Issue
Can R2 BACnet alarms be sent to and acknowledged from a G3 Server console.
Environment
Niagara R2 UNC, Niagara G3 ENS
Cause
Want to be able to view and acknowledge R2 BACnet Alarms from in a G3 console.
Resolution
This can be accomplished by using the BACnetRecipient object in R2.
Follow the steps listed in the “Configuring for BACnet Alarm Generation” section of the R2 BACnet Integration Reference guide.
The part most forget is adding the G3 station as a BACnet device under the R2 BACnetService, and adding the UNCs as a BACnet device under the G3 NiagaraNetwork