LON communications is intermittent at best on a new installation of a Jace-645.
  • LON communications is intermittent at best on a new installation of a Jace-645.
‎2018-09-11 01:50 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:50 AM
Replaced a Niagara R2 UNC with a Jace-645 embedded with R2.  LON communications was stable at first but now it is intermittent.
Niagara G3 - AX version 3.6.47 or higher
Niagara R2 version 535
The intermittent LON communications issue was identified and a supporting jar file in R2-535 needs to be upgraded.
Replace the lonworks jar file with this updated version:
lonworks-2.301.535c