Value does not change as the referenced point in a different BCX1 updates
  • Value does not change as the referenced point in a different BCX1 updates
  • YangboLIU
    YangboLIU
‎2018-09-06 09:39 AM
Need to reference the outside temperature and humidity under another BCX1, but the value does not change as the referenced point changes. The program is running.
The program code is as below:
Line 1
Temp_Outside= NetworkA\BCX1_2\Temp_outside
line E
state=enabled
goto 1
The result is : The value of Temp_outside does not change to equal the value of NetworkA\BCX1_2\Temp_outside
  • Continuum
  • BCX1
  • B3
  1. A difference between the two BCX1s.
  2. The object type of the two points is not compatible.
  1. Correct the submask setting to make sure they have the same submask exactly
  2. Correct the object type to make sure they are compatible with each other
Tags (3)
  • 15824
  • changed
  • sunmask