Creating binding templates

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating binding templates
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
15382 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating binding templates

Picard Product_Support
‎2018-09-11 01:52 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Issue

Creating binding templates.

Product Line

EcoStruxure Building Operation

Environment

Binding templates for Script and Function block programs.

Binding template examples: 

  • Type Binding Template Examples
  • Path Matching Binding Templates and Syntax
  • Path Matching Binding Template Examples 

Cause

1 - Output points need to be bound to the Requested Value attribute, but the default name matching template only matches the value attribute.

2 - Binding  a Graphic which contains several controllers which all have the same names in the system tree structure, using a binding template.

3 - Binding Template Types examples

Resolution

1 - Output points need to be bound to the Requested Value attribute, but the default name matching template only matches the value attribute.

Under the system folder of the AS or ES there is a folder called "Binding Templates".

In here you can create custom templates by right clicking and selecting "New", "Binding Template".

To create a generic template that will bind both inputs, outputs, values and other object types follow these steps:

Press Next and the following screen appears:

Select All Types and press Next:

Click twice on the Add Rule icon (Green +) then enter the three rules as follows:

Press create and the new IO Binding template will be created.

 If you have used a common naming convention in your points and within the programs, you will be able to use this template to bind all the points and values to your programs.

Drag the AS across to the IO Binding template (as below) and it will match all of the point names and use Requested value attribute for the output points.

This example shows 2 IO Binding templates, as one was created at the AS level and another at the ES level. Only 1 is actually required to provide this functionality.

You can subsequently edit the binding template and it will show as follows:

 

2 - Binding  a Graphic which contains several controllers which all have the same names in the system tree structure, using a binding template.

It is common for a system to consist of many controllers that have been created from the same import file. This will mean that there are many instances of the same names being used, but this is not an issue until a graphic containing several controllers are to be bound.

Create a "Path Matching Binding Template" as shown above and configure as shown in the following screen shot. Notice that the Binding candidate has /Application/ between the "Unit" and "Point" to match the tree structure. 

 

 

 

The screen shot below shows the site system tree structure, with part of the graphic binding page. Note that for the binding template to work, the bind names used in the graphic must be unique. eg. L6W1_CHB_006 (Unit) and ReturnAirTemp (Point).

 

 

For an Export of this template, click Binding Template Export 2013-08-15 083240.zip.

3 - Binding Template Types examples see the Online Help.

An additional resource is the Exchange Community in particular the following Knowledge Reinforcement Session

Also check out the SmartStruxure-Binding Templates-Lesson 1-7 Quick-Help video on the Exchange.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Binding Template Export 2013-08-15 083240.zip
Tags (1)
  • Find more articles tagged with:
  • 11684
Was this article helpful? Yes No
100% helpful (6/6)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore