Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 486
    • 487
    • 488
    • …
    • 509
  • Next »

Adjusting the size of a text field on a monitoring tab may cause the dashboard to freeze

Issue Dashboard may freeze when adjusting a text field smaller than the content on a monitoring tab  Environment Windows 7 Cause Earlier versions of firmware in the MPM may have this condition Resolution Upgrade from version 2.8 to version 2.10 in the MPM
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • EcoStruxure Building Expert
1165 Views

Sigma - Integrated Controller (IC-Lon), objects show default values.

Issue IC-Lon objects show default values. Environment IC-Lon Defaults Default values Sleep Cause The IC-Lon controller works normally for a varying period of time, before default values are displayed. Resolution The IC-Lon has a number of limitations, and one of these is the number of output SNVT's used, and the frequency of the heartbeats used. When configuring the gateway.txt file for the IC-Lon ensure that all NVO's have their heartbeat settings set to an acceptable maximum value, and that the settings used vary. By default the NVO 's heartbeat value is set to 300 seconds, these should be changed to the acceptable maximum
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • Satchwell BAS & Sigma
1079 Views

Modbus RTU Annex points do not operate correctly with the special function codes

Issue When using a Modbus RTU block reads with a special function code incorrect data can be seen. Environment Modbus RTU X Driver All controller types that support X Drivers Cause The Modbus RTU X Driver does not support the use of block reads (annex points) for the special function codes. Resolution The Modbus RTU XDriver supports special function codes to convert various (Non Modbus standard) data formats for use in Continuum points. As detailed in the Modbus RTU X Driver manual (Param6) function codes, Parameter 6 should not be entered for Function codes 241 to 254. A separate X Driver point is required for each value to be read when using a special function code.
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • Andover Continuum
1466 Views

CNT block in the Function Block Editor is replaced by the PI block.

Issue CNT block in the Function Block Editor is replaced by the PI block. How to set up a pulse counter input in a function block program Environment StruxureWare Building Operation Workstation Function block editor Cause Differences between the regular Menta and the Builder Function Block editor programming Resolution The CNT block is replaced by the PI (Pulse input) block in the function block editor. In Workstation, connect the PI to a input where the sensor type is set to counter.
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • EcoStruxure Building Operation
1724 Views

Save schedule failed and get error "An attempt to write property has failed because not enough dynamic memory space exists in the addressed BACnet Device"

Issue The schedule works well for a long time, when save the schedule after edited, the error pops up ,"An attempt to write property has failed because not enough dynamic memory  space exists in the addressed BACnet Device" Environment Continuum BCX1 b3 devices Cause "Clear past events" is not checked in the schedule objects, the past events are kept in the controller and occupy a lot of dynamic space. Resolution Delete the schedule and  create an new one with the same configuration as  the original one Check "Clear past event " in the schedule objects to avoid the same issue happening again
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • Andover Continuum
1342 Views

Can the setpoints on a SE7600 Room Controller be locked out on the keypad so no one can modify it?

Issue Can the setpoints on a SE7600 Room Controller be locked out on the keypad so no one can modify it? Environment SE7600 or VT7600 room controllers Cause Design feature Resolution There are three keypad lockout levels: 0 = Full access to both occupied and unoccupied setpoints 1 = Temporary override capability for both occupied and unoccupied setpoints 2 = No access to both occupied and unoccupied setpoints Review the engineering guide specifications at www.viconics.com.
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • TAC IA Series
1199 Views

Does the MNL controller line have any built-in surge protection for main AC power?

Issue Does the MNL controller line have any built-in surge protection for main AC power? Environment MNL controllers Cause Design specification Resolution No main AC power surge protection is part of the MNL controllers' design.  It will have to be externally applied.
View full article
Picard Product_Support
‎2018-09-06 09:40 AM

Labels:
  • TAC IA Series
885 Views

Maximum load on MPM-UN analog Output

Issue What is the maximum load on MPM-UN analogue Output? Environment MPM-UN SmartStruxure™ Lite Multi-Purpose Manager Cause Avoid overload on output ports Resolution The analog output ports has a maximum nominal load of 50mA each.
View full article
Picard Product_Support
‎2018-09-06 09:40 AM

Labels:
  • EcoStruxure Building Expert
1054 Views

DDE won't work when running Vista as a service

Issue DDE won't work when running Vista as a service Environment Windows 2008 Server or Windows 7 Vista server communication with a device or application via DDE (Dynamic Data Exchange) Cause Applications and services no longer run under the same session in Windows 2008 server or Windows 7. Resolution Run Vista as an application.
View full article
Picard Product_Support
‎2018-09-06 09:40 AM

Labels:
  • TAC Vista
1187 Views

Internal time schedules in SE8000 series devices

Issue Internal time schedules in the SE8300 and other 8000 series room controllers. Environment Schneider Electric SE8xxx Cause As of the time this article is being written these devices are intended to be controlled by a network management controller or using contact closure on the device. However, some sales documentation states that these devices have "7 day occupancy scheduling (2-4 events)". This documentation was released prematurely and, although future models will have this capability, as of March of 2014 the current models do not. Resolution Currently occupancy of the SE8xxx devices can be controlled by a network variable over the Lon, BACnet or ZigBee network. Alternatively, occupancy can be controlled by configuring the device for contact closure control of occupancy. Future model series SE8xxx devices will support scheduling. Note, however, that it will not be possible to upgrade older devices to support scheduling since the hardware will also be changed.
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • EcoStruxure Building Expert
1380 Views

What are the cable specifications for wiring controller inputs to field devices.

Issue What are the cable specifications for wiring controller inputs to field devices. Environment Inputs Cable Sensors End devices Cause There is no specification for IO field wiring.   Resolution The line drop produced by cable resistance should be taken into account when choosing the wire gage for Input devices. It is good practice to run a shielded cable for analog inputs simply because it give you a way to drain off any externally induced voltage.
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • Andover Continuum
1070 Views

Value does not change as the referenced point in a different BCX1 updates

Issue Need to reference the outside temperature and humidity under another BCX1, but the value does not change as the referenced point changes. The program is running. The program code is as below: Line 1 Temp_Outside= NetworkA\BCX1_2\Temp_outside line E state=enabled goto 1 The result is : The value of Temp_outside does not change to equal the value of NetworkA\BCX1_2\Temp_outside Environment Continuum BCX1 B3 Cause A difference between the two BCX1s. The object type of the two points is not compatible. Resolution Correct the submask setting to make sure they have the same submask exactly Correct the object type to make sure they are compatible with each other
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • Andover Continuum
1013 Views

Power Failure on MPM, the clock goes back to 1/1/2000.

Issue Each time that a power failure happens on a sites MPM, the clock goes back to 1/1/2000. Environment StruxureWare Lite MPM Cause This is most likely due to the battery shelf life, this happens if the controller was purchased and left unused for over 5 months before being installed. Resolution ∙ BR1220 from Panasonic (Lithium Carbon-Monofluoride) ∙ nominal voltage 3V ∙ Capacity 35mAh ∙ Self-discharge 1%/year, under standard conditions ∙ Operating temperature range -30°C to 85°C Units manufactured after week 13 2016 have a super capacitor rather than a battery. The capacitor has a charge time of approximately 5 minutes after which it will provide backup for the RTC for approx. 48 hours
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • EcoStruxure Building Expert
892 Views

Values on graphic pages constantly showing 'down' momentarily

Issue Values on graphic pages constantly showing 'down' momentarily The following message can be seen in the standard output. "duplicate server session kills" Environment I/A Series R2 Enterprise Server Cause There is another copy of the same Enterprise Server station running on the network. In this particular case, there is a another computer on the network that has been licensed as an Enterprise Server and it has a copy of the Enterprise Server station. This computer is meant as a standby computer and the Enterprise Server station should not be running.  Resolution In this particular case, there is a another computer on the network that has been licensed as an Enterprise Server and it has a copy of the Enterprise Server station. This computer is meant as a standby computer and the Enterprise Server station should not be running.  Stop the Enterprise Server station that is running on the standby computer. From the Admin Tool, connect to the localhost and right click on the Enterprise Server station. Make sure auto run is uncheck. 
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • TAC IA Series
1587 Views

When exporting a c2g file, the "Save As" window does not appear

Issue When exporting a c2g file, the "Save As" window does not appear Environment SmartStruxure Lite Cause When exporting a C2g file, the "Save As" window does not appear  Resolution For Firefox ensure the ESR (Extended Support Release) version is installed. Update / Install the latest release of Adobe Flash Player
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • EcoStruxure Building Expert
980 Views

Niagara G3 Fails To Send Alarm Emails. Email Are Discarded with Null Pointer Exception

Issue Niagara G3 station fails to send out emails and discards to the email with this error message: "BOutgoingAccount could not dequeue in-memory email: null" Environment Niagara G3 (AX) ENC and ENS stations (all versions) Cause After watching the output with debug turned on, the station connects to the email server and authenticates. When it tires to send out an email there is a null pointer exception and it discards the email. There is a trailing semicolon in the To Field of the EmailRecipient under Alarm Service. The email handler is looking for another email address after the last semicolon and sees a null when trying to add the last non-existent email address.   Resolution Remove the trailing semicolon.  
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • TAC IA Series
3655 Views

Vulnerability Reported for SSL of Xenta Server by Security Software

Issue Some security software will report that there are vulnerabilities for SSL of Xenta Server. Some vulnerabilities look like: SSL Server allow anonymous authentication vulnerability SSL Server allow Cleartext communication vulnerability  Weak encryption model Environment Vista I/NET Cause This is how Xenta Server designed to work. Resolution There is a security enhancement for Xenta Server in Xenta 5.1.9. Update the firmware to Xenta 5.1.9 will fix these vulnerabilities. You can download Xenta 5.1.9 from Buildings Download Center.
View full article
Picard Product_Support
‎2018-09-11 07:07 AM

Labels:
  • TAC INET
  • TAC Vista
1217 Views

Xenta 913 is Locked Up Randomly

Issue Xenta 913 is locked up randomly, and it needs reboot to make it return to work. When referring to the error log on the web page, the following errors show up: event power PowerFail 1 System is safely shutdown (Error#:49154) event power InitSYS 1 System start - power on (WARMSTART) (Error#:49156) Environment Xenta 913 BACnet Cause Possible cause is the baud rate for BACnet communication is too high that Xenta 913 can't deal with it properly. Resolution It is recommended to decrease baud rate for BACnet communication to 9600 or 19200 bps, and then Xenta 913 should work fine now.
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
1171 Views

Replacement actuator for M52L on V354 / V355

Issue M52L is obsolete and needs to be replaced. Environment V354 V355 M52L MC52A MC52B Cause Replacement of obsolete actuator.  Resolution   The M52L on a V354 or V355 is replaced by MC52A or MC52B: -MC52A , part no 8532221010, modulating control -MC52B-24, part no 8532320000, 24V, Inc/Dec -MC52B-230, part no 8531320000, 230V, Inc/Dec  These part numbers does also include an adapter ring that needs to be used when mounted to the V354 or V355 valves. Please note that the suggested replacement actuators listed above does NOT carry a 16V output. If this feature is required, an external 16V supply must be provided.
View full article
Picard Product_Support
‎2018-09-06 09:38 AM

Labels:
  • Field Devices
1441 Views

How many MTN880451 and MTN880541 could be supplied by the Power Supply MTN884019?

Issue How many LON Bus Coupling Unit MTN880451 and LON Multi-Sensor LA-21 MTN880541 could be supplied by the Power Supply MTN884019? Environment Schneider Electric Lighting Cause Both MTN880451 as well as MTN880541 has a power consumption about 285 mW, that gives about 7 mA. The power supply MTN884019 could give 1.3 A used with 230 Volt or 1 A used by 115 Volt, so it is more than the number of devices you could have on a segment that are important.   Resolution Both MTN880451 as well as MTN880541 has a power consumption about 285 mW, that gives about 7 mA. The power supply MTN884019 could give 1.3 A used with 230 Volt or 1 A used by 115 Volt, so it is more than the number of devices you could have on a segment that are important. If you use LinkPower, you theoretical have up to 128 devices, but if you also have FTT devices, these should be counted twice, so 20 LPT and 15 FTT devices should be counted as 50. It is a recommendation to stay below 64 devices on one segment.  
View full article
Picard Product_Support
‎2018-09-06 09:38 AM

Labels:
  • TAC Vista
1258 Views
  • « Previous
    • 1
    • …
    • 486
    • 487
    • 488
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of