP address Verify the IP address change by going to Start>Run>Cmd (DOS Prompt) and type Ipconfig/all. The IP address will show under the network card similar to the following: Description . . . . . . . . . . . : Intel(R) 82577LM Gigabit Network Connection Dhcp Enabled. . . . . . . . . . . : No Physical Address. . . . . . . . . : 5C-26-0A-45-7C-D8 Autoconfiguration Enabled . . . . : No IP Address. . . . . . . . . . . . : 192.168.203.2 Subnet Mask . . . . . . . . . . . : 255.255.255.128 Default Gateway . . . . . . . . . : 192.168.203.1   Launch Cyberstation Open the Workstation object using Continuum Explorer (Right click>Edit) Click on the "Teach" button (Distributes the New IP address to the controllers)
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • Andover Continuum
1688 Views

The I/A Series G3 Platform Software Manager indicates "Not Available Locally" when connected to the remote platform (ENC or JACE).

Issue The I/A Series G3 Platform Software Manager indicates "Not Available Locally" when connected to the remote platform (ENC or JACE). Environment I/A Series G3 - All versions Cause Upon start of Workbench, the modules residing in the local Workbench module folder are scanned by the software.  During this process, new and/or updated modules are copied and saved into the local software database.  "Not Available Locally" indicates the associated module is missing from the local Workbench software database.  The following example finds the Installed Version of tacMs at TAC 3.4.64.4 with the Available Version missing with the comment "Not Available Locally." Resolution There are two methods to correct this issue. Method 1:  Copy the module directly into ~\modules directory. This makes the module(s) available in your Workbench environment, and also available to install in other remote platforms.  When the installer runs, the module(s) are also copied into your software database, available for installation. This is the typical choice. Method 2:  Copy the module into your ~\sw\inbox directory (or, use the equivalent “Software Import” feature in the Software Manager). In this case, the module(s) are not used in your Workbench environment, but are available in your software database for installation in remote platforms. If the module is invalid or corrupt, the software manager will generate and place the module in the "failed_imports" folder (e.g. unable to read the manifest files, class files, etc.).  Verify the module is valid. Reference the Niagara AX Platform Guide - Software Manager for additional details.
View full article
Picard Product_Support
‎2018-09-11 01:21 AM

Labels:
  • TAC IA Series
1696 Views

Enable a Sigma controller to broadcast more than 50 globals (bit mask)

Issue How can more than 50 globals be transmitted from a Sigma controller when I have a lot of digital objects states to pass between controllers? Environment Sigma Controller (all) Cause Sigma controllers are limited to 50 broadcast globals. Resolution Up to 16 Sigma Digital objects states can be reference in a single programmable object.  By performing a binary count the various states can be represented by a single analogue value which can then be broadcast as global data. Sigma programmable object MASK command can be used to decode analogue representation of a single analogue value that represents up to 16 digital states (on/off).   For example the value of 901 represents the state of a number of Sigma DI Objects where each bit indicates the on/off.  Hence, this translate to the 16-bit binary value  0000001110000101  where 1 = on and 0 = off To set-up bit masking click here for details. 1.  Create a program object in the transmitting controller that 'binary' counts up to 16 digital objects. 2. In the receiving controller create up to 16 programmable objects to decode the transmitted analogue value.  e.g
View full article
Picard Product_Support
‎2018-09-07 08:23 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:08 AM

Labels:
  • Satchwell BAS & Sigma
1689 Views

Only receive one Email notification per alarm

Issue An alarm goes on and off several times in a short amount of time. Each time the alarm condition clears and reasserts itself, by default, another email will be sent. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation SMTP alarms Cause Every time an alarm goes off, the email notification checks its parameter and, if true, sends an email. Resolution Filter the email notification by "count." Set it to "from 0 to 1" and you will only get a email on the first alarm (count).
View full article
Picard Product_Support
‎2018-09-06 09:30 AM

Last Updated: Captain SharlinaRe Captain ‎2022-08-19 07:54 AM

Labels:
  • EcoStruxure Building Operation
1695 Views

Can TAC BACnet (Viconics) thermostats have identical names and deviceids within sub networks using their default names?

Issue Can TAC BACnet (Viconics) thermostats have identical names or device ids within sub networks using their default names? Product Line Andover Continuum, EcoStruxure Building Operation Environment Viconic BACnet Thermostats BACnet BCX B4 MSTP Cause Viconic stats need a unique address and unique name across the entire BACnet network. Resolution BACnet Viconics thermostats must have a unique name and device id across the entire BACnet network. The BACnet data link layer has two key parameters: the device object name and the device object ID. The device object name must be unique from any other BACnet device object name on the BACnet network (i.e. not just the MS/TP sub-network). Typically this question comes up because a thermostat will not come online. Run an acctrace during the Find and you will probably see a duplicate MAC address. Once you have given unique names and comm addresses to each of the thermostats on the entire BACnet network, these devices should communicate and come online properly. Each of the Viconic stats are given a unique name that includes the address (once it has been made unique) To change the communication address: Hold down the menu button until the option for menu comes up Answer the questions for the various options and eventually you will be brought to change comm address. Change Comm address, select Yes and then use the up or down arrows to give this MSTP Viconic stat a unique address. There is a Configuration Tool to access and edit the name and device id unique naming scheme. Click here for ViconicsConfigurationTool.zip. Installing and using the Viconics Configuration Tool on a Windows Laptop  You will need a serial adapter connection to tie into the MSTP bus that the thermostat(s) are connected to Select the Viconics folder > ViconicsConfigurationTool.zip You can install this ZIP file in any directory you wish, but the bacdocm.ini file must be installed on your C:\Windows directory. Use the bacdocm.ini file to configure your network settings at the Configurator Tool level. You can set the MAC address of your tool, the baud rate of your connection (max 38400 - limited by the RS-232 to RS485 port and Windows) etc. The "Our Device Instance" value represents the MAC address of the tool which must be unique on the MSTP network. Also the "MaxMaster" value must be set to a higher value than the highest MAC value on the MSTP network. You can edit this INI file to modify your settings OR you can modify the settings by going though the BACdoor Configuration Tool. Once you launch the Configuration Tool, you'll notice a white applet appearing at the right bottom of your screen. That is the BACdoor MSTP sniffer that actually looks for devices and objects. If you click on that icon, and select the "Configure" tab, a configuration window will be displayed. Select the baud rate at which you want to communicate with your device. This BACdoor configuration does the same thing as changing the BACDOCM.ini file (if properly located in C\Windows). Launch the Configurator Tool application. It automatically looks for devices on that network (at the baud rate set in the bacdocm.ini file or in the BACdoor Configuration window). If no device is detected an error message will pop-up after 1-2 minutes. All discovered devices will show up in the "Device List" you have to "Connect to device" in order to list all the objects of that device. After you changed the Baud Rate, you have to click on the "Apply changes" button. Don't forget that the max speed of this tool is 38400. For the first connection, you need to power cycle the thermostat (if it was running at 76800 previously) so that it auto-detects the 38.4 network. Once you set it to 76.8, you can not connect to that thermostat with the tool because of that 38.4 limitation. Also this tool does not support Read Multiple Property so it reads every property of every object one at a time. In its default mode of operation, the device will automatically match its baud rate to the baud rate of the network. Automatic baud rate detection will occur when the MS/TP communication port is initialized (on power up). If the network speed is changed, the device will keep listening at the previously detected speed for 10 minutes before resuming auto-bauding. Re-powering the devices will force right away auto-bauding. SE7xxx series requires the tool. The SE8xxx series does not as access is available through the menu on the device.
View full article
Picard Product_Support
‎2018-09-07 12:48 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:09 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1691 Views

Unable to bind programming or points in the AS to control LCM blocks

Issue Programming or points in the AS can not be bound to control LCM blocks. Product Line EcoStruxure Building Operation Environment AS Network 8000 interface Cause The AS Network 8000 interface replicates the function of a GCM and a GCM's blocks are not able to link directly to LCM blocks. Resolution The AS Network 8000 interface replicates the function of a GCM. As such the LCM blocks in the AS can be monitored, manually commanded and bound to share within the AS, but cannot be bound to AS points or logic for control. This is as it would be with an actual GCM and the LCM's connected to it. As with the GCM, the SGCM block is available in the AS and can be used to send data in the AS to the LCM for use in the LCM's logic. The LCM must contain the RGCM block and the use of the data received is determined in the LCM logic.
View full article
Picard Product_Support
‎2018-09-06 09:29 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-15 07:00 AM

Labels:
  • EcoStruxure Building Operation
1691 Views

Grayed out fields in the basic alarm tab on BACnet b3 controllers

Issue Alarms cannot be created in a BACnet b3 controller because the fields are grayed out. Product Line Andover Continuum Environment Continuum Cyberstation b3 BACnet MS/TP controllers Cause Alarms are created differently in a BACnet controller than with an Infinet controller.  These fields are grayed out since they are not used for alarm creation in a BACnet controller. Resolution There are instructions in the BACnet section in the Continuum help for creating an event notification and then mapping the point and the event notification within an alarm enrolment. For an example see AlarmCreatingAndConfiguring BACnet.doc
View full article
Picard Product_Support
‎2018-09-09 09:49 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM

Labels:
  • Andover Continuum
1686 Views

UI inputs of the MNB-1000 do not support pulse inputs

Issue Do the universal inputs (UI) of the MNB-1000 support pulse inputs? Product Line TAC IA Series Environment MNB-1000 Cause Attempting to wire a pulse input to a UI on the MNB-1000 can cause issues. Resolution The UI inputs of the MNB-1000 do not support pulse inputs and can not be used for this purpose.  The digital inputs (DI) of a MNB-1000 do support pulse inputs. Pulse Input Rate Minimum rate of 1 pulse per 4 minutes Maximum rate of 10 pulses per second  
View full article
Picard Product_Support
‎2018-09-06 01:18 PM

Labels:
  • TAC IA Series
1682 Views

"No entries in data base" when attempting software restore

Issue Edit > Host Computer > Software Restore results in pop-up error "No entries in data base" Product Line TAC INET Environment I/NET Seven host Cause The network configuration does not have any entries saved in the database. Resolution Go to Edit > Host Computer > Network Configuration In the Link Summary window, find the correct Link. If the Cnf column has a plus sign (+) in it, then this link is not saved. If the correct link is not shown, reference Error: "No Entries in Database" for more information. Highlight the correct link and press "Save" With the correct link highlighted, click "Penetrate" Any controller with a + in the Cnf column has not been saved. Click "Save All" Hit "Close" on the Station Summary and "Close" on the Link Summary. There are now entries in your database. The software restores should now show the correct options. For instructions on performing a software restore, see How to upgrade bin and SAV files in I/NET controllers
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:31 PM

Labels:
  • TAC INET
1683 Views

Backup feature in function block programming

Issue All setpoints are lost after a power outage and the function block programs revert back to initial value. Environment Menta Function Block Editor Menta Editor Xenta 280/300/400 Controllers Cause A Menta, Menta Editor, or Function Block Editor program with configurable setpoints will be lost if the default programming settings are used and there is a power loss. Resolution Backup feature in function blocks Menta and Menta Editor When the Backup check box is selected, the current value of the block output and internal states in the RAM are used when the device makes a warm start. Otherwise, the block output and internal states are reset to their initial values (same as for a cold start) at a warm start if the Backup box is not checked. If a power outage lasts longer than the power failure protection time for the device and the RAM contents are lost, the restart is a cold start. All blocks will be rest to their initial states regardless of the Backup option. The RAM working member that includes current values will last for 72 hours without power. Function Block Editor When the Backup check box is selected, the current value of the block output and internal states in the RAM are used when the device makes a warm start. If a power failure occurs, all important variables are automatically saved to the flash memory before complete shutdown. When power returns, this data retention function ensures that the Automation Server can continue to run with the correct set of values.
View full article
Picard Product_Support
‎2018-09-11 07:34 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1681 Views

Modbus communication with LC&D GR2400 lighting controller

Issue Unable to get modbus to communicate with the automation server and LC&D GR2400 lighting controller. Environment Modbus Automation server LC&D GR2400 SmartStruxure Solution 1.5 Cause The LC&D GR2400 lighting controller will ONLY allow 1 stop bit in it's modbus communication. Normally the stop bit setting in a modbus slave device is an "at least number", meaning the GR2400 should except 1 or more stop bits, but it does not. The problem comes from the automation server by  default sends the 1 stop bit and addition "guard bits" for modbus communication. The guard bit setting was not available in versions prior to 1.5 and by default the automation server would send 3 stop bits causing the modbus communication to fail with the GR2400lighting controller. Resolution In SmartStruxure 1.5 right click on the Modbus Master Network and select properties. Click the advanced tab:         3. Here you see the guard bit setting. This value should be a 0 if the automation server is to ONLY send 1 stop bit. If this number is left at default the automation server will add the number of guard bits to the user       setting of stop bits. By default that makes 3 stop bits from the Automation Server. To properly communicate to the GR2400 the guard bit setting should be a 0 and the user selected stop bit should be a 1 in order to ONLY send 1 stop bit.
View full article
Picard Product_Support
‎2018-09-11 07:56 AM

Labels:
  • EcoStruxure Building Operation
1755 Views

lc_checkout failed: Cannot checkout an uncounted license within a Windows Terminal Services guest session.

Issue Vista 5.1 license is not working.  Trying to launch Vista components results in error:  lc_checkout failed: Cannot checkout an uncounted license within a Windows Terminal Services guest session. Environment Vista 5 Terminal Services Virtual Machine VM Cause There is a special feature needed in the license which allows the use of Terminal Services. Resolution You must download the 14 day Demo TS Evaluation License on The Exchange Download Center. *note that Terminal Services are only supported in Vista 5
View full article
Picard Product_Support
‎2018-09-07 03:55 AM

Labels:
  • TAC Vista
1696 Views

Bacnet object rejected generated in response to a confirmed request... when creating a schedule

Issue Creating a bacnet schedule to control a 3rd party device generates the error:  “Bacnet operation rejected generated in response to a confirmed request apdu in which the service choice field specifies an unknown or unsupported service”  Environment Continuum 3rd party bacnet device Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause The bacnet error occurs when dynamic creating of schedules is not supported in the 3rd party device and the packet gets rejected. Resolution An ethereal capture from the Cyberstation will show the packet getting rejected. A work around for this is to use a BCX to create the schedule and communicate to the 3rd party device.
View full article
Picard Product_Support
‎2018-09-06 01:56 PM

Labels:
  • Andover Continuum
1758 Views

Date and time gets incorrect periodically in TAC Xenta Programmable controllers, all time settings correct in TAC Xenta

Issue Date and time gets incorrect periodically in TAC Xenta Programmable controllers Time stamp in alarm list is incorrect Time stamp in alarm list is wrong  Vista Server local time and the local time in all Xenta controllers in the network go out of synch.   All local time settings are correct in TAC Xenta Environment TAC Xenta 30x/401/28x Cause The time in a TAC Xenta can be changed by TAC Vista TAC OP, note that a change of the time in one controller is broadcasted to the whole network. TAC Xenta group master will broadcast the time to it's group every 24 hours A Xenta Server (Xenta7xx, Xenta5xx, Xenta 913) Menta, this only affects the controller Menta is connected to. Most likely, the problem is a Xenta Server in the network that has the wrong time. It can be enough that a Xenta server is connected to the network, it does not have to be configured in this network.. Resolution Log in to Xenta server from the web interface. Go to Configuration-time If the date and time is incorrect set the correct date and time. Click on time synchronization, the lonworks time synchronization should only be set to enable  if this is a Xenta Server in TAC Vista or if this is a site that does not have TAC Vista on it and it is the only source to sync the time to.
View full article
Picard Product_Support
‎2018-09-06 02:12 PM

Labels:
  • TAC INET
  • TAC Vista
1681 Views

Vista Server start hangs on trend log initialization

Issue When starting the Vista Server, the splash screen displays the current state of the startup.  It gets to the "Trend Log Initialization" screen and then hangs. Product Line TAC Vista Environment Vista Server Cause Queued files in the $queues folder in the Vista database are being written to the SQL database.  If the queued files folder has grown very large, it can take a very long time (hours) to write this data to SQL.  If the connection to the SQL database has been broken, then it will take an infinite amount of time. Resolution Check for queued files in the $queues folder Navigate in a Windows Explorer window to the Vista Database. (If you are unsure of the location, you can verify it in the TAC Vista Server Setup Vista Database tab). Go to the $queues folder Look inside the insertevents and insertlogvalues folders. This is where data is stored temporarily before it is written to the SQL database. Having queued files is not necessarily a sign of a problem. However, if there is a connection problem, these folders will continually grow in size without older queued files being written from the folder. Allow time for the files to write the SQL Start Vista Server. Insure that TAC DSS Writer Service is running. When it gets to trend log initialization, leave the PC alone and allow time for the files to write to the SQL server.  If the size of the $queues folders are shrinking, then the process is working and after enough time, the server will start. Note: If you have cleared the $queues folder but it still hangs on trend log initialization, still allow plenty of time for the server to come up. There is a good chance that the Xenta controllers are passing all of their trend logs over to the SQL server. This could take hours or even overnight to complete. Delete the queued files If the data is not of dire importance, delete all the files inside both of the $queues folder.  For an efficient method for deleting many queued files, see An efficient method for deleting all queued files in the $queues folder. Check the SQL connection Open the TAC Vista Server Setup In version 5.1.3 and prior: Start > Programs > TAC > TAC Vista Server X.X.X > Server Setup In version 5.1.4 and later: Start > Programs > Schneider Electric > TAC Vista Server X.X.X > Server Setup Go to the SQL Server tab In the lower right-hand corner of the tab, press the Test Connection button. If it pops up a window that says "Connection test succeeded!" then your SQL connection is okay. If it fails the connection test, check the instance name. If you are using default settings it should be: SQL Server name: PCname\TACVISTA or (local)\TACVISTA Log database name: taclogdata If these are set correctly and the connection still fails, one method for reestablishing the connection is to uninstall/reinstall the Vista software. Remove TRL files This can also occur if the database has been upgraded from a lower versions, and still has information in the TRL files in the database. Stop the server Locate all TRL files in the $thisfil folder Delete any TRL file over 32Kb. Start the server again.
View full article
Picard Product_Support
‎2018-09-07 08:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:13 AM

Labels:
  • TAC Vista
1677 Views

Implement temperature sensor and override on two wires of an STR-104 to a Xenta Programmable

Issue An STR-104 can be used to monitor space temperature with a Xenta programmable controller. If a zone override is also required, the most straight-forward solution is to wire the override button to a digital input on the same controller. However, if those wires were not installed, or sufficient inputs are not available on the controller, the override button can be sent via the temperature sensor wires. Environment STR-104 Xenta programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause If enough wires were not run, or sufficient inputs are not available on the controller, the override button can be sent via the temperature sensor wires. Resolution The override signal sent via temperature sensor wires is accomplished by shorting the temperature sensor reading to ground. The Menta application senses this short and interprets it as a zone override. On the STR-104, short terminals 12 to 14 (Therm to Switch) On the STR-104, short terminals 11 to 15 (M to MX) Terminals 11 and 12 on the STR-104 go to M and B1 on a Xenta programmable (for example). Download this Menta macro for use in the programmable Menta application. While the button is pressed, the temperature will jump to a failed-shorted value of 300+ °F.  The attached Menta app will read in this jump, filter it out from a failed sensor, and enable an override for an adjustable duration.
View full article
Picard Product_Support
‎2018-09-06 01:21 PM

Labels:
  • TAC Vista
1694 Views

Smart Sensor Availability / Obsolescence

Issue What TTS-SD-LED and TTS-SD-LCD Smart Sensors are available? Environment TTS-SD-LED Series • TTS-SD-LED-1 • TTS-SD-LED-B-1 TTS-SD-LCD-Series • TTS-SD-LCD-1 • TTS-SD-LCD-4-2 • TTS-SD-LCD-B-1 • TTS-SD-LCD-C-1-10P • TTS-SD-INFBUF Cause Some products in this range have become obsolete due to the discontinuation of some key components. Resolution Full details are on the attached Product Announcement PA-00171 TTS-SD-LED-1 Discontinued TTS-SD-LED-B-1 Discontinued TTS-SD-LCD-1 Modified TTS-SD-LCD-4-2 Modified TTS-SD-LCD-B-1 Replaced by TTS-SD-LCD-1 TTS-SD-LCD-C-1-10P Discontinued TTS-SD-INFBUF Discontinued
View full article
Picard Product_Support
‎2018-09-11 01:28 AM

Labels:
  • Andover Continuum
  • Field Devices
1691 Views
  • « Previous
    • 1
    • …
    • 171
    • 172
    • 173
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of