Cannot Connect to the Platform on New or Cleaned JACE-8000

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot Connect to the Platform on New or Cleaned JACE-8000
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
12976 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot Connect to the Platform on New or Cleaned JACE-8000

Guinan RandyDavis Guinan
‎2019-09-30 08:32 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:53 AM

Issue

On a new JACE-8000, or on one in which the clean-dist or factory restore procedure has been applied, the JACE can be pinged but, you cannot connect to the platform, and the system time's year shows as 2020 or greater.

 

The following symptomatic messages can be observed in the serial shell via the debug port: 

ERROR [01:26:53 01-Jan-2037] [tid = 1] niagarad: policy file verification failed. Policy files may have been tampered with. Cause is: [/opt/niagara/security/policy/java.security failed signing verification] 
ERROR [01:26:53 01-Jan-2037] [tid = 1] niagarad: throwable occurred while initializing daemon (java.lang.SecurityException), can not continue 
sysmon: niagarad is no longer running 

The following symptomatic messages appear in the system logs: 

Jan 01 01:26:53 2 11111 0 niagarad: policy file verification failed. Policy files may have been tampered with. Cause is: [/opt/niagara/security/policy/java.security failed signing verification] 
Jan 01 01:26:53 2 11111 0 niagarad: throwable occurred while initializing daemon (java.lang.SecurityException), can not continue 
Jan 01 01:26:53 2 11111 4 sysmon: niagarad no longer running

Product Line

TAC IA Series.

Environment

I/A Series Jace-8000

Cause

This issue is encountered when the RTC clock's date is Wednesday, December 30, 2020, or later. 

Resolution

Use the debug port to connect to the system shell with PuTTY. See the System Shell section of the JACE-8000 Install and Startup Guide
Set the system clock to a date before the year 2020, and then commission the JACE with 4.2 or newer. 

The issue is corrected within the fix for the following issue, addressed in Niagara 4.2.36.10:

 

NCCB-19628: Code signing timestamps checked improperly, verification will fail Jan 1, 2021 

 

We will continue to see the issue on new JACE-8000 as they ship with a 4.1 daemon. This may also occur on a JACE-8000 on which the clean-dist or factory restore procedure has been applied.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • RandyDavis19
Was this article helpful? Yes No
92% helpful (11/12)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore