Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,853
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1826 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 89
    • 90
    • 91
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

LON communications is intermittent at best on a new installation of a Jace-645.

Issue Replaced a Niagara R2 UNC with a Jace-645 embedded with R2.  LON communications was stable at first but now it is intermittent.  Environment Niagara G3 - AX version 3.6.47 or higher Niagara R2 version 535 Cause The intermittent LON communications issue was identified and a supporting jar file in R2-535 needs to be upgraded. Resolution Replace the lonworks jar file with this updated version:   lonworks-2.301.535c
View full article
Picard Product_Support
‎2018-09-11 01:50 PM

Labels:
  • TAC IA Series
1237 Views

BACnet points are not updating in the UNC after the replacement of a BACnet device.

Issue BACnet points are not updating in the UNC after the replacement of a BACnet device. Environment Niagara R2, UNC 520 Cause Tech replaced a drive from one manufacturer with a drive from a different manufacturer. The BACnet device object in the UNC was reused. Since the replacement drive was not the same model or manufacturer as the one being replaced, the BACnet points between the two devices are different. The points in the replacement device do not match the points in the reused BACnet device object in the UNC. Resolution The solution would be to delete the BACnet device object in the UNC, discover the replacement device and learn it into the UNC.
View full article
Picard Product_Support
‎2018-09-06 09:15 AM

Labels:
  • TAC IA Series
1609 Views

Unable to display Traditional Chinese characters in Workbench graphics and Alarm Portal

Issue Unable to display Traditional Chinese characters in Workbench graphics and Alarm Portal Product Line TAC IA Series Environment I/A Series G3 version 3.7 and 3.8 Cause There was change between I/A Series G3 version 3.6 and 3.7. A lexicon tool was added so that the user could use a default set of lexicons (modules). This is a change in the implantation of lexicons in I/A Series G3. The issue was that the default lexicon module for (zh) did not include the font parameters causing the software to not know how to display the Unicode characters. Resolution The I/A Series  lexicon tool can be used to build and enhance the module by the user for deployment on sites. In addition, the I/A Series G3 still supports the use of the previous mechanism that used lexicon files. The lexicon file basically overrides the default module.  Copy the lexicon zh folder from I/A Series G3 3.6 (\niagara\niagara-3.6.xxx\lexicon\) Create a lexicon folder under '\niagara\niagara-3.7.xxx\' in I/A Series 3.7 (or 3.8) and add zh folder copied in step1. Exit the Alarm Portal, stop the station and close Workbench. Update the system.properties file (see below) which is located in '\niagara\niagara-3.7.xxx\lib\'. Change the field to 'niagara,lang=zh' and save.  # This system property is used to override the the default locale. # If not specified, then the VM will attempt to use a default based # on the current operating system settings. This value should map # to a lexicon directory. niagara.lang=zh Launch Workbench and Alarm Portal and verify that the issue has been resolved. 
View full article
Picard Product_Support
‎2018-09-06 09:14 AM

Labels:
  • TAC IA Series
1238 Views

A BACnet device on the Bacnet internetwork is broadcasting an incorrect time and this is being reflected in the ENC's. How can this be disabled?

Issue A BACnet device on the Bacnet internetwork is broadcasting an incorrect time and this is being reflected in the ENC's. How can this be disabled? Environment G3 ENC's JACE's BAcnet Cause Third party BACnet device broadcasting incorrect time periodically on the internetwork. Resolution By default "Time Synch Allowed" is enabled in the ENC and JACE's.  This can be disabled by the following steps. 1. Open the ENC station  with WorkBench then open Config, Drivers, BacnetNetwork and BacnetComm. 2. Right click on Server and View the Slot sheet. 3. Right click on timeSyncAllowed, right click on ConfigFlags, uncheck the box next to Hidden and click OK.  4. Right click on Server - View - Properties and change Time Synch Allowed to false and save.
View full article
Picard Product_Support
‎2018-09-06 09:14 AM

Labels:
  • TAC IA Series
996 Views

Which versions of SIGNAL can be migrated to SBO?

Issue Which versions of SIGNAL can be migrated to SBO? Environment SIGNAL Cause The migration manual does not identify which versions are accepted. Resolution Two versions of SIGNAL can be backed up and migrated to SBO:  Version 4.4.1 (for Windows 95/98) and Version 5.0.0 (for Windows XP).
View full article
Picard Product_Support
‎2018-09-06 09:13 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
891 Views

I/A Series G3 license cannot be issued for a SoftJace installation because of an incorrect HostID

Issue When submitting a license request for a G3 SoftJace installation, because the HostID provided is for an Enterprise Network Server instead of a SoftJace. Environment I/A Series G3 SoftJace version 3.7.106 I/A Series G3 SoftJace version 3.8.x Cause Installer error.  The nre.properties file is not created properly during the installation. Resolution The nre.properties file should be edited to remove the duplicate softjace product type definition. The file to be edited is c:\niagara\rel\lib\nre.properties which will contain the following text: ######################################################## # # File: nre.properties # # This file contains properties which used # the NRE launch executable # # Revision History # 17 Feb 04 Brian Original # ######################################################## # The list of options separated by spaces to pass thru to the VM java.options=-Xmx256M -XX:MaxPermSize=128M -Dfile.encoding=UTF-8 -Xss256K # This property is used to toggle how the hostid is calculated # for the current installation. If true on a Window's box, then # the hostid will be prefixed with "WinSJ" softjace=false #This is a SoftJace softjace=true To correct the issue, open the file in a text editor and delete the line that reads: softjace=false After saving the file, you can verify that the SoftJace HostID is now generated properly by using the following procedure. Open the SoftJace console window by selecting "Console" under the "TAC IA Series ENC SW" entry in the Windows start menu. In the console window enter the following command: nre -hostid Verify that the displayed HostID begins with WinSJ-  instead of Win-
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • TAC IA Series
1359 Views

Cannot interface to the GE Lighting Control Panel PSLP Object nviPattern and nvoPatternFb with G3 lonGe-3.8.37.

Issue Cannot interface to the GE Lighting Control Panel PSLP Object nviPattern and nvoPatternFb with G3 lonGe-3.8.37.  Network variables nviPattern, nvoPatternFb, and nciChannelCfg are missing from the proxy points within the object definition. Environment I/A Series G3 - 3.8.37 Cause Network variables nviPattern, nvoPatternFb, and nciChannelCfg are based upon manufacturer types (GEPatternType and GEChType) and are not properly defined in the lonGe 3.8.37 module. The pslp object within the lonGe module generates warnings when added. WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nviPattern WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nvoPatternFb WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_0 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_1 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_2 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_3 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_4 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_5 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_6 WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_7 Resolution Upgrade to lonGe-3.8.38.1.   The updated module is available for download from the Schneider Electric Download Center. https://ecobuilding.schneider-electric.com/search?documentUUID=c52247c8-921b-4f51-90cf-d8d79adc93b7&title=lonGe%203.8.38.1%20-%20G3%20Firmware
View full article
Picard Product_Support
‎2018-09-11 01:22 PM

Labels:
  • TAC IA Series
1457 Views

What are the definitions for the enumerated value representing CTSTS (control status) for the Network 8000 MicroNet FLO2 controller?

Issue What are the definitions for the enumerated value representing CTSTS (control status) for the Network 8000 MicroNet FLO2 controller? Environment IA Series G3 tacAsd driver Cause CTSTS is displayed as an enumerated value and the associated definition is not provide. Resolution The definitions for CTSTS (control status) are: Hex - Decimal - Definition 0x00 0  CAL 0x01 1  UNOFF 0x02 2  WRMUP 0x03 3  REV 0x04 4  COOL 0x05 5  CLMX 0x06 6  CLMN 0x07 7  HEAT 0x08 8  HTMX 0x09 9  HTINT 0x0A 10  FOPN 0x0B 11  FCLS 0x0C 12  FMX 0x0D 13  FMN 0x0E 14  FFAN 0x0F 15  GFOPN 0x10 16  GFCLS 0x11 17  FGMX 0x12 18  GFMN 0x13 19  CALDP 0x14 20  DIAG
View full article
Picard Product_Support
‎2018-09-06 09:10 AM

Labels:
  • TAC IA Series
1535 Views

Integrating a SE7200F5045E to Niagara G3 / AX. Which snvt can be used to display the current setpoint?

Issue Integrating a SE7200F5045E to Niagara G3 / AX. The tenant can change the occupied heating or cooling setpoint locally.  Which snvt can be used to display the current setpoint? Environment Niagara G3 Niagara R2 SE7200 series Cause Application question - wants to plot the proper setpoint on the graphic Resolution The nciSetpts snvt displays the current setpoints used by the SE7200 for heating and cooling in both occupied and unoccupied modes. Note:  The tenant can only change the occupied heating and cooling setpoints from the local keypad / display.
View full article
Picard Product_Support
‎2018-09-06 09:10 AM

Labels:
  • EcoStruxure Building Expert
  • TAC IA Series
1324 Views

What does block attribute EMSCO control in a Network 8000 MicoFlo II controller?

Issue A job site is being retrofitted for SmartStruxure. It currently uses Network 8000. When the GCM is removed, the existing MicroFlo II controllers must control individually until a SmartStruxure AS is ready. Can the EMSCO attribute be used to switch to local control until the AS is online? Product Line TAC IA Series Environment Network 8000 MicroFlo II controller Cause Standalone control requirements Resolution From the MicroFlo II Engineering Manual (F-23119): EMS CONTROL [EMSCO] * default = OFF If this input is ON, the MICROFLO II controller will operate from the GCM's setpoints. If this input is OFF, the local setpoints are used. If the input goes ABNORMAL or NOT ACTIVE the controller will treat it as an OFF. Under typical operation, EMSCO is ON and setpoints from the GCM are used. The moment it switches to OFF (ie: loss of communication to a GCM), the local setpoints will be used. At this job site, ensure the local setpoints are identical to the GCM-based setpoints so that when the GCM is removed and EMSCO switches to OFF, the MicroFlo II continues to control. This will provide temporary control until an AS is brought online. There are other 'EMS'-based attributes that should also be reviewed depending on how applicable they are to VAV control at a job site. See the engineering manual for more information.
View full article
Picard Product_Support
‎2018-09-06 09:08 AM

Labels:
  • TAC IA Series
1184 Views

Does the Niagara R2 Transition Tool convert graphics?

Issue Does the Niagara R2 Transition Tool convert graphics? Environment Niagara R2 StruxureWare Building Operation Cause Product inquiry Resolution The tool does not convert graphical images.  It does convert bindings to inputs of a GxPage.  See the R2 Transition Guide (F-27835) for more details.  An excerpt from the guide follows: 3.4.3 GxPage The TAC I/A Series R2 GxPage object is converted to a Building Operation Graphic object. The converted Graphic object contains a Dynamic Text object for each dynamic Gx object at the coordinates of the corresponding Gx object from the GxPage. The Dynamic Text objects in the Building Operation Graphic are named to match the corresponding Gx objects from the GxPage. Graphical images from the GxPage are not converted to the Building Operation database. Bindings to inputs of the GxPage are converted to the Building Operation database as links to the corresponding Dynamic Text objects within the converted Graphic.
View full article
Picard Product_Support
‎2018-09-11 01:01 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1195 Views

Niagara R2 Transition Tool list of R2 Functionality that transitions and does not transition

Issue Niagara R2 Transition Tool list of R2 Functionality that transitions and does not transition Product Line EcoStruxure Building Operation, TAC IA Series Environment Niagara R2 StruxureWare Building Operation Cause Quick Reference Resolution From page 15 of the R2 Transition Tool Guide (F-27835): TAC I/A Series R2 Functionality That is Transitioned Certain functionality is transitioned to Building Operation: Common control functions BACnet/IP network BACnet MS/TP networks 1 and 2 BACnet MS/TP networks 3 and 4 as routed networks BACnet device objects BACnet shadow objects Container and object tree structure LonWorks Service LonWorks networks LonWorks device objects V2.x Standard MNL LON devices V3.x Standard MNL LON devices V4.x Standard MNL LON devices and associated application files MNL-800 LON devices and associated application files R2 Local LON Device SNVTs Many type conversion, LON multiplexer and demultiplexer objects IbsASDNetwork Service ASD network ASD Device objects TAC I/A Series R2 Functionality Not Transitioned Not all UNC functionality can be transitioned to Building Operation. This functionality is listed in the Objects report. Functionality that is not transitioned includes: BACnet Ethernet network User accounts Address book Security Trigger mechanisms TRIPL program object runtime Object bundling Command objects Right-click commands Communications other than BACnet, ASD, or LonWorks Configurable routers and repeaters LON manufacturer specific control and conversion objects External LON Network Management Tool support UNC physical points (UNC-410 NDIO)
View full article
Picard Product_Support
‎2018-09-11 01:08 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1499 Views

Does the MNB-1000 have a point archiving feature?

Issue Does the MNB-1000 have a point archiving feature? Environment MNB-1000 (all firmware revisions) Cause Field request (for troubleshooting) Resolution The MNB-1000 does not come with any point archiving features.  That would have to be provided at the network level (i.e. SmartStruxure AS).
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • TAC IA Series
1140 Views

How to broadcast a value from one MicroSmart controller to other MicroSmart controllers under the same DMS.

Issue The sending MicroSmart controller has revision 9 firmware.  The receiving MicroSmart controllers have revision 10 and revision 11 firmware.  How can a point value be broadcast? Environment MicroSmart controllers Cause Peer-to-peer sharing of data was introduced to the MicroSmart controllers with revision 10 firmware. In this scenario, the revision 9 controller cannot broadcast (or receive) peer-to-peer. Resolution Link the sending point and the receiving points to the DMS. Depending on the programming, use the sending DMS point with the receiving DMS point and the value will be available down in the MicroSmart controller.
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Labels:
  • TAC IA Series
909 Views

WorkPlace Tech will not recognize the Echelon U10 USB Lon Network Interface adapter.

Issue WorkPlace Tech will not recognize the Echelon U10 USB Lon Network Interface adapter. The “Loading Device Driver” is displayed but nothing happens after that. Environment WorkPlace Tech 5.8.x Cause LON1 port may have been previously assigned to another LON interface. Resolution 1. Make sure the Echelon Open LVD 4.0 is installed on PC. 2. Close WorkPlace Tech if open 3. Disconnect the Echelon Lon USB adapter from the PC. 4. Open Control Panel and open LonWorks Interfaces 5. Select View from the Menu and check “Show Detached Interfaces” 6. Highlight LON1 in the tree and click the “Remove” from the menu        - Click Yes in the “Confirm Removal” window to remove the detach device 7. While in same widow, reconnect the Echelon USB Lon Adapter to the PC        - The messages: “Installing device driver” will display in the system tray followed by “Echelon USB Network Interface Installed.        - The LON1 interface should now be displayed You can test the communication if you like Now open WorkPlace Tech and you should be able to discover the LON devices.  
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Labels:
  • TAC IA Series
3941 Views

"Invalid status code: 401 Access Denied" on "Save Runtime DB" of the localhost

Issue Getting an "Invalid status code: 401 Access Denied" error when doing a "Save Runtime DB" of the localhost or a "Get" to save a remote UNC station to the localhost. The errors read: Error when doing a “Save Runtime DB” of localhost station:  tridium.nre.net.HttpException: Invalid status code: 401 (Access denied)            at tridium.ui.admintool.DbAdminConfigPanel.doRemoteBackup(DbAdminConfigPanel.java:1100)            at tridium.ui.admintool.DbAdminConfigPanel$Worker.run(DbAdminConfigPanel.java:1224) Error when doing a “Get” of a remote UNC station:            java.io.FileNotFoundException: c:\niagara\r2.301.535\stations\anystation\config.sns (Access is denied)            at java.io.FileOutputStream.open(Native Method)            at java.io.FileOutputStream.(Unknown Source)            at java.io.FileOutputStream.(Unknown Source)            at tridium.ui.admintool.DbAdminConfigPanel.doOnlineGet(DbAdminConfigPanel.java:848)            at tridium.ui.admintool.DbAdminConfigPanel.doGet(DbAdminConfigPanel.java:764)            at tridium.ui.admintool.DbAdminConfigPanel$Worker.run(DbAdminConfigPanel.java:1216) Product Line TAC IA Series Environment WorkPlace Pro ES UNC Cause Either the username or password, or both, being used are invalid. A valid username and password must be entered to perform a "Save Runtime DB" of the localhost, or a "Get" to save a remote station to the localhost. Resolution Use a valid station username and password to perform these functions on the localhost.  
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Labels:
  • TAC IA Series
1427 Views

Can R2 BACnet alarms be sent to and acknowledged from a G3 Server console.

Issue Can R2 BACnet alarms be sent to and acknowledged from a G3 Server console. Environment Niagara R2 UNC, Niagara G3 ENS Cause Want to be able to view and acknowledge R2 BACnet Alarms from in a G3 console. Resolution This can be accomplished by using the BACnetRecipient object in R2. Follow the steps listed in the “Configuring for BACnet Alarm Generation” section of the R2 BACnet Integration Reference guide. The part most forget is adding the G3 station as a BACnet device under the R2 BACnetService, and adding the UNCs as a BACnet device under the G3 NiagaraNetwork  
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Labels:
  • TAC IA Series
1350 Views

G3 station will not email alarms to intended recipients.

Issue G3 station will not email alarms to intended recipients. Getting “java.security.cert.CertificateException: failed certificate validation” error in the station Application Director window. The error reads: mail.MessagingException: Could not connect to SMTP host: outbound.att.net, port: 465; nested exception is: javax.net.ssl.SSLHandshakeException: java.security.cert.CertificateException: failed certificate validation, at com.sun.mail.smtp.SMTPTransport.openServer(SMTPTransport.java:1972) at com.sun.mail.smtp.SMTPTransport.protocolConnect(SMTPTransport.java:642) at javax.mail.Service.connect(Service.java:317) at javax.mail.Service.connect(Service.java:176) at javax.mail.Service.connect(Service.java:125) at javax.baja.email.BOutgoingAccount.pollQueue(BOutgoingAccount.java:769) at javax.baja.email.BOutgoingAccount.poll(BOutgoingAccount.java:715) at javax.baja.email.BEmailAccount.doPoll(BEmailAccount.java:567) at javax.baja.email.BEmailAccount.access$0(BEmailAccount.java:36) at javax.baja.email.BEmailAccount$Poller.run(BEmailAccount.java:617) Caused by: javax.net.ssl.SSLHandshakeException: java.security.cert.CertificateException: failed certificate validation, at sun.security.ssl.Alerts.getSSLException(Alerts.java:192) at sun.security.ssl.SSLSocketImpl.fatal(SSLSocketImpl.java:1884) at sun.security.ssl.Handshaker.fatalSE(Handshaker.java:276) at sun.security.ssl.Handshaker.fatalSE(Handshaker.java:270) at sun.security.ssl.ClientHandshaker.serverCertificate(ClientHandshaker.java:1341) at sun.security.ssl.ClientHandshaker.processMessage(ClientHandshaker.java:153) at sun.security.ssl.Handshaker.processLoop(Handshaker.java:868) at sun.security.ssl.Handshaker.process_record(Handshaker.java:804) at sun.security.ssl.SSLSocketImpl.readRecord(SSLSocketImpl.java:1016) at sun.security.ssl.SSLSocketImpl.performInitialHandshake(SSLSocketImpl.java:1312) at sun.security.ssl.SSLSocketImpl.startHandshake(SSLSocketImpl.java:1339) at sun.security.ssl.SSLSocketImpl.startHandshake(SSLSocketImpl.java:1323) at com.tridium.crypto.core.io.CryptoCoreClientSocketFactory$NSSLSocket.startHandshake(CryptoCoreClientSocketFactory.java:334) at com.sun.mail.util.SocketFetcher.configureSSLSocket(SocketFetcher.java:548) at com.sun.mail.util.SocketFetcher.createSocket(SocketFetcher.java:352) at com.sun.mail.util.SocketFetcher.getSocket(SocketFetcher.java:207) at com.sun.mail.smtp.SMTPTransport.openServer(SMTPTransport.java:1938)   Environment Niagara G3 3.8.37, ENS, ENC Cause The security certificate for the SMTP server has not been accepted/approved. This error was seen when attempting to connect to the outbound.att.net SMTP server. It may apply to other SMTP server as well. Resolution Check to see if there’s a certificate for the mail server and if it has been approved. - Open the station’s Platform and select ‘Certificate Management’. - Select the Allowed Hosts tab. - Look for host named ‘outbound.att.net’ (it’s probably has not been approved) - Right-click on it and select ‘Approve’ - Select ‘Yes’ for the messages ‘Are you sure you want to approve the selected exemption(s)?’ To send or clear queued emails: - Double-click on the station’s ‘EmailService’ - Right-click on the OutgoingAccount and select ‘Actions’ and then ‘Send’ or ‘Clear Alarms’ If it was a certificate issue, you should now be able to send emails to the SMTP server.  
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Labels:
  • TAC IA Series
1506 Views

A graphic on an InVue client computer does not match the same graphic on the InVue server. How can it be updated?

Issue One graphic is not the same on the InVue client computer as it is on the InVue server.  InVue Viewer has been re-started on the client computer which initiates an automatic file transfer from the server.  But the graphic is still different.  How can the graphic be updated on the client? Environment InVue Cause The graphic is not considered a 'modified' graphic so it doesn't automatically transfer to the client computer. Resolution Open InVue Developer and modify the graphic slightly and then save it.  Use 'Notify Clients' under the 'Special' dropdown to propagate the modified graphic to the client computer.
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Labels:
  • TAC IA Series
1260 Views

When converting a station from R2 v522 to v535 getting error: "Link is not valid: Link invalid for unknown reason".

Issue When converting a station from R2 v522 to v535 getting error: "Link is not valid: Link invalid for unknown reason". Environment R2 UNC and WPP Cause The v535 LonExtras jar is not correctly handling converting  links that reference SNVT type FlexSnvtTempSetpts. Resolution Download and Install the v532a LonExtras jars in WPP.   Convert the station successfully then install v532a lonExtras jar and the station in the UNC.
View full article
Picard Product_Support
‎2018-09-06 09:04 AM

Labels:
  • TAC IA Series
1064 Views
  • « Previous
    • 1
    • …
    • 89
    • 90
    • 91
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of