Modbus RTU Annex points do not operate correctly with the special function codes
  • Modbus RTU Annex points do not operate correctly with the special function codes
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
‎2018-09-06 09:41 AM
When using a Modbus RTU block reads with a special function code incorrect data can be seen.
Modbus RTU X Driver
All controller types that support X Drivers
The Modbus RTU X Driver does not support the use of block reads (annex points) for the special function codes.
The Modbus RTU XDriver supports special function codes to convert various (Non Modbus standard) data formats for use in Continuum points.
As detailed in the Modbus RTU X Driver manual (Param6) function codes, Parameter 6 should not be entered for Function codes 241 to 254.
A separate X Driver point is required for each value to be read when using a special function code.
Tags (2)
  • 15677
  • multiple