Issue
Niagara R2 Transition Tool list of R2 Functionality that transitions and does not transition
Product Line
EcoStruxure Building Operation, TAC IA Series
Environment
- Niagara R2
- StruxureWare Building Operation
Cause
Quick Reference
Resolution
From page 15 of the R2 Transition Tool Guide (F-27835):
TAC I/A Series R2 Functionality That is Transitioned
Certain functionality is transitioned to Building Operation:
- Common control functions
- BACnet/IP network
- BACnet MS/TP networks 1 and 2
- BACnet MS/TP networks 3 and 4 as routed networks
- BACnet device objects
- BACnet shadow objects
- Container and object tree structure
- LonWorks Service
- LonWorks networks
- LonWorks device objects
- V2.x Standard MNL LON devices
- V3.x Standard MNL LON devices
- V4.x Standard MNL LON devices and associated application files
- MNL-800 LON devices and associated application files
- R2 Local LON Device SNVTs
- Many type conversion, LON multiplexer and demultiplexer objects
- IbsASDNetwork Service
- ASD network
- ASD Device objects
TAC I/A Series R2 Functionality Not Transitioned
Not all UNC functionality can be transitioned to Building Operation. This functionality is listed in the Objects report.
Functionality that is not transitioned includes:
- BACnet Ethernet network
- User accounts
- Address book
- Security
- Trigger mechanisms
- TRIPL program object runtime
- Object bundling
- Command objects
- Right-click commands
- Communications other than BACnet, ASD, or LonWorks
- Configurable routers and repeaters
- LON manufacturer specific control and conversion objects
- External LON Network Management Tool support
- UNC physical points (UNC-410 NDIO)