Issue
Cannot interface to the GE Lighting Control Panel PSLP Object nviPattern and nvoPatternFb with G3 lonGe-3.8.37. Network variables nviPattern, nvoPatternFb, and nciChannelCfg are missing from the proxy points within the object definition.
Environment
I/A Series G3 - 3.8.37
Cause
Network variables nviPattern, nvoPatternFb, and nciChannelCfg are based upon manufacturer types (GEPatternType and GEChType) and are not properly defined in the lonGe 3.8.37 module.
The pslp object within the lonGe module generates warnings when added.
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nviPattern
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nvoPatternFb
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_0
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_1
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_2
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_3
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_4
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_5
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_6
WARNING [09:03:14 16-Dec-14 CST][lon1.DynaDev] No lonData for PsLp.nciChannelCfg_7
Resolution
Upgrade to lonGe-3.8.38.1. The updated module is available for download from the Schneider Electric Download Center.