Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 480
    • 481
    • 482
    • …
    • 508
  • Next »

How does the controller-resident schedule work in a Revision 11.x MicroSmart controller?

Issue How does the controller-resident schedule work in a Revision 11.x MicroSmart controller? Environment MicroSmart controllers revision 11.x and 10.x Cause Main DMS panel and/or NC panel were removed. Resolution With the loss of schedule control from the DMS or NC, each controller has two built-in schedules numbered 1 and 2. The Start/Stop point requiring a schedule can be assigned either one of these schedules followed by a letter A or letter B. Letter A stands for 'always' and letter B for 'backup'. With no DMS or NC present, enter the schedule as 1/A or 2/A.  Assign 'off' and 'on' times as required. Remove any reference to a DMS or NC schedule number (i.e. set it to a value of 00). 
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • TAC IA Series
783 Views

Analog inputs on a MicroSmart controller are all reading a negative value.

Issue Analog inputs on a MicroSmart controller are all reading a negative value. Environment MicroSmart controllers (all versions) Cause Hardware issue or sensor failure Resolution If the connected sensor is a RTD, a negative reading reflects an electrical short somewhere between the controller and the sensor.  Note that a high positive reading reflects an electrical open circuit. If the connected sensor is a 4-20 mA device, it typically reads a high positive value which reflects an electrical open circuit.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • TAC IA Series
851 Views

Accessing WorkPlace Tech help files in Internet Explorer 11

Issue The drop down menu to select WorkPlace Tech help manuals does not function in Internet Explorer 11. Environment WorkPlace Tech 5.8.6 Internet Explorer 11 Cause Internet Explorer changes how they handle compatibility mode for websites and webpage used to access the help files requires updating in a new version of WorkPlace Tech. Resolution Use one of the following options to access the help files Access them directly by going to the folder they are stored. On a Windows 7 (64 bit) operating system this is C:\Program Files (x86)\WorkPlace Tech\Help by default. Modify the index.htm, BACnet.htm, LON.htm, search.htm, Sensors.htm, and Software.htm files found in the C:\Program Files (x86)\WorkPlace Tech\Help\bin directory. Add the following line in front of the first "meta http-equiv=" line:   <meta content="IE=EmulateIE8" http-equiv="X-UA-Compatible" />   <meta content="IE-EmulateIE8" http-equiv="X-UA-Compatible" />
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
947 Views

Webstation and Xenta Server web interface, text size is too large in TGML graphics

Issue Font size is very large in Xenta Server and Webstation TGMLs, both in the web interface and when viewing from Vista Text in TGML graphics is too large, it word wraps when it shouldn't Environment TAC Xenta 700 TAC Xenta 511 TAC Xenta 527 TAC Xenta 555 TAC Vista TAC Vista Webstation Cause Windows Font Size is set to more than 100%. It has been found set to 125% as default on some PCs. Resolution In Windows 7 and 2008 Server: Goto Control Panel -> Appearance --> Display Click "Smaller - 100%" option and then apply settings The font in TGMLs should now display normally
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • TAC Vista
1341 Views

Acknowledge alarms from HMI

Issue Is it possible to acknowledge an alarm from a third party HMI? Environment StruxureWare Building Operation Cause The only way to acknowledge an alarm in SmartStruxure is via the Workstation/Webstation or EcoStruxure Web Service. Resolution The only way to acknowledge an alarm in SmartStruxure from a third party HMI is via EcoStruxure Web Service.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • EcoStruxure Building Operation
1582 Views

How often is a SNVT in a Lon device polled if an alarm monitors that variable?

Issue How often is a SNVT in a Lon device polled if an StruxureWare Building Operation alarm monitors that variable? What happens if a shunt variable is used - is the polling rate still the same? Environment Lon Device StruxureWare Building Operation Cause Alarms are to monitor SNVTs in a Lon device put polling may overload the network. Resolution An alarm monitoring a SNVT will be polled every 100 ms. If a shunt variable is then activated the pollrate will drop to 5 000 000 ms. This can be seen in the variable manager: Go to Server 1/System/Modules/RuntimeDBManager/VariableManager/Variables in Workstation Locate the variable in question and ensure that the Imposed Pollrate column is shown.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • EcoStruxure Building Operation
944 Views

Is the Niagara G3 Andover Infinity driver compatible with the NetController II (Model CX 9680)?

Issue Is the Niagara G3 Andover Infinity driver compatible with the NetController II (Model CX 9680)? Environment Niagara G3 any version Cause Site has a trunk of NetController II controllers Resolution The driver was never tested with the NetController II.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • TAC IA Series
1113 Views

What SNVT_temp_p value in the AS local node is required to force an MNL controller to fallback to a Not Active (NA) condition?

Issue What SNVT_temp_p value in the AS local node is required to force an MNL controller to fallback to a Not Active (NA) condition?  The AS station is configured to use degrees Fahrenheit and standard SNVT_temp_p definition uses degrees Celsius. Environment StruxureWare Building Operation Cause SNVT_temp_p is defined by the standard as a degrees Celsius temperature with a range of - 273.17 to + 327.66 Deg C (0.01 Deg C).  A value of 327.67 Deg C (0x7FFF) will cause the MNL controller to fallback to an NA condition.  The AS station is configured to use degrees Fahrenheit the value must be entered in Deg F. Resolution Sending a Not Active (NA) To write SNVT values, one is to write from programming logic to the local node out of the mirrored network variable to the controller SNVT.  Example: Mirrored variable, local node -> Vav??? -> nvoSetpoint, writes to VAV??? nviSetpoint [MNL-V2RV3] Go to the local node Find the nvoSetpoint Expand to Temperature value Right-click and select Properties Under Basic tab, General Information Section, Limit Section, locate the Invalid value Use the following value for NA in your programming [for SNVT_temp_p it is 621.81]
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • EcoStruxure Building Operation
1793 Views

Valves to be used in system with 28% bio-ethanol.

Issue Are the V211T, V222, V292 valves suitable in a system containing 28% bio ethanol? Environment V211T V222 V292 Cause Application requirement on content. Resolution With a content of only 28%, the valves should work just fine. Cast iron is not ideal, but it works fine. Stem packing materials are EPDM and teflon, and they will also work fine with this content.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • Field Devices
974 Views

Unable to Relay error message when sending alarm via SMTP in StruxureWare Building Operation

Issue Receiving an 550 Unable to relay alarm in StruxureWare Building Operation alarm list when sending an alarm via email. Environment StruxureWare Building Operation Enterprise Server 1.4.0.4020 Cause The SMTP email server restricted sending to external email addresses Resolution Contact the IT department to resolve configuration. Until resolves restrict email messages to email addresses on the SMTP server.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • EcoStruxure Building Operation
1259 Views

Opened graphics not poll the objects' value when there is a power cycle on the controller

Issue Open a graphics, all the objects' value display normally, when there is a  power cycle on the controller which the objects resided., the graphics will  not poll the objects' value, unless reopen the graphics or move to design mode then go back to run mode. Environment BCX1 b3s Cyberstation 1.94 SQL express 2005 + Windows 7 SQL server 2008 R2 +Windows server 2008 SP2 Cause Controller is in a heavily workload condition, the scan value reaches to high value Write value to the point under another controller but the controller is offline or there is some communication failure, although the scan is low but the program not work Resolution Delete or disable the program Modify the program to make sure the scan value is not greater than 1
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • Andover Continuum
1099 Views

On a DMS jobsite, Operator Interface does not display the MicroSmart controllers on the screen.

Issue On a DMS jobsite, Operator Interface (OPRIF) does not display the MicroSmart controllers on the screen.  There are a dozen controllers and they are confirmed as communicating to the DMS but they do not appear in the controller list in OPRIF. Environment OPRIF DMS MicroSmart Cause In OPRIF, the MicroSmart controller list displays 32 controllers per screen and it reserves spaces even if that controller address does not exist on the jobsite. If the controller addresses begin with number 33, then the first screen will appear as blank.  However, the second screen will list controllers 33 to 65. Resolution Use the Page Down and Page Up buttons to move back and forth between controller lists 1-32 and 33-65.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • TAC IA Series
961 Views

Get "Invalid System Enumeration" error when polling an XDriver point

Issue After configuring an XDriver point, clicking the refresh button on the editor results in an error "Invalid system enumeration" and no value response from the Slave device. Environment BCX1 Cyberstation 1.9X Modbus RTU Cause There is a register number shift (+1 or -1) some equipment uses. The registers listed in the manual do not actually exist. Resolution Add a register number shift (+1 or -1) to the register number listed in the manual.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • Andover Continuum
979 Views

An "Invalid Pointer" error message is displayed when attempting to open an existing project in the WorkPlace Tech Tool software.

Issue An "Invalid Pointer" error message is displayed when attempting to open an existing project in the WorkPlace Tech Tool software. Environment WorkPlace Tech Tool release 5.x.x Cause The WorkPlace Tech Tool project database file (project-name.wtp) is missing or is corrupted. Resolution Use the WorkPlace Tech Tool software to recreate the project and reassociate the applications with the project. Navigate to the project folder using Windows Explorer. If the a .wtp project database file is present, rename the file, by adding .save to the end of the existing .wtp file name, for example, rename My_Project.wtp to My_Project.wtp.save Close Windows Explorer. Open WorkPlace Tech but do not open the project. Under the WPT Project Menu, select New Specify the name of the project. Use the same name as the existing project folder. Using my example from step 2, you would create the project named My_Project In the displayed "Add Application to Project From..." window, select the "Unassigned File" tab. All existing applications for that project will appear in the list. Select them all by holding down the [Ctrl] key on your keyboard and clicking on each file shown in the list. Click the [OK] button at the bottom of the window to add all the selected applications to the newly created project. Exit from the Workplace Tech Tool software. When you reopen this project, all applications should be shown and any of them should open properly.
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Labels:
  • TAC IA Series
2201 Views

Microsoft Licensing for SmartStruxure Report Server

Issue How many SQL client licenses to run SQL if SQL 2008 is used to run Report Server? When Report Server is installed, is there a connection between SQL and the Enterprise Server. Environment Report Server Licensing Cause Licenses must be purchased for supporting software (OS, SQL, etc). Resolution Because SQL and Report Server have to be running on the same machine, there is only one sequel user that requires licensing.  There is no connection between the Enterprise Server and SQL when Report Server is installed.
View full article
Picard Product_Support
‎2018-09-06 09:49 AM

Labels:
  • EcoStruxure Building Operation
916 Views

Unable to log into Reports Server after upgrade

Issue Unable to log into Reports Server after upgrade Environment Reports Server Cause The Enterprise Server Address must be correctly entered in the required fields during the upgrade. If this is left as the default, the application will not function correctly. Resolution Browse to the SE.SBO.WebReports.Installer that was used for your original upgrade attempt. Right click on this and select "Run as administrator" In the Setup Type select the Upgrade option Follow the Prompts and be sure to enter the correct site information Under the Reporting Agent Section change the Enterprise Server URL to the correct Enterprise Server location and port. You may need to verify this on the ES PC. Complete the installation and attempt to log into web reports again.
View full article
Picard Product_Support
‎2018-09-06 09:49 AM

Labels:
  • EcoStruxure Building Operation
1364 Views

Where can I get information on Merten products?

Issue Support is required for Merten switches and Merten KNX products Environment Schneider Electric Merten products Cause Merten products are not supported by Buildings PSS Resolution Information on Merten Products can be found on their website: http://www.merten.com/ Contact details are at: http://www.merten.com/Customer-service.100.0.html For Technical Support email: tsc-wiehl@schneider-electric.com (Old email: infoline.merten@schneider-electric.com) For pricing information and ordering Merten products please contact your local Customer Care Centre (CCC).
View full article
Picard Product_Support
‎2018-09-11 06:28 AM

Labels:
  • Field Devices
1237 Views

What is the difference between Crompton and Modbus?

Issue What is the difference between Crompton and Modbus? Environment IC3-Modbus IC-Modbus Cause Adding Modbus slave devices to a network that have Crompton devices and the IC Modbus is set to Crompton. Resolution The IC Modbus when set to MODbus reads 16bit registers separately. It can add 2 consecutive 16 bit registers together to make a 32 bit word. The IC Modbus when set to Crompton reads a single 32 bit register. Crompton uses 32 bit registers. Therefore Modbus and Crompton slave devices cannot be mixed on the same IC Modbus network.
View full article
Picard Product_Support
‎2018-09-06 09:49 AM

Labels:
  • Satchwell BAS & Sigma
1172 Views

Venstar T2700 stuck in OFF mode when wired to Xenta controller

Issue The thermostat appears to be in OFF mode and can't be cycled through the modes as indicated by the manufacturer's directions.   Environment Venstar T2700, VST2700 thermostats for red-wire control connected physically to a controller Cause It seems that the polarity of the dry contact was set to the default Normally Open (NO) state. Using the Venstar EZ-Programmer to apply the correct settings for use with an occupancy point did not overwrite the polarity of the Venstar's dry contact, but did overwrite the Dry Contact Operation. Also, by wiring everything up first, we did not power up the thermostat to change the mode before it got the closed dry contact command from the BAS. So when we did power everything up, the dry contact was closed, but the thermostat understood that this was an "unoccupied" command since it was still set to NO. Even though the security settings allowed the mode to be changed, when Dry Contact Operation is enabled, the mode can only be changed in occupied mode. When the thermostat goes unoccupied, it stays in whatever mode it was in previously, and controls to the unoccupied setpoints. By not realizing that the EZ Programmer didn't overwrite the polarity, we assumed the dry contact operation and polarity were correct and a closed dry contact would enable the occupied mode.   Resolution This issue can be resolved by powering up the thermostat before connecting the dry contact relay and changing the mode to "auto". If already wired, make sure the dry contact polarity is set to Normally Closed (NC) and Dry Contact Operation is "Yes". Then the modes can be cycled while occupied. < acc0432manualrev1.pdf="" manuals="" support="" www.venstar.com="">
View full article
Picard Product_Support
‎2018-09-06 09:49 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • TAC IA Series
  • TAC INET
  • TAC Vista
1080 Views

SmartStruxure with I/A Series Micronet BACnet (MNB) controllers

Issue SmartStruxure with I/A Series Micronet BACnet (MNB) controllers Environment SmartStruxure version 1.4 and earlier I/A Series Micronet BACnet (MNB) controllers Cause Need to know if it is possible to use MNB controllers with SmartStruxure.  Resolution I/A Series MNB controllers can be integrated into SmartStruxure as 3rd party BACnet devices. For more information on SmartStruxure with MNB controllers, download document MNB BACnet Support within a StruxureWare Building Operation System Solution Guide.
View full article
Picard Product_Support
‎2018-09-11 02:44 PM

Labels:
  • TAC IA Series
1624 Views
  • « Previous
    • 1
    • …
    • 480
    • 481
    • 482
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of