Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 109
    • 110
    • 111
    • …
    • 501
  • Next »

Numeric Input, Numeric Output and Numeric Public, differences

Issue What is the difference between a Numeric Input, Numeric Output and Numeric Public within a script program. Is using a Numeric Public a less efficient choice (as opposed to using a Numeric Input or Numeric Output) that will generate negative overhead in the AS? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server (AS, AS-P or AS-B) Building Operation Workstation b3 and Infinet controllers Cause Want to determine best practices when choosing numeric types during script programming. Resolution Numeric Input is a read only numeric (from the point of view of the script program) that accepts a binding. Numeric Output is a write only numeric (from the point of view of the script program) that accepts a binding. Numeric Public is both read and write (from the point of view of the script program). Numeric Public also accepts a binding. (A Numeric Public can be bound to both a Graphic and a Value Object to allow overriding of values from a Graphic. See SBO Script Public.zip for an example) When choosing the numeric type in a script program there is no overhead cost difference between using one of these numeric types vs the others. Also check out the Script Programming - Writing the Script Program Quick-Help video on the Exchange. NOTE b3 and Infinet Controller scripts do not support "Numeric Public", but "Numeric Output", in these controller scripts, can be used in a similar way to "Numeric Public" The Bound value is read by the script as well as being written to.
View full article
Picard Product_Support
‎2018-09-10 11:36 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:54 AM

Labels:
  • EcoStruxure Building Operation
4418 Views

Replacements for Satchwell sensors

Issue Replacements for Satchwell sensors Product Line Satchwell MicroNet, Satchwell Sigma, Field Devices Environment DR DR3253 DRT DRT3451 DRT3453 DRT4453 DRT3651 DRT3652 DRT3801 DRT3851 DU DU4301 DUS DUS4302 DUSF DUSF4351 DUSF4352 DRTE DRTE2201 DRTE2801 DRTE2851 DRH DRH7702 DRH7703 DRTH DRTH7712 DRTH7713 DOT DOT0001 DOT0002 DOS DOS0002 DDT DDT1701 Cause Replacements for Satchwell Room sensors Resolution DOT0001/0002 Outside temperature sensor For CSC, KMC, MMC, IAC, MNN New part number: STO600/5126060000 DOS0002 Outside solar sensor For CSC, KMC, MMC, IAC, MNN New part number:  SSO600/5126050000 DR3253 Room sensor non-adjustable For SVT New part number: STR614/004604900 DRT3451 Room sensor exposed adjustment For CZU, CSC New part number: STR612/004604700 DRT3452 Room sensor concealed adjustment For CZU, CSC New part number: STR611/004604600 DRT3453 Room sensor non-adjustable CZU, CSC, CXR, CZT, KMC, MMC, IAC, MNN New part number: STR600/004604100 DRT4451 Room sensor non-adjustable As DRT 3453 in S-Link housing Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRT3651 Room temperature sensor exposed adjustment For CXR, CZT, KMC, MMC, IAC, MNN New part number: STR602/004604300 DRT3652 Room temperature sensor exposed + LED For MMC, IAC, MNN Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRT3801 Room temperature sensor fan switch On/off for CZU, MNN, IAC Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRT3851 Room temperature sensor fan speed switches As above plus medium and high Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DU4301 Room sensor temperature For MNN & URC New part number: STR601/004604200 DUS4302 Room sensor temperature setpoint advanced basic sensor New part number: STR613/004604800 DUSF4351 Room sensor temperature setpoint adjustable fan auto/on/off fan override New part number: STR609/004604400 DUSF4352 Room sensor temperature setpoint advanced fan Auto/1/2/3 fan override New part number: STR610/004604500 DRTE2201 Active room detector Basic sensor Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRTE2801 Active room detector On/off Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRTE2851 Active room detector Off/low/medium/high Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRH7702 2% 0-10V DC humidity only For KMC, MMC, IAC, MNN New part number: SHR100/006902340 DRH7703 3% 0-10V DC humidity only For KMC, MMC, IAC, MNN New part number: SHR100/006902340 DRTH7712 2% 0-10V DC humidity with Satchwell NTC TEMP OUTPUT For KMC, MMC, IAC, MNN New part number: SHR100-T6/006902420 DRTH7713 3% 0-10V DC humidity with Satchwell NTC temperature output For KMC, MMC, IAC, MNN New part number: SHR100-T6/006902420 DDT DDT1701, DDT1702 and DDT0001 Duct sensor non-adjustable New part number: STD660 5126030000 Contact Details: Titan Controls: http://www.titancontrols.net/ Sontay Controls https://www.sontay.com
View full article
Picard Product_Support
‎2020-09-29 10:29 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:54 AM

Labels:
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
7932 Views

SSL Certificates - Security Certificate Risk warning logging in to WorkStation or WebStation using HTTPS

Issue When logging in to SmartStruxure WorkStation you get a security certificate risk warning Security Certificate Risk There were errors validating the security certificate in use. This may pose a security risk to the system. The certificate presented by this server was issued for a different server's address. How do you wish to proceed? Trust certificate or Cancel You can also get a warning when logging in through WebStation if you use the https address Warning in Google Chrome - FireFox - Internet Explorer Product Line EcoStruxure Building Operation Environment SmartStruxure version 1.6 and newer WorkStation WebStation Cause Starting in version 1.6, a new security feature has been introduced validating the ES and AS server identity based on security certificates. In order to avoid seeing this warning each time you log in, you need to apply a certificate to each server (ES, AS, ASP or ASB) - either a self-signed or an existing. Resolution This article will describe how to import or generate a certificate, and how to install the certificate through WorkStation or a browser. If you generate the certificate for an Automation Server, make sure that the time and time zone is correctly set in the Automation Server before generating the certificate. Regarding external CA certificates In step 8 below, it's shown how to generate a self-signed certificate. It might be that it's required to use an external CA certificate issued by a trusted issuer e.g. Verisign. All X509 certificates are supported. The format of the certificate must be PEM (as opposed to DER, PKCS7 or PKCS12). More about certificate types here. SBO currently only supports certificates using the PEM format which is the most common. If the external CA certificate is delivered in a container format (such as .pfx) it must be extracted before it can be used in SmartStruxure. More about extracting certificates here. Importing or generating a certificate Log in to Workstation clicking "Trust certificate" Navigate to the control panel Click on "Security Settings" Click on "Certificates" If you see a message saying that a secure communication protocol is not in use, it means that one or more AS's are communicating with the ES using the TCP port (4444) rather than https. In order to manage certificates for all servers in one operation, you need to change the communication ports. Click on "Configure communication settings" to do that. - and change the protocol to HTTPS and the port to 443 Back in the certificates settings, select one or more servers (in this example just the ES) and click "Manage Certificate" Select a certificate type to add. Unless a certificate is bought from a third party provider, select "Generate certificate" which will make a self-signed certificate. Enter a name, tick "Use IP/DNS..." and select a date when the certificate will expire as a minimum, and fill out more info if needed. Click "OK".  NOTE: Do not exceed year 2060 in the "Valid to" field, doing so will result in a certificate expired error when trying to apply the certificate. Select the certificate just created and save   Installing a certificate through Workstation Close Workstation (just logging out is not enough) Open Workstation and log in using the IP address or DNS name - never "localhost" as that name will not match the certificate. Now you will be able to tick "Always trust this certificate" as the name (IP address or DNS name) in the certificate matches the server you are logging on to. Tick the box, and click "Trust Certificate". Click "Yes" to confirm the installation of the certificate Now you will not get the security warning when logging on Installing a certificate through a browser Access the server using Internet Explorer (important) entering the https address (e.g. https://localhost) Click on "Continue to this website" Click on the "Certificate error" field next to the address bar Click on "Install certificate" Select "Trusted Root Certification Authorities" Click next and ok Close the browser Now you can use both Internet Explorer, Google Chrome and FireFox to access the server from Webstation using https and not get the warning If the certificate fails to install and be trusted properly, it might be because you need to manually select which physical storage to add it to. Refer to the following discussion
View full article
Picard Product_Support
‎2018-09-11 01:38 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:54 AM

Labels:
  • EcoStruxure Building Operation
36880 Views

TGML JavaScript data types affect addition, comparisons, and string concatenation

Issue Using addition in a JavaScript, but it is performing a string concatenation. Example: The value in the database is 3. value = value + 1; The resulting value is 31, not 4.  Comparisons are returning unexpected results NaN (Not a Number) resulting from a JavaScript function Product Line TAC Vista Environment TGML JavaScript Vista 5 Graphics Cause Values that are read into a JavaScript in a TGML graphic need to be cast to the correct data type. Some values may be read in as an ASCII string, and this can cause unexpected results. Resolution Cast the value being read to the desired data type. There are three options for casting values to numerical values that can then be used in mathematical operations. In the example below a variable named "value" reads a database value from a binding. No type casting is performed, so this value may be interpreted as an ASCII string. function OnSignalChange(evt){ value = evt.getValue(); } To ensure that the data are represented as numerical value, select one of the three options below. Replace the variable declaration (highlighted) with one that utilizes the appropriate type casting. Number() value = Number(evt.getValue()); The Number() function will treat the whole object as a number. Non-numerical characters will return NaN. parseInt() value = parseInt(evt.getValue()); The parseInt() function will convert the beginning of a string to an Integer value, ignoring any decimal points or any trailing non-numbers. parseFloat() value = parseFloat(evt.getValue()); The parseFloat() function will convert the beginning of a string to a floating point decimal value, ignoring any trailing non-numbers. Also check out the JavaScript Essentials - Episode 3 - Value Types Quick-Help video on the Exchange.
View full article
Picard Product_Support
‎2018-09-07 04:06 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • TAC Vista
4117 Views

Controller cold starts after power fail

Issue Controller cold starts after power fail Product Line Andover Continuum Environment Continuum 1.x CX BCX Cause ACCRestartMode system variable is set to Cold Start Resolution Change the ACCRestartMode system variable. See the bCX1 Controller Technical Reference Guide Rev F  document page 55 onwards for an explanation of the changes that are required.
View full article
Picard Product_Support
‎2018-09-10 05:18 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • Andover Continuum
6048 Views

Replacement of Satchwell "M 1201" Actuator forming part of combined Actuator / 2-port Valve Body assembly due to obsolescence.

Issue Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly requires replacement. Environment Stand alone Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly M 1201 Actuator 2-port Valve Body Cause Obsolescence of Satchwell “M 1201” forming part of combined Actuator / 2-port Valve Body assembly. Resolution There is no direct replacement for the "M 1201" Actuator and as a result both the "M 1201" Actuator and the 2-port Valve Body to which it is connected will also require replacement.  Replace Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. Satchwell MB series 3-port Rotary Shoe Valve Body may be converted for use as a 2-port Zone Valve by means of the installation of a plumber’s plug in Port 3 Install plumber's plug in Port 3 of MB series 3-port Rotary Shoe Valve Body. Tighten plumber's plug sufficiently to ensure PN 10 rating of Valve Body is not compromised. It is possible that the "M 1201" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 04:56 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • Field Devices
8072 Views

Postgres/TimescaleDB leaves us without a reporting engine. SSRS is licensed part of MSSQL.

Issue Moving from Webreports going to Postgres/TimescaleDB instead, leaves us without a reporting engine. SSRS can supposedly utilise a PostgreSQL database, but SSRS is a licensed part of MSSQL. Product Line EcoStruxure Building Operation Environment Building Operation Timescale Database Cause From EcoStruxure Building Operation version 4.0 (2022) the Building Operation Report Server is no longer supported. Instead, we support PostgreSQL/TimescaleDB, using Dashboards and Excel from within EBO, to make reports, using Notification reports to start Excel and reports. Resolution EBO 3.2 introduced Enhanced Reporting, based on the current feature Notifications in combination with Notification Report Template, which also supports report data such as Alarms, Groups, Multi Log list, Relative events and Users. The Notification result can also be presented in XLSX format and converted to PDF with signing capabilities. If External Log Storage is configured and connected (PostgreSQL/TimescaleDB), then historical report data can be fetched from there.   EBO 2023 introduced External Log Storage support for Microsoft SQL Server in addition to PostgreSQL/TimescaleDB   Information  and examples of Enhanced Reporting and Dashboards can be found in EBO Webhelp, My LearningLink and the Automation Experts Community.   NOTIFICATION REPORTS : EBO Webhelp: Notification Reports  Community: Reporting in EcoStruxure Building Operation 3.2 Community: Reports showcase - share your reports! Community: Get more data out of the system with Notifications! EcoXpert Extranet Video: Community Video : Fusion Fridays - Session 20 Community: Change Control and Enhanced Reporting Lab Guides Community: Example Report Templates  Community: Forced Values Report Example My LearningLink: EcoStruxure Building: Enhanced Reporting and Dashboards 3.2 My Learning Link: EBO 2022: Enhanced Reporting and Dashboards   DASHBOARDS : EBO Webhelp: How Dashboards Work EcoXpert Extranet Video: Dashboards EcoStruxure Building Operation 3.0 - Informational Video Community: What Custom Types have to do with Dashboards Community: Public vs Personal Dashboards Community: Graphics in Dashboards [Advanced] Community: Dashboards: Share your screenshots! EcoXpert Extranet: PA-00701 EcoStruxure™ Building Operation 3.0 Captures the Spotlight
View full article
Guinan MikaelKrantz Guinan
‎2023-01-31 06:29 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • EcoStruxure Building Operation
4233 Views

Cannot Connect to the Platform on New or Cleaned JACE-8000

Issue On a new JACE-8000, or on one in which the clean-dist or factory restore procedure has been applied, the JACE can be pinged but, you cannot connect to the platform, and the system time's year shows as 2020 or greater.   The following symptomatic messages can be observed in the serial shell via the debug port:  ERROR [01:26:53 01-Jan-2037] [tid = 1] niagarad: policy file verification failed. Policy files may have been tampered with. Cause is: [/opt/niagara/security/policy/java.security failed signing verification]  ERROR [01:26:53 01-Jan-2037] [tid = 1] niagarad: throwable occurred while initializing daemon (java.lang.SecurityException), can not continue  sysmon: niagarad is no longer running  The following symptomatic messages appear in the system logs:  Jan 01 01:26:53 2 11111 0 niagarad: policy file verification failed. Policy files may have been tampered with. Cause is: [/opt/niagara/security/policy/java.security failed signing verification]  Jan 01 01:26:53 2 11111 0 niagarad: throwable occurred while initializing daemon (java.lang.SecurityException), can not continue  Jan 01 01:26:53 2 11111 4 sysmon: niagarad no longer running Product Line TAC IA Series. Environment I/A Series Jace-8000 Cause This issue is encountered when the RTC clock's date is Wednesday, December 30, 2020, or later.  Resolution Use the debug port to connect to the system shell with PuTTY. See the System Shell section of the JACE-8000 Install and Startup Guide Set the system clock to a date before the year 2020, and then commission the JACE with 4.2 or newer.  The issue is corrected within the fix for the following issue, addressed in Niagara 4.2.36.10:   NCCB-19628: Code signing timestamps checked improperly, verification will fail Jan 1, 2021    We will continue to see the issue on new JACE-8000 as they ship with a 4.1 daemon. This may also occur on a JACE-8000 on which the clean-dist or factory restore procedure has been applied.
View full article
Guinan RandyDavis Guinan
‎2019-09-30 08:32 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • TAC IA Series
12975 Views

TAC Graphic Clipart Library

Issue TAC Graphic Clipart library is a collection of clipart to use as a starting point for an image based graphic page. There are pieces for building air handler ductwork, controlled equipment, dampers and actuators, and water side equipment. Product Line TAC INET, TAC Vista Environment I/NET gpg graphic Vista ogc graphic Cause Without libraries to build a background image for HVAC equipment, it can be difficult to create user-friendly graphic pages to display dynamic data.  In a graphic editor that relies on bitmaps or jpgs to build the airflow diagrams, floor plans, water side diagrams, etc, this library can be used as a starting point. Resolution Download the attached .zip file. Unzip the contents to a location on the hard drive of the computer that will be used to edit the graphic pages. Browse the contents of the .zip file.  It will be separated into logical folders.
View full article
Picard Product_Support
‎2018-09-07 03:44 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • TAC INET
  • TAC Vista
4516 Views

Understanding custom card formats in Continuum

Issue How can the format of a custom card be determined/understood Product Line Andover Continuum Environment Access Control AC1 AC1Plus ACX Cause The format of access cards is unknown. Resolution The document Understanding custom card formats in Continuum describes how to determine the custom format of proximity cards.  
View full article
Picard Product_Support
‎2021-02-11 03:35 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • Andover Continuum
5061 Views

Supplemental Documentation on the Menta OPT block

Issue Supplemental Documentation on the Menta OPT block for optimized start and stop. Product Line TAC Vista, EcoStruxure Building Operation Environment Menta Function Block Cause The document below is intended to clarify the inputs and configuration parameters of the Menta OPT block and when/how to use them. Resolution Click here to download the example Menta macro A Brief Overview of Optimized Control Optimal Start Optimal Start measures how long it takes a room temperature to reach setpoint each morning when the air-handling unit is enabled. These measurements are then used to predict how long it will take the next time. As time goes on, the predictive algorithm is refined until it becomes quite accurate. An optimally started unit saves energy by only starting as early as is needed, not just an arbitrary hour or two before occupancy. Optimal Stop Optimal Stop is less common. An optimally stopped unit stops running prior to the end of the day. It measures how long it takes before the measured room temperature drifts outside of an acceptable range around the setpoint. This saves energy on cooling a building until 5:00pm (for example) when the occupants are just about to walk out the door. The example in this document will not implement Optimal Stop. Inputs to the OPT Block RoT Room Temperature. If there is just one room temperature sensor being served by the optimally started unit, then this is where it would be used. However, if the unit has several room temperatures or serves many VAV terminal units, consider the following options: Average all temperatures Pick one interior zone Highest room temperature for cooling/lowest room temperature for heating Use return air temperature In all of these scenarios, some consideration should be made for if the input sensors fail: Averaging all temperatures is the most robust method. However, if SNVT inputs are used, it may be necessary to discard invalid values (621.8°F) from the averaging calculation. If one interior zone is used and the temperature sensor fails, the unit will eventually revert to starting as early as is allowed every day. The default value for this is 12 hours early; the example in this document uses 2 hours. If the primary sensor fails, use a secondary, or disable optimal start on a failed condition. Instead of the highest and lowest room temperatures, it may be wise to use the second highest and the second lowest room temperature. This allows for one failed sensor in each direction before the Optimal Start calculation is affected. Using return air theoretically is a lot like using the average of all room temperatures. Adjusting the setpoint to get the desired result might be required. A failed sensor input should disable the Optimal Start calculation. SP Setpoint. Using two OPT blocks – one for Optimal Start cooling, one for Optimal Start heating – allows each to be fine tuned. If there is a morning warm-up sequence, then the heating Optimal Start may be much quicker than the cooling. Using one block requires the internal calculation to adjust as the needs change from cooling to heating, and can be less agile when switching from cooling to heating requirements. OuT Outdoor Temperature. Resets to the curve occur based on the outside air temperature. If it is very cold or very hot outside, the unit will start sooner. This curve is reset automatically as time goes on to better predict the effect outside air temperature has on the controlled space (if AutoAdjust > 0). OpI Operation Indication. In the example of an air-handling unit, OpI would be the fan status. If the configuration parameter OperIndicF is set to 1, then this will be used for internal calculations. Otherwise, it will just use the command as status. This prevents a mechanically failed unit from affecting the calculation. A good rule to follow is if fan status is available, use it. TmL Time left. A time schedule (TSCH) input goes here. This tells the calculation how much time is left before the unit is scheduled to turn on (or off). The OPT block then starts the unit early based on this number. It also ensures that the unit always runs during the scheduled occupied time. Mode Mode is for heating/cooling or enabled/disabled. It is advantageous to always program in a method for disabling Optimal Start through a public variable (PVB). Many times the seeming complexity of Optimal Start is found to be undesirable by building operators and they will ask to have it disabled. Mode could be programmatically set for heating/cooling based on outside air temperature (or some other factor), but in the example in this document, two separate OPT blocks are used and are hard-coded for their respective modes. Configuration Parameters of the OPT Block AutoAdjust AutoAdjust refers to whether or not the OPT block gets smarter by adjusting the curves set initially on the first download. If AutoAdjust is set to 0, then the OPT block will still adjust the start time every day based on the room temperature and outside air temperature, but it will not adjust those early start times based on past experience. Set the AutoAdjust to 1, and the curves will adjust a little every day. Set AutoAdjust to 2 and the OPT block will also adjust the holiday compensation (the unit will start a little earlier after a 3-day weekend, but may need to learn exactly how much as time goes by). To maximize the potential of the OPT block, it is suggested to set this value to 2. RoomTempF Room Temperature Flag. Is a room temperature sensor present? Without a room temperature sensor, it is not possible for the OPT block to adjust its curves. It is guessing at that point based on pre-determined curves. It is not recommended to use OPT without a room temperature sensor. OperIndicF Operation Indication Flag. If OperIndicF is set to 1, then the OpI input will be used for internal calculations. Otherwise, the OpI input is ignored and the command is used as status. This prevents a mechanically failed unit from affecting the calculation. A good rule to follow is if fan status is available, use it. StartTimeLo Start Time at Low Outside Air Temperatures. When it is cold outside, how much earlier should the unit start? This will change between a cooling and a heating optimal start block. If AutoAdjust is set to 1 or 2 then this is just a default value. It will adjust as needed each day, but a good default value is important. StartTimeHi Start Time at High Outside Air Temperatures. When it is hot outside, how much earlier should the unit start? This will change between a cooling and a heating optimal start block. If AutoAdjust is set to 1 or 2 then this is just a default value. It will adjust it as needed each day, but a good default value is important. HolidayComp Holiday Compensation. This is the default compensation for a holiday (longer than 48 hours of continuous unoccupied time). The value is a percentage. If there is a 3-day weekend, how much earlier should the unit start on the following Tuesday? If AutoAdjust is set to 2 then this is just a default value. It will adjust it as needed each day, but a good default value is important. MaxStartTi Maximum Start Time. This is the maximum amount of hours the unit is permitted to start prior to the occupied time. The default value is 12 hours. The first time the unit is downloaded, it will start this early and measure how long it takes to achieve setpoint. 12 hours is very early. The example in this document uses 2 hours. Even if something goes wrong with the internal calculation (failed sensor input, for example) the earliest it could start would be 2 hours early. ETol Error Tolerance. How close to the desired setpoint does the temperature sensor need to be to be considered at setpoint? An error tolerance of 0.5°F is default and is usually acceptable. StopLoTemp, StopTimeLo, StopHiTemp, StopTimeHi, StopTimeErr All of these parameters refer to the Optimal Stop portion of the OPT block. Setting them to 0 disables the Optimal Stop functionality. Output of a OPT Block There are three possible output values of an OPT block: 0 = The unit is off, unoccupied 1 = The unit is on, occupied 2 = The unit is on, optimally started Putting It Into Practice The example below is a Menta Hierarchy Function Block (HFB) and shows HFB inputs to the blocks. The top OPT block is set to heat mode and looks to a heating setpoint. The bottom OPT block is set to cool mode and looks to a cooling setpoint.   OPT_START_HEAT OPT_START_COOL AutoAdjust 2 2 RoomTempF 1 1 OperIndicF 1 1 StartTimeLo 60 0 StartTimeHi 0 60 HolidayComp 0 0 MaxStartTi 2 2 Etol 0.5 0.5 StopLoTemp 0 0 StopTimeLo 0 0 StopHiTemp 0 0 StopTimeHi 0 0 StopTimeErr 0 0 Using the hints and tips suggested will allow not only for proper programming techniques, but also for creation of macro libraries that can be reused and shared to improve effectiveness across business units.
View full article
Picard Product_Support
‎2018-09-07 08:33 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
5276 Views

SPP920 Datasheet, Technical Information and Installation Instructions

Issue SPP920 Datasheet, Technical Information and Installation Instructions Product Line Field Device Environment SPP920 Differential Pressure Switch Cause No information available for the SPP920. The Sensor catalogue says it is supported by Huba. Resolution Either click link www.hubacontrol.com and search for 630. or the Technical information can be downloaded here. Installation Instructions can be downloaded here. Mechanical connections are: P1 = High Pressure (discharge/flow), P2 = Low Pressure (suction/vacuum) All of the various pressure range options come with the following options: - EPDM diaphram material - Brass Case - Spec Cover PG9 - IP65 Rating - Bracket Type A
View full article
Picard Product_Support
‎2018-09-10 10:48 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • Field Devices
11675 Views

Simple Modbus Lua Script

Issue Simple Modbus Lua Script Product Line EcoStruxure Building Expert Environment Lua Programming Cause Simple script to test Modbus function Resolution In each of the samples, the following needs to be observed: The Modbus port is closed and opened with the port settings. The samples can be combined but the port is only set once. The settings for the Modbus RS485 port requires an address, in this instance 99 is used. This must be different from the slaves. The nnn.MOD1 must be left unchecked so that it is not enabled. This will allow the Lua script ModbusB to work. For added functionality the "Print" command is used. The "print" command provides added functionality indicating a successful read / write in the output window. If the result = 0 then the read / write is successful. Anything else is an error code. Contact Product Support. The value = is the value that is either read in or written dependant on the function used. The following samples provide simple read / write functions.: Coil Registers Digital Input Registers Holding Registers Input Registers 32bit Floating Point
View full article
Picard Product_Support
‎2018-09-11 09:06 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • EcoStruxure Building Expert
8720 Views

Design and Architecture of iBMS

Issue Documentation for architectural design for illustration, explanation, sales presentations, or other medium Environment Schneider Electric office, partner office, or other site needing documentation Cause Inability to find literature and need to explain, illustrate, or define issues. Please find the links below for each of the product lines. Resolution Continuum: download architectural Flyer:  pdf   jpg  INET: download  architectural Flyer Vista:  download architectural flyer pdf   jpg  I/NET and Vista together pdf
View full article
Picard Product_Support
‎2018-09-10 04:52 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • Andover Continuum
  • TAC INET
  • TAC Vista
3552 Views

"Invalid certificate for https communication" alarm

Issue “Invalid certificate for https communication” alarm pops up after upgrading to EBO 4.0     Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause "Invalid certificate settings for Server to Server communication" is set to enabled (Generate Alarm) by default for new installations/upgrades. This function was deliberately designed to alert existing installations that their sites might be subject to security-related issues, and necessary action needs to be taken. Resolution If users want to get rid of this alarm, they need to: Suppress the alarm by unchecking the “Generate alarm” under Security Settings/ Invalid certificate settings for server to server communication   Or Replace the server certificates with one that can be validated against a CA certificate.   Note: Please refer to the following web pages for more information. CA Certificate Management Security Settings – Control Panel  SSL Certificates 
View full article
Lt. Commander Reza Lt. Commander
‎2022-07-19 10:56 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Labels:
  • EcoStruxure Building Operation
3317 Views

Troubleshooting Lon communication issues

Issue Controllers underneath a LonWorks Interface are going offline, or values are taking long periods of time to update. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause There could be a number of causes for Lon communication problems including running the communication wire near high voltage, the Lon is shorted out, or loose terminations. Resolution In EcoStruxure Building Operation (EBO) Workstation you can use the Diagnostics tab under each controller to help troubleshoot the communication issue. From here you can monitor the device state, packet errors, transaction timeouts, receive transaction full errors, lost messages, missed messages, last reset case, and the last error logged. To access the Diagnostics tab, select the controller in the System Tree, and click the Variables tab. Then click the Diagnostics tab on the right side of the screen. Here you will find the different device statuses and statistics. The Packet errors can be used to help identify controllers that are having severe problems and may need the communication wire to be physically checked. In order to test the Packet errors, first you will want to clear the current packet error count. You can do this by right clicking on the controller and selecting Advanced -> Clear Status. This will set the packet error count back to zero and now you can click refresh to monitor how fast the errors are building up. If this number is climbing quickly then there may be a physical layer communication problem. If a lot of packet errors is found, the next step in the investigation will be a deeper analysis of the Lon network, using, for example, a Lon Protocol Analyzer (LPA). Refer to the Knowledge Base Article Troubleshooting LON Network Communication.
View full article
Picard Product_Support
‎2018-09-07 08:56 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
5250 Views

Creating binding templates

Issue Creating binding templates. Product Line EcoStruxure Building Operation Environment Binding templates for Script and Function block programs. Binding template examples:  Type Binding Template Examples Path Matching Binding Templates and Syntax Path Matching Binding Template Examples  Cause 1 - Output points need to be bound to the Requested Value attribute, but the default name matching template only matches the value attribute. 2 - Binding  a Graphic which contains several controllers which all have the same names in the system tree structure, using a binding template. 3 - Binding Template Types examples Resolution 1 - Output points need to be bound to the Requested Value attribute, but the default name matching template only matches the value attribute. Under the system folder of the AS or ES there is a folder called "Binding Templates". In here you can create custom templates by right clicking and selecting "New", "Binding Template". To create a generic template that will bind both inputs, outputs, values and other object types follow these steps: Press Next and the following screen appears: Select All Types and press Next: Click twice on the Add Rule icon (Green +) then enter the three rules as follows: Press create and the new IO Binding template will be created.  If you have used a common naming convention in your points and within the programs, you will be able to use this template to bind all the points and values to your programs. Drag the AS across to the IO Binding template (as below) and it will match all of the point names and use Requested value attribute for the output points. This example shows 2 IO Binding templates, as one was created at the AS level and another at the ES level. Only 1 is actually required to provide this functionality. You can subsequently edit the binding template and it will show as follows:   2 - Binding  a Graphic which contains several controllers which all have the same names in the system tree structure, using a binding template. It is common for a system to consist of many controllers that have been created from the same import file. This will mean that there are many instances of the same names being used, but this is not an issue until a graphic containing several controllers are to be bound. Create a "Path Matching Binding Template" as shown above and configure as shown in the following screen shot. Notice that the Binding candidate has /Application/ between the "Unit" and "Point" to match the tree structure.        The screen shot below shows the site system tree structure, with part of the graphic binding page. Note that for the binding template to work, the bind names used in the graphic must be unique. eg. L6W1_CHB_006 (Unit) and ReturnAirTemp (Point).     For an Export of this template, click Binding Template Export 2013-08-15 083240.zip. 3 - Binding Template Types examples see the Online Help. An additional resource is the Exchange Community in particular the following Knowledge Reinforcement Session Also check out the SmartStruxure-Binding Templates-Lesson 1-7 Quick-Help video on the Exchange.
View full article
Picard Product_Support
‎2018-09-11 01:52 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
15382 Views

How to extract an XIF out of a Lon controller

Issue There may be a situation where the External Interface File (XIF) needs to be extracted out of the controller in order to properly set up the controller in a building automation system.  Product Line EcoStruxure Building Operation, TAC IA Series, TAC Vista Environment External Interface File (XIF) NodeUtil Loytec XIF Builder Cause These tools will help with the extraction of an XIF file. An XIF file is used to create a Niagara R2 shadow object, a Niagara G3 LMNL file, LonWorks device template, and a SmartStruxure device template.  Resolution The device manufacturer should provide an XIF, and in most cases, a DRF kit as well. The XIF provided by the manufacturer of the controller should be used first but if issues arise it may be required to extract the file from the controller. There are a number of tools available that will create an XIF, but the DRF kit cannot be created by any tool and must be supplied by the manufacturer. This MUST be provided along with the device. The list below covers some of the tools which are available. NodeUtil                          (header: bad,           NVs: ok,                      DMA/File-SCPTs are omitted) Vista's XIF-builder           (header: bad,           NVs: almost ok..,       DMA/File-SCPTs are omitted)  Loytec plugIn                  (does a perfect XIF from a device using Loytec's stack)   NodeUtil is available from the Echelon website (free registration is required) - The NodeUtilLauncher package attached makes it easy to use NodeUtil with Loytec interfaces. Loytec XIF Builder is available from the Loytec website (free registration is required) Using Lonmaker and the XIF Builder. Using NL220 and the XIF Builder. If the uploaded XIF still contains some detailed prompted error, refer to Error displayed when importing a device XIF into SmartStruxure.
View full article
Picard Product_Support
‎2018-09-11 02:59 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
9602 Views

PT100/PT1000 sensors used with Xenta controllers

Issue Do Xenta controllers support PT100/PT1000 sensors for measuring the temperature? Environment Xenta Controller TAC Menta PT100/PT1000 Temperature sensors Cause Requirement to measure the temperature using PT100/PT1000 Temperature sensors. Resolution PT100/PT1000 sensors are not supported within any of the Xenta controllers.  The following is a method to achieve this using Menta: When using PT100/PT1000 to connect to a thermistor input, Menta Logic is required to add a polynom using the expression block. It is also strongly recommended to implement some calibration software in Menta to allow for fluctuations in resistance for every input that PT100/PT1000 is connected to. If a sensor is replaced / changed, re-calibration will be required. Sample experiment results and Menta Logic's are available here.
View full article
Picard Product_Support
‎2018-09-10 03:04 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • TAC Vista
1949 Views

Technical Tips documentation for I/NET Seven

Issue Links to the Technical Tips Papers Product Line TAC INET Environment I/NET Seven Tech Tip Cause Formerly only available on the FTP site, now available in the Knowledge Base. Resolution Tech Tips linked below. Tech Tip 001   System S7000 Upgrade to I/NET 7700 Tech Tip 002   Calculated Point and Docutrend Operator Rankings Tech Tip 003   MIP01 Memory Interface Processor Installation Tech Tip 005   I/NET 7700 Printer Enhancements Tech Tip 006   Use of LAN Repeater on I/NET 7700 Tech Tip 007   I/NET System Messages Tech Tip 009   I/NET 7700 Setup Tech Tip 010   ICI HHC Memory Addresses Tech Tip 011   S/90 Purging Visitors Tech Tip 012   Shipping MIP Products Tech Tip 013   Mechanical Door Interlock Wiring Tech Tip 014   S90 Graphics PCX File Requirements Tech Tip 015   Indala Reader Card Types Tech Tip 016   New RAM Configuration for MIP Tech Tip 017   Transient Protection On DPUs with I/Disc Tech Tip 018   I/NET 7700 Taps and Building Managers Bias Straps Tech Tip 019   Docutrend and Hard Disk Space Tech Tip 020   Docutrend Reports Tech Tip 021   ADAA Tap Addresses Tech Tip 022   Docutrend:Number of Days of Report Tech Tip 023   S/90 Memory Requirements Tech Tip 024   ADAA System Messages and Docutrend Setup Tech Tip 025   I/NET 7700 Work-Arounds and Known Problems Tech Tip 026   I/NET 7700 Controllers BOOT ROM Compatibility Tech Tip 027   S/90 Color Mapping Tech Tip 028   Controller Battery Back-up Tech Tip 029   I/NET 7700 Host Sign-on/off and Host Lost/restored Messages Tech Tip 030   MR Minimum Trip and Close Tech Tip 031   I/Disc Installation Method Tech Tip 032   ADAA S7000 to I/NET 7700 Upgrade Tech Tip 033   I/DISC Reader Maintenance Tech Tip 034   UCI/UC Use of Bit Offset 08 & 09 Tech Tip 035   MR Memory Usage Tech Tip 036   DPI, MRI & MCI Memory Allocation Tech Tip 037   WIRING AND CONFIGURING CSI CONTROLLERS Tech Tip 038   Programming the 7750 Building Manager Tech Tip 039   7910 and 7920 DPU Memory Usage Tech Tip 040   Lantastic 6.0 Installation for use with S/90 Tech Tip 041   Using pcANYWHERE 5.0 with S/90 Tech Tip 042   MR Memory Usage Correction Tech Tip 043   “P” only Mode of Operation for PID Modules Tech Tip 044   I/STAT Functionality Tech Tip 045   I/NET 7700 Backup Station Tech Tip 046   S/90 and RDTAP Dial Tech Tip 047   Mixing Different Types of ADAA TAPs Tech Tip 048   Universal Asynchronous Receiver-Transmitter Chips Tech Tip 049   Special Days Tech Tip 050   Supervised Inputs Tech Tip 051   I/NET 7700 Ethernet LAN System Tech Tip 052   I/NET 7700 Modem Compatibility Tech Tip 053   I/NET 7700 Modem Compatibility Update Tech Tip 054   SETTING UP THE SITE TAP EDITOR TO CALL A PAGER Tech Tip 055   History Recall Report to DBF File Output Tech Tip 056   Use of I/NET 7700 Message Masking Tech Tip 057   LTS80 Series Lini-Temp Sensors Tech Tip 058   MR55X with Kavlico Transducer Tech Tip 059   I/NET 7700 Controller Interface Cabling Tech Tip 060   Use of DC/DM Points with Sub-Lan Devices MRs and UCs Tech Tip 061   AI and PI Fractional Digits Tech Tip 062   PID and Control Point Tech Tip 066   Momentary Release & Automatic Time Schdl. Release w/ I/NET 7700 used w/ Elevator Tech Tip 063   I/NET Personnel Reports Tech Tip 064   Watermark's in S/90 Video Badging Tech Tip 065   System 90 and Video Badging System Installation Tech Tip 067   12 Steps to I/NET Access Control Tech Tip 068   Application to Disable the “1-OPEN” state of a Supervised DI point Tech Tip 069   TTS100 SERIES THERMISTOR SENSORS Tech Tip 070   BATCH FILES FOR REMOTE SITE GRAPHICS PAGES Tech Tip 071   Access Control Doc-to-DIF Report Tech Tip 072   Standalone MR-VAV-AX Start-up Tech Tip 073   I/NET 7700 Modem Compatibility Tech Tip 074   SETPOINT ADJUSTMENT DEVICE PROGRAMMING Tech Tip 075   Using Belimo NM24 Actuator with MR-ASC’s Tech Tip 076   Running I/NET 4 on a Windows95 Tech Tip 077   How to Convert an Idisc Number Tech Tip 078   How to program a Modem without the use of a TerminalEmulator Tech Tip 079   COMMONLY ASKED ASC QUESTIONS Tech Tip 080   S/90 ACI/DACI Battery Life Tech Tip 081   Integrated I/NET Video Badging Requirements for Single PC Systems Tech Tip 082   How to program Forced Door & Door Open Too Long Alarms Tech Tip 083   How to get started with Integrated I/NET Video Badging
View full article
Picard Product_Support
‎2018-09-07 02:11 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • TAC INET
91712 Views
  • « Previous
    • 1
    • …
    • 109
    • 110
    • 111
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore