Configure a 7740 to read a 4-20ma input
  • Configure a 7740 to read a 4-20ma input
‎2018-09-07 12:57 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:36 AM
Can a 7740 read 4 to 20 milliamp input?
I/NET site
Some sensors will only output a 4-20ma signal and the controller must be able to read it in order to display the sensor values.
Although the controller is calibrated to read 1 to 5 volts, a voltage sensing resistor can be added to read 4 to 20 milliamps. Refer to TCON 092 for details.
  • TAC INET
  • 1585