Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 107
    • 108
    • 109
    • …
    • 501
  • Next »

Personnel.csv file fails to import into Continuum

Issue Personnel.csv file fails to import into Continuum No error message is shown Product Line Andover Continuum Environment Continuum access control Keywords: CSV, Import, cardholder, personnel Cause CSV file gets modified by MS excel such that the import fails During the process of manually changing and saving a personnel.csv file within MS excel, a number of commas are added to the first line (corresponding to the number of column fields in the CSV) Resolution Use notepad or similar to delete commas before importing into Continuum as Microsoft Excel does not show up any trailing commas This will NOT import correctly Personnel,,,,, Name,FirstName,LastName,CardNumber,CardType,SiteCode Smith_Fred,Fred,Smith,10,Infinity_37,3701 This will import correctly Personnel Name,FirstName,LastName,CardNumber,CardType,SiteCode Smith_Fred,Fred,Smith,10,Infinity_37,3701 For more information on CSV imports Click Here For an example .csv file for testing Click Here Note: If importing X Driver points using a .csv file the comm port attribute "Port" must always be defined before the X Driver parameters Param1, Param2 etc. The Port must contain the full path e.g. "Network1\CXName\Comm1" Example X Driver Numeric: InfinityNumeric Name,Alias,Format,Description,Port,Param1,Param2,Param3,Param4 XDRPoint1,XDRPoint1,##,First X Driver Point,Network1\CX1\comm4,1,3,10001,1
View full article
Picard Product_Support
‎2018-09-07 08:05 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • Andover Continuum
2442 Views

AVU2201 Replacement

Issue AVU2201 Replacement Product Line Field Device Environment AVU2201 Cause AVU2201 obsolescence, replacement required. Resolution The replacement actuator is the MZ300S-24F actuator.
View full article
Sisko DavidChild Sisko
‎2021-09-27 02:04 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • Field Devices
2515 Views

EBO 3.2.x SNMP Engine ID

Issue EBO 3.2.x SNMP Engine ID seen in EBO 3.2.x is not the one used by the EBO 3.2.x system. Product Line EcoStruxure Building Operation Environment Building Operation Workstation (from v3.2) Building Operation Automation Server (AS-P and AS-B) (from v3.2) SNMP Cause EBO 3.2.1 introduced a new SE3Linux operating system for the AS-P and AS-B servers. The engine ID: seen in Device Administrator or Workstation is the engine ID: contained in Linux, this is not the one used by EBO 3.2.x Resolution The SE3Linux engine ID:  “0x80001f8803005006042bd7” viewed using the Device administrator: The SE3Linux engine ID:  “0x80001f8803005006042bd7” viewed using the Workstation The engine ID used by EBO for this example would be: 0x80002a1d03005006042bd7 The difference is always 2a1d compared to 1f88 and the rest of the bytes are the same. For further information see the attached document SNMP SBO 3.2.x Engine ID Explained.
View full article
Gary Schneider Alumni (Retired)
‎2021-04-23 06:16 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • EcoStruxure Building Operation
2743 Views

Alert, Confirm and Prompt in graphics on Advanced Display

Issue The TGML JavaScript methods alert(), confirm() or prompt() do not work on Advanced Display when using the Webstation app. Nothing happens when the methods are used, and the modal window that is expected is not displayed. See attached TGML file for a graphic example using the JavaScript methods. Product Line EcoStruxure Building Operation Environment Building Operation Advanced Display V2 Building Operation Advanced Display V3 Cause The embedded browser in the Webstation app does not support alert(), confirm() and prompt(). Resolution Use other ways to interact with the user that do not use modal windows. It is also likely that the usability of your graphics will benefit from removing the above mentioned JavaScript methods.
View full article
Janeway PeterEdvik Janeway
‎2020-05-12 02:50 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • EcoStruxure Building Operation
1583 Views

Connecting a serial cable to a Xenta 5/7/9xx controller

Issue Connecting a serial cable to a Xenta 5/7/9xx controller Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause Xenta Servers have a service portal for use with HyperTerminal with a serial connection to the RS-232B port. Resolution Connect a serial cable, Programming Serial Kit, part no. 0-073-0920-0, between the PC and the RS232 port B on the TAC Xenta.  For more information about the cable see Cable Guide OFL-3972. Go to Start/All Programs/Accessories/Communications/HyperTerminal, and open the HyperTerminal. In Connection Description Windows, type any name you like in the Name box. Click OK. In the Connect to window, choose the correct COM port that the RS-232 cable is using. If you do not know which COM port it is using. Go to your computer device manager. (Right click on “My computer” icon, and choose “Manage”. Then under “System Tools”, choose “Device Manager”. Find “Ports (COM & LPT)” and expend it Find the COM port number that is used by the RS-232 cable. Click OK. In the COM Properties window, type 9600 for “Bits per second”, 8 for “Data bits”, “Parity” is None, “Stop bits” is 1, and “Flow control” is None. Click OK. Options: you can save this setting for future use. Click on File Menu and Save. Press ENTER to activate the command prompt. Default username and password is both “root”. Type “root” and press ENTER for both the username and password. Type “setip” and press ENTER. NOTE: Product support has also witnessed strange behavior with serial connections when certain laptops were not plugged into a power source or the Xenta Server was not grounded. If connection problems persist after the connection setting above are verified, make sure the Hyperterminal PC is plugged into a 120 vac power source.
View full article
Picard Product_Support
‎2018-09-07 12:37 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
7823 Views

Determining M-Bus addressing

Issue Addressing issues with M-Bus metering application because it is unclear what Storage# or Tariff# to use in Xbuilder. Environment Xenta 913 5.x.x Xbuilder 5.x.x Cause Manufacturers of meters which utilize the M-Bus protocol may not specify the Storage# or Tariff# needed by Xbuilder. They may instead include DIF or DIFE information regarding their meter points. These codes correspond to the M-Bus protocol and indicate the Storage# and Tariff# of the data. Resolution Use the M-Bus DIF calculator to parse the data type, Storage#, and Tariff# of the data point. This spreadsheet should be sufficient for the majority of applications, but some exceptions apply. The hexadecimal codes for the data point must be provided by the manufacturer for the calculator to be useful.
View full article
Picard Product_Support
‎2018-09-07 07:58 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • TAC Vista
1727 Views

New UNC-520 will not save a changed IP address.

Issue The IP address can be entered into a UNC-520 using the Admin Tool but after rebooting or power cycling the device, the IP address is reset back to the factory default. Environment I/A Series (Niagara) R2 UNC-520-2(-N) with serial number greater than 36183  Cause The newer UNC hardware manages stored OS configuration data in a different manner than the older UNC-520 devices.  Because of this change, the factory default operating system has the capability to read, but not permanently change the device IP address. Resolution You must use the Admin Tool Installation Wizard to install the r2.301.527 (or newer) version of the OS and NRE (system software) before you can save any new Ethernet address information to the UNC. Follow the procedure in the UNC-520 installation manual (F-27391) section "Upgrade, License and Configure the Host" to install the OS and NRE system software.  Click here to see the referenced page of the manual.
View full article
Picard Product_Support
‎2018-09-07 02:34 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • TAC IA Series
1705 Views

Sunrise/Sunset Schedule in Menta

Issue Control HVAC or especially lighting based on the sunrise and sunset times for a given location on a given date, even though this functionality does not exist in Vista like it does in I/NET. Environment Menta Cause Menta/Vista time schedules have no built-in sunrise/sunset capability.  If this is required, it will need to be programmed into a Menta file. Resolution The attached Menta Macro calculates the sunrise and sunset for a given location. Click the picture to download.       Inputs - Menta Simple Blocks Month Date Hour Minute Configurable Parameters Year = Current year.  As Menta has no "Year" block, it must be calculated in the controller and should be set initially for the current year. DST = Does this location participate in Daylight Savings Time?  1=Yes, 0=No. TimeZone = Location's offset in hours from GMT Latitude = Location's latitude in degrees. North is a positive value, south is a negative value. Longitude = Location's longitude in degrees. West is a positive value, east is a negative value. Outputs - Available Data Current minutes past midnight Sunset minutes past midnight Sunset hour Sunset minutes Sunrise minutes past midnight Sunrise hour Sunrise minutes Output integer represents minutes until next transition.  Mimics a Menta time schedule.  Positive values count down minutes until sunrise.  Negative values count down minutes until sunset.
View full article
Picard Product_Support
‎2018-09-06 01:52 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • TAC Vista
2819 Views

BACnet b3 or Infinet i2 controller shows version 0.000000

Issue BACnet b3 or Infinet i2 controller shows version 0.000000 Product Line Andover Continuum Environment BACnet b3 Controller Infinet i2 Controller Cause The Controller is likely to be in bootloader mode, this can be confirmed by looking at the CPU flash speed. If you can count the flashes it is likely to be in bootloader mode see CPU LED flashing rate  Resolution Reflash the controller OS with the firmware compatible with the Continuum installation on site, using "Update b3 OS" or ""Update Infinet2 OS" NOTE - An ACX57 with Comm1 set to Infinet is unlikely to be able to communicate with an i2 device in bootloader mode, in this case an NC2 or other NetController may be required
View full article
Picard Product_Support
‎2018-09-06 02:08 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Labels:
  • Andover Continuum
2699 Views

I/A Series R2 station installed on a JACE-645 retrofit board (TRD-RB-645) fails to run

Issue I/A Series R2 station installed on a JACE-645 retrofit board (TRD-RB-645) fails to run with the following errors Product Line TAC IA Series Environment JACE-645 Retrofit Board (TRD-RB-645) I/A Series R2 version 2.301.535.v1 I/A Series G3 version 3.6.406 Cause The R2 station has not been upgraded to R2 version 2.301.535 using the dbadmin command in the Niagara console. There are errors when converting the upgraded XML version of the station to SNS.  Resolution Ensure that the R2 station is upgraded as per step 3 on page 4 of the Retrofit Board Niagara R2 Install & Startup Guide before copying the station into the JACE-645 retrofit board. 
View full article
Picard Product_Support
‎2018-09-11 12:41 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • TAC IA Series
4278 Views

Using Modbus RTU X Driver to connect to PM700 and PM750 Power meters.

Issue Are examples available to show how to write Plain English programs and create points for a Modbus RTU X Driver linked to Schneider Electric Power meters? Environment Modbus RTU X Driver Schneider Electric PM700, PM750 Power meters. Cause Requirement for some examples to see how Modbus RTU programs can be written to poll for the data in a 3rd party Modbus device. Resolution The attached example was written by an application engineer in the UK to extract data from the Schneider Electric PM700 and PM750 meters. This example provides the mapping of data for these 2 specific meters, but the polling principle utilized in the Plain English programming can be applied to any Modbus RTU interface Download file here. 
View full article
Picard Product_Support
‎2018-09-06 01:42 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • Andover Continuum
2230 Views

How many controllers can be connected to an ASD bus before a repeater is required?

Issue How many controllers can be connected to an ASD bus before a repeater is required? Environment Global controller with an ASD bus connected (GCM, UNC, ENC, LNC-100, SIM-CCN, SIM-MTECH, SIM-TRANE, SIM-YORK) ASD controller (LIM-1,MicroFlo II, MicroZone II, MN-ASDI integrator, PEM-1) Cause Requirements for ASD bus installation. Resolution A maximum of 32 nodes are allowed for each ASD bus segment.  Each controller and repeater count as one node, so a bus segment with a master (GCM, UNC, etc.) and a repeater can have 30 other nodes on it ( MZII, MN-ASDI, etc.) For details, See the Network 8000 Hardware Installation Practices manual, F-23061-1, "Network & Communication Wiring", "Repeaters - RS-485".
View full article
Picard Product_Support
‎2018-09-10 02:48 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • TAC IA Series
1460 Views

Maximum MSTP cable length without a repeater

Issue What is the maximum MSTP cable length without a repeater? Environment Bacnet BCX B3 MSTP Cause Controller was not responding as online. Resolution Below is a document that explains the Maximum Cable Length for MSTP communications without a repeater. Click HERE for document.
View full article
Picard Product_Support
‎2018-09-10 12:16 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • Andover Continuum
1772 Views

Commport is not XDriver enabled.

Issue Getting "Commport is not XDriver enable" error when attaching the driver file to the comm port. Comm port has been flashed to enable XDriver operation. Controller Options shows Xdvr Comm2:00000009 (0000) Product Line Andover Continuum Environment BCX NCI NCII B4920 XDriver Comm Port Cause Bad controller XDriver support flash file. Resolution 1. Take the Workstation offline, edit the comm port, and set the default mode to "XDriver". 2. Go back online and send the comm port to the Controller. 3. Attempt to attach the Driver file to the comm port, if the same error occurs then contact Schneider repair department for a new XDriver option flash file. See article Determine if a controller comm port is XDriver enabled - Communities (se.com) 
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • Andover Continuum
1652 Views

NXT will not communicate using RS-485 port 3

Issue NXT will not communicate using RS-485 port 3 Environment R2/AX Niagara Cause Incorrect documentation of communication port number and RS-485 wiring diagram Resolution New document is available with correct comport number 4 and RS-485 wiring diagram.  To download a copy click on link T-NXT-MtgWiring Guide
View full article
Picard Product_Support
‎2018-09-06 01:24 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • TAC IA Series
6091 Views

Converting Infinity SX8000 objects to Continuum.

Issue How to bring SX8000 objects to Continuum when upgrading. Environment Infinity SX8000 Continuum CyberStation Debug document Cause Upgrading from legacy Infinity SX8000 system to Continuum Resolution See Infinity to Continuum upgrade for information on how to convert Infinity SX8000 objects to Continuum.
View full article
Picard Product_Support
‎2018-09-10 03:48 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • Andover Continuum
3141 Views

Unable to open a time chart via TGML graphic in webstation.

Issue Unable to open a time chart via TGML graphic in webstation. The same graphic works in workstation. Environment TAC Vista 5.1.X - workstation & Webstation TGML Editor 1.1.X Cause Binding to the PV value of a time chart isn't the correct way to do this, but workstation is unable to display a dialogue for an object that has multiple properties and so displays the complete time chart. Resolution A link should be used that is linked to the time chart object Attached is a TGML component adapted from the standard analogue clock component that explains how to do this. The binding should be bound to -your time chart- .PV and the link should be linked to the time chart object. Time_Chart_Link.tgml        
View full article
Picard Product_Support
‎2018-09-10 04:56 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • TAC Vista
1281 Views

Sample PE Optimized Start/Stop routines

Issue While PSS does not write PE for partners we do in some instances provide sample PE code for guidance. This article provides sample PE code for optimized Start/Stop routines. Environment CyberStation All CXs All b3s All i2s Cause Complex PE routines may be difficult to implement without sample. Resolution See Self-adaptive Optimized Start and Optimized Stop Routines Sample PE Code.pdf
View full article
Picard Product_Support
‎2018-09-10 10:10 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • Andover Continuum
2531 Views

String Bindings between Infinet Controllers

Issue String Bindings between Infinet Controllers fail Product Line EcoStruxure Building Operation Environment Infinet Controllers I2 Controller String Transfer Cause Direct string transfers between Infinet Controllers were possible in Continuum (via an import PE Program), but not in EBO via Script Program Resolution Following a Continuum Conversion, direct string transfers (via an import PE Program) downloads correctly but the Strings do not update. This type of transfer is not seen often, but was possible in Continuum. See the Knowledge Base article Passing InfinityString object between Continuum controllers Details in "Infinet Troubleshooting" in "Technical Reference Guide" from version 4.0.2 Also see WebHelp The workarounds are Bind string values direct (object to object), but this will force an EBO transfer via the ASP, so if the AS is not available the transfer will fail. Also more bandwidth is used. Rewrite the script to avoid using string transfers, by using numerical Objects
View full article
Dave_Shore Schneider Alumni (Retired)
‎2021-03-17 07:38 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • EcoStruxure Building Operation
1209 Views

Interfacing M-Bus meters to Modbus

Issue Interfacing M-Bus meters to Modbus. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell Sigma Environment Sigma IC3-Modbus Mbus Modbus Kampstrup Heat Meter Multical 601 Cause Multical 601 M-Bus meters are required to be interfaced with the BMS. Resolution A M-Bus/Modbus converter (RS-485, RS-232 or TCP) and configuration software are required. The converter  and software are available from SyxthSense or similar suppliers. Using the converter and software setup the M-Bus/Modbus system without the BMS system connected. The M-Bus/Modbus converter will automatically assign the M-Bus registers as Modbus registers. From the software note the tables and registers used. Create the Modbus registers as required for the BMS system used. For Sigma - Create the gateway.txt, connect and configure the IC3-Modbus. A sample of the gateway.txt can be downloaded here: MultiCal Modbus Gateway.zip. For further M-Bus information see M-Bus Protocol Information. 
View full article
Picard Product_Support
‎2018-09-10 11:27 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
7685 Views
  • « Previous
    • 1
    • …
    • 107
    • 108
    • 109
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore