When PIV card is presented at the card reader a Bad Card Parity event is generated.
Non PIV cards present no problem.
  • Card Access
  • AC1 module
  • PIV Format cards
  • PIVReaderFormat
The controller was improperly configured for PIV cards.
In this case the PIVReaderFormat system variable was not set.
When the PIVReaderFormat is left blank the system defaults to FIPS_PIV_75 Bit for FIPS cards, if the FIPS reader is configured to send a diferent FIPS output such as FIPS_PIV_Full_FASC-N (200 bits) then the system will generate a bit count not supported error.
Once the PIVReaderFormat system variable was set to the proper value the cards generated valid access events.