Save schedule failed and get error "An attempt to write property has failed because not enough dynamic memory space exists in the addressed BACnet Device"
  • Save schedule failed and get error "An attempt to write property has failed because not enough dynamic memory space exists in...
  • RobertAndriolo
    RobertAndriolo
  • YangboLIU
    YangboLIU
‎2018-09-06 09:41 AM
The schedule works well for a long time, when save the schedule after edited, the error pops up ,"An attempt to write property has failed because not enough dynamic memory  space exists in the addressed BACnet Device"
Continuum
BCX1
b3 devices
"Clear past events" is not checked in the schedule objects, the past events are kept in the controller and occupy a lot of dynamic space.
  1. Delete the schedule and  create an new one with the same configuration as  the original one
  2. Check "Clear past event " in the schedule objects to avoid the same issue happening again