Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,845
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1824 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 71
    • 72
    • 73
    • …
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

Can the B&B Electronics Converter Model # 485OT9L be used to connect PSI 4.1 to a Network 8000 Microzone II?

Issue Aside from the recommended models from B&B Electronics, can Model # 485OT9L be configured to work with PSI 4.1? Product Line TAC IA Series Environment PSI 4.1 Network 8000 ASD devices (Microzone II, MicroFlo II) Cause On a jobsite and the only model available is the 485OT9L. Resolution It can work by using the following settings for the on-board configuration switches: Switches 1-4:  19200 baud (SW1=off, SW2=off, SW3=on, SW4=off) Switch 5:  Echo off (SW5=off) Switch 6:  Half-duplex (SW6=on) Switch 7:  Half-duplex (SW7=on) Switch 8:  Term Resistance (SW8=off) Jumper 1:  JP1=SD Note:  Model # 485OT9L was discontinued by B&B Electronics in Sept. 2011
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Labels:
  • TAC IA Series
1302 Views

Unable to display Traditional Chinese characters when accessing graphics in an ENC via a web browser

Issue Unable to display Traditional Chinese characters when accessing graphics in an ENC via a web browser Does I/A Series G3 provide non-English language support? Environment I/A Series G3 Enterprise Network Controller (ENC). Cause I/A Series G3 provides non-English language support by use of lexicons. Lexicons are identified by Java locale codes, such as “fr” (French) or “de” (German). The lexicon 'Zh' was not installed into the ENC. Resolution I/A Series G3 provides non-English language support by use of lexicons. Lexicons are identified by Java locale codes, such as “fr” (French) or “de” (German). The lexicon 'Zh' is for Chinese. This needs to be installed into the ENC. Open the ENC Platform. Expand Platform and go to the 'Lexicon Installer'. Click on the 'Install' button, select the lexicon folder you need and click 'OK'. The selected lexicon is now installed in the ENC.   * This article may apply to issues with other languages and not just Traditional Chinese.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Labels:
  • TAC IA Series
1166 Views

Does the database file for a ProView display vary in size based on the amount of programming done to it with Niagara R2?

Issue Does the database file for a ProView display vary in size based on the amount of programming done to it with Niagara R2? Environment Niagara R2 all versions ProView Cause Observation:  A backup of an empty ProView display and a backup of a ProView display programmed with 30+ screens and dozens of bindings produced the same file size:  49 kB. Resolution No. A backup database file from any ProView display, using the Niagara R2 wizard, will be 49 kB in size, whether the display is empty or has been extensively programmed.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Labels:
  • TAC IA Series
1113 Views

Attempting to start I/A Series G3 Workbench generates the following error - Exception in thread "main" java.lang.NoClassDefFoundError: com/tridium/sys/Nre caused by: ja...

Issue Attempting to start I/A Series G3 Workbench generates the following error: Exception in thread "main" java.lang.NoClassDefFoundError: com/tridium/sys/Nre Caused by: java.lang.ClassNotFoundException: com.tridium.sys.Nre         at java.net.URLClassLoader$1.run(Unknown Source)         at java.security.AccessController.doPrivileged(Native Method)         at java.net.URLClassLoader.findClass(Unknown Source)         at java.lang.ClassLoader.loadClass(Unknown Source)         at sun.misc.Launcher$AppClassLoader.loadClass(Unknown Source)         at java.lang.ClassLoader.loadClass(Unknown Source)         at java.lang.ClassLoader.loadClassInternal(Unknown Source) Environment I/A Series G3 Workbench (all versions) Cause The software is unable to locate class files provided within the baja.jar file.  The baja.jar is missing from the Niagara G3 module folder. Resolution Re-install Niagara and verify the path for installation is correct.  If this does not correct the issue, manually copy all files from the I/A Series G3 installation CD module folder into the appropriate modules folder on the target computer.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Labels:
  • TAC IA Series
1680 Views

How do I get a LonWorks license for an Enterprise Server station?

Issue Wants to run old UNC-600 station as an enterprise server but the license does not include LON.  How do you order it? Environment I/A Series R2 Enterprise Server I/A Series SoftJace Cause Customer wants to migrate a UNC-600 station to an enterprise server.  The UNC-600 was already providing the needed database services so the station cannot be directly moved to a UNC.  Even without the database service, the station may be too large for one UNC-520. Resolution Tridium does not make the LonWorks license available for the Enterprise Server or for the SoftJace.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Labels:
  • TAC IA Series
992 Views

I/A Series G3 Enterprise Network Server (ENS) learned proxy point does not properly inherit the maximum override duration facet setting configured for the point or points at the ...

Issue I/A Series G3 Enterprise Network Server (ENS) learned proxy point does not properly inherit the maximum override duration facet setting configured point or points at the ENC.  Environment I/A Series G3 versions 3.5.xx and earlier Cause The mechanism within the core G3 software that controls the inheritance of the maxOverrideDuration facet for a learned proxy point was not added until 3.6.31. Resolution Upgrade the I/A Series G3 Enterprise Network Server (ENS) and ENC to version 3.6.31 or higher.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Labels:
  • TAC IA Series
996 Views

Hardware platforms to replace the I/A Series R2 UNC-600 or UNC-610

Issue What hardware platform can be used to replace the I/A Series R2 UNC-600 or UNC-610? Product Line TAC IA Series Environment I/A Series R2 UNC-600 UNC-610 Cause The I/A Series R2 UNC-600 and UNC-610 are obsolete and can no longer be repaired. Resolution The JACE-NXT (TRD-NXT-R2) can be considered the replacement for a UNC-6xx. The JACE-NXT includes (2) 10/100 Mb Ethernet ports and (1) RS-232 port, one isolated RS-485 port, one FTT-10A LonWorks interface, four USB ports, a 250 GB hard drive and includes a Windows XP Embedded operating system. Similar to the UNC-610 the JACE-NXT supports LonWorks and BACnet Ethernet / BACnet IP. Legacy driver support includes GCM, ASD, and DMS. Note: The JACE-NXT will not directly support BACnet MSTP or MicroSmart devices. The JACE-NXT requires installation of R2 Release 2.301.532 or higher. TRD-NXT-UI (Web Browser Support) TRD-NXT-UPS (Optional UPS - includes UPS unit and battery)
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
1593 Views

The unlock code for a TreeTech 3.1 installation does not work.

Issue TreeTech 3.1 is installed on a Windows 7-32 bit computer.  After receiving the unlock code and entering it, a pop-up error window appears stating "Cannot Access Registry". Environment TreeTech 3.1 Windows 7-32 bit Cause The Windows user account was not configured for a password. Resolution Modify the Windows user account to ensure it has administrative rights and that it has a non-blank password.
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
787 Views

After installing an upgraded I/A Series G3 license, the system does not allow access to the updated features.

Issue Installing an updated I/A Series G3 license does not enable options updated in the new license. Environment I/A Series G3 Workbench or G3 Enterprise Network Server (all versions) Cause When installing a new I/A Series G3 license, it may be necessary to restart the NiagaraD service before the updates contained in the license take effect.  This issue is most often noticed when a demo license update is installed after the previous demo license has expired. Resolution After installing an upgraded license, regardless of whether the license was installed automatically from the license server or manually, stop and restart the NiagaraD service.  The NiagaraD service can be restarted either from the Windows Services control panel applet or by using the Install Niagara Platform Daemon.
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
952 Views

I/A Series R2 Soft JACE - Unable to select and define as a Soft JACE during the installation process on a Windows 7 32-bit operating system.

Issue I/A Series R2 Soft JACE - Unable to select and define as a Soft JACE during the installation process on a Windows 7 32-bit operating system. Environment I/A Series R2 Soft JACE (build 529 or higher) Cause The I/A Series R2 installation utility does not recognize the Windows 7 operating system as a platform for the Soft JACE and bypasses the associated Soft JACE selection screen. The software is properly installed, however the licensing mechanism is unable to use the R2 Soft JACE dongle. Resolution Continue the installation of the I/A Series R2 software (as would be similar to installing the R2 Enterprise Server). Upon start, the software will generate a standard host ID (xxxx-xxxx).  Note: The I/A Series R2 Soft JACE license dongle will not be used. Fill out the associated I/A Series R2 Soft JACE license form with the new host ID and jobsite information. Forms can be found on both the iPortal and The Exchange Download Center websites. iPortal https://iportal2.schneider-electric.com  - Login and navigate to Tools & Support > Tools and select Manage Forms. The Exchange Extranet - IA Series R2 License Forms v6.6 - 112013 The license request can be emailed to the following address.  IASeries.License@schneider-electric.com   *Note (added September 2018) - The I/A Series R2 Product LIne has been discontinued and it is no longer possible to request or generate and I/A Series R2 licenses. Refer to PA-00458 I/A Series R2 Licensing. 
View full article
Picard Product_Support
‎2018-09-10 08:41 PM

Labels:
  • TAC IA Series
1001 Views

How do I order a BACnet MS/TP licence for an ENC-410?

Issue Needs to add two MNB-300 controllers under an ENC-410.  How do I order the license? Environment ENC-410 Cause Needs to add some MNB-300 controllers under an existing ENC-410. Resolution According to our published literature, the ENC-410 does not support BACnet MS/TP because the RS-485 port is not isolated. If it becomes absolutely necessary to license an ENC-410 for BACnet MS/TP, you must submit a written or emailed request to the I/A Series G3 product marketing manager.  The product marketing manager may approve or deny the request based on the information contained in your request.  If approved, he will provide ordering and pricing information.
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
911 Views

Getting the error "Class not found exception: com.microsoft.sqlserver:jdbt.sqlserverdriver" when attempting to convert a Cloudscape database to SQL 2005 in the Niagar...

Issue Getting the error “Class not found exception: com.microsoft.sqlserver:jdbt.sqlserverdriver” when attempting the convert a Cloudscape database to SQL 2005 in the Niagara R2 console window. Environment Niagara R2, WorkPlace Pro version 529 and higher, Windows SQL 2005 Cause The wrong command was entered in the Niagara Command Line window (the console). The following was entered at the prompt: “dbadmin station_name m cs ms host_IP:TCP_port username password”. The “ms” portion of the command is used with SQL versions prior to SQL 2005. The “ms” portion of the command line should read “msj”, which SQL 2005 requires. Resolution Open the console and re-enter the correct migration command. 1. Open the console window 2. Type the following in the Command Line: dbadmin "station_name" m cs msj host_IP:TCP_port# username password 3. Enter The database migration should be displayed in the console window.  
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
1210 Views

Error "java.sql.SQLException: Invalid object name 'STATION_NAME.dbo.sysobjects'."

Issue The following error asserts when attempting to convert a Cloudscape database to SQL 2005 in the Niagara R2 console window: java.sql.SQLException: Invalid object name STATION_NAME.dbo.sysobjects'. at net.sourceforge.jtds.jdbc.SQLDiagnostic.addDiagnostic(SQLDiagnostic.java:368) at net.sourceforge.jtds.jdbc.TdsCore.tdsErrorToken(TdsCore.java:2816) at net.sourceforge.jtds.jdbc.TdsCore.nextToken(TdsCore.java:2254) at net.sourceforge.jtds.jdbc.TdsCore.getMoreResults(TdsCore.java:631) at net.sourceforge.jtds.jdbc.JtdsStatement.executeSQLQuery(JtdsStatement.java:477) at net.sourceforge.jtds.jdbc.JtdsPreparedStatement.executeQuery(JtdsPreparedStatement.java:777) at tridium.util.MSSqlServer.doesTableExist(MSSqlServer.java:341) at tridium.util.MSSqlServer.checkTableWithKey(MSSqlServer.java:316) at tridium.datax.sql.DxSqlUtil.checkTableWithKey(DxSqlUtil.java:190) at tridium.datax.sql.DxSqlUtil.checkTable(DxSqlUtil.java:173) at tridium.tools.DbAdmin.migrateData(DbAdmin.java:1007) at tridium.tools.DbAdmin.main(DbAdmin.java:198) at tridium.tools.DbAdmin.main(DbAdmin.java:122) at sun.reflect.NativeMethodAccessorImpl.invoke0(Native Method) at sun.reflect.NativeMethodAccessorImpl.invoke(Unknown Source) at sun.reflect.DelegatingMethodAccessorImpl.invoke(Unknown Source) at java.lang.reflect.Method.invoke(Unknown Source) at tridium.nre.Nre.mainImpl(Nre.java:663) at tridium.nre.Nre.main(Nre.java:603) Environment Niagara R2 WorkPlace Pro version 529 and higher Windows SQL 2005 Cause The Enterprise Server and SQL 2005 database names do not match. The Enterprise Server and SQL 2005 database names have to be the same when migrating the Cloudscape database to a SQL 2005 database. Resolution Rename either the Enterprise Server station or SQL Server database so that the names are the same. Once the names are the same, the migration should go without issues.
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
4306 Views

TreeTech 3.1 & 3.2 GCM/LCM block compatibility

Issue Does TreeTech version 3.1 & 3.2 support all block types in all types of GCMs and LCMs? Product Line TAC IA Series Environment TreeTech version 3.1 or 3.2 GCM-84xxx GCM-86xxx SIM-xxxxx LNC GIM-2100 LCM-8xxxx Cause Block types supported are not listed in the Tree-Tech Engineering Guide document, F-26640 Resolution The following table lists the sub-devices supported by TreeTech 3.1 or 3.2 for each Network 8000 device type. GCM (rev 4.x & 5.x) ASDGCM (rev 4.x & 5.x) GIM-2100 / SIM-GCM (All rev)  LCM (rev 4.x)  LCM (rev 4.x)  MICROZONE-II  LCM (rev. 5.x)  LCM (rev 5.x)  PEM    MICROZONE-II  LIM    PEM      LIM   The following table lists the block types supported by each device family.  GCM 4.X ASD-GCM 4.X GCM 5.X ASD-GCM 5.X GIM-2100 SIM-GCM LCM 4.X/5.X AI AIPLC ALARM AO AOPLC APT BTUH CALEN COS CURVE DAILY DCC DEGDA DELAY DI DIPLC DO DOPLC DPT EDL EMS ENTHL FLOW HILO HOLI LIMIT LOGIC LOOP MATH MOMEN MTR MZHP1 MZONE MZRT1 MZSAT MZST1 OSS POLL PULSE PWM RAMP RESET RLCM RNET SEQ SGCM SLECT SNET SYS TOTAL TREND TSTAT VVBOX WEEK   ALARM AO APT BTUH CALEN COS CURVE DAILY DCC DEGDA DELAY DO DPT EDL EMS ENTHL FLO2 FLOW HILO HOLI LIM LIMIT LOGIC LOOP MATH MOMEN MTR OSS PEM1 POLL PWM RAMP RESET RLCM RNET SEQ SGCM SGRP SGRP2 SLECT SNET SYS TOTAL TREND TSTAT WEEK ZONE2   AI AIPLC ALARM AO AOPLC APT BTUH CALEN COS CURVE DAILY DCC DEGDA DELAY DI DIPLC DO DOPLC DPT EDL EMS ENTHL FLOW HILO HOLI LABEL LIMIT LOGIC LOOP MATH MOMEN MTR MZHP1 MZONE MZRT1 MZSAT MZST1 NIM NSCHD OSS POLL PULSE PWM RAMP RESET RLCM RNET SEQ SGCM SLECT SNET SYS TOTAL TREND TSTAT VVBOX WEEK   ALARM AO APT BTUH CALEN COS CURVE DAILY DCC DEGDA DELAY DO DPT EDL EMS ENTHL FLO2 FLOW HILO HOLI LABEL LIM LIMIT LOGIC LOOP MATH MN MNFLO MOMEN MTR NIM NSCHD OSS PEM1 POLL PWM RAMP RESET RLCM RNET SEQ SGCM SGRP2 SLECT SNET SYS TOTAL TREND TSTAT WEEK Z2HSC Z2SCH ZONE2   ALARM AO APT BTUH CALEN COS CURVE DAILY DCC DEGDA DELAY DO DPT EDL EMS ENTHL FLO2 FLOW HILO HOLI LIM LIMIT LOGIC LOOP MATH MOMEN MTR OSS PEM1 POLL PWM RAMP RAV21 RDS21 RDV21 RESET RNET SEQ SGRP2 SLECT SNET SYS TOTAL TREND TSTAT WAV21 WDV21 WEEK ZONE2   ALARM AO APT BTUH CALEN CNTR1 CNTR2 COS CURVE DAILY DCC DEGDA DELAY DO DPT EDL EMS ENTHL FLO2 FLOW HILO HOLI LABEL LIM LIMIT LLLB1 LOGIC LOOP LWC1 MATH MN MNFLO MOMEN MTR NIM NSCHD OPM1 OSS PEM1 POLL PWM RAMP RECP1 RESET RMA1 RNET ROOF1 SEQ SGRP2 SIM SLECT SNET SYS TOTAL TREND TSTAT UNTV1 WEEK WMA1 WSHP1 Z2HSC Z2SCH ZONE2 AI ALARM AO APT BTUH CALEN COS CURVE DAILY DCC DEGDA DELAY DI DO DPT EDL EMS ENTHL FLOW HILO HOLI LABEL LIMIT LOGIC LOOP MATH MOMEN MTR NSCHD OSS POLL PULSE PWM RAMP RESET RGCM SEQ SLCM SLECT SYS TOTAL TREND TSTAT WEEK   NOTE 1: Refer to the table at the beginning of chapter 4 of the GCM/LCM Programmer's Manual, F-23120, for more information on what object types are supported in specific versions or types of controllers. NOTE 2: The block types listed for the "GIM-2100 / SIM-GCM:" encompass the blocks supported by all the devices of the group.  You will be able to create any block type listed however, an error will be displayed when you attempt to download an unsupported block type into a specific controller in the GIM-2100 / SIM-GCM family.  Please refer to the controller manual (LNC, SIM-York, SIM-Trane, SIM-CCN, SIM-MTech or GIM-2100) for information on the block types supported by that controller type. The following ASD device blocks are supported by TreeTech. MICROZONE II PEM LIM AO DO EMS HOLI LOOP OSS RESET RGRP SCHED SEQ UI UTIL WINDO AO AS AT AV DI DO EMS LOOP RESET RGRP SEQ UTIL WINDO EMSA EMSD HOLI OVI RGRP RO SCHED UTIL WINDA WINDD  
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Labels:
  • TAC IA Series
1724 Views

Is there a way to output the average of logged values contained within the I/A Series G3 history records?

Issue Is there a way to output the average of logged values contained within the I/A Series G3 history records? Environment I/A Series G3 Cause I/A Series G3 history tables contain records of values logged by the associated trend objects.  A BQL query must be used to read records from the table and perform a calculation to average the values. Resolution A program object that contains a BQL query can be used to read the records from a history table and calculate minimum, maximum, average, etc. The AX community module contains a BQL object (Trend Dynamic Analyzer) that can be assigned to a history ord and configured to a particular timeframe. A new trend with a specific number of records (rolling) can be queried by this object which in turn calculates the Count, Min, Max, Average, and Sum. The axCommunity module contains a library of useful objects for the Tridium Niagara AX platform created by AX programmers.  Download the axCommunity module from the following website - http://sourceforge.net/projects/niagaraaxcommun/. Note: Schneider Electric does not maintain and is not responsible for the content within the axCommunity module. The user should test and utilize at their discretion and risk. Copy the axCommunity.jar file into the Workbench platform (modules folder).  Install into the target platform as needed. Open the axCommunity palette and add a TrendDynamicAnalyzer object into the station. View the TrendDynamicAnalyzer property sheet and then assign the History using the History Ord Chooser. Connect an Interval Trigger if a time based refresh of the values is required. You may want to limit the values at the output if the values trended by the history can get out of range (e.g. initialization, etc.).
View full article
Picard Product_Support
‎2018-09-10 09:03 PM

Labels:
  • TAC IA Series
2419 Views

The web service within the ENC-520 indicates a status fault - Unlicensed:javax.baja.license.FeatureNotLicensedException.

Issue The web service within the ENC-520 indicates a status fault - Unlicensed:javax.baja.license.FeatureNotLicensedException. Environment I/A Series G3, ENC-410, ENC-520 Cause The web service has been added to the station however the ENC-520 is not licensed to support the web services.  The web services status will indicate the fault condition and the ENC will not serve up graphics. Resolution Requires purchase of the web services option for the appropriate platform. ENC-410-1 >> purchase ENC-410-WEB ENC-520-2 >> purchase ENC-510-WEB
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Labels:
  • TAC IA Series
1417 Views

In a Niagara R2 Modbus integration, the 4 view changes cached by the JDE cannot be modified

Issue In Chapter 5 of the Niagara R2 Modbus integration manual, the following note describes the JDE "View Cache": ... After viewing linked Gx objects in JDE, polling will continue for the associated shadow objects in PollOnDemand containers until that view is removed from the view cache. Typically, this means 4 view changes before polling stops... In an effort to reduce the number of shadow objects being polled (on a large job), can the 4 view changes, that are cached, be reduced to zero? Product Line TAC IA Series Environment Niagara R2 Modbus Cause The 4 view changes are by design. Resolution There is no way to configure the number of view changes or manually clear the cache.  Closing the JDE and re-opening it is the only way to stop the values from updating.
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Labels:
  • TAC IA Series
1166 Views

Will Niagara G3 integrate to a lighting system by Lutron?

Issue A job site has a Lutron lighting system called the GRAFIK Eye QS.  It comes with a network interface with model number QSE-CI-NWK-E.  Will this allow the system to integrate to Niagara G3? Environment Niagara G3 Cause Lighting system installed on a jobsite and end customer would like to integrate to the building automation system (Niagara G3). Resolution The Lutron network interface QSE-CI-NWK-E provides an interface to a Windows-based platform via a RS-232 or TCP/IP connection.  It is a "text-based" interface meaning commands are sent via a terminal program like HyperTerminal. In order to interface the GRAFIK Eye QS to Niagara, the FlexSerial Driver can be used.  This driver can be configured to communicate to a wide range of "simple" serial communicating devices.  It allows the user to model the native device messages like framing details and payload content. The part number for the FlexSerial drive is ENC-DRV-FLEX.  It is an option for the ENC-520, Jace-6, Jace-7, and Jace-Nxt.
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Labels:
  • TAC IA Series
1135 Views

Attempting to send email with I/A Series G3 and the SMTP server responds with an error "Must issue a STARTTLS command first."

Issue Attempting to send email with I/A Series G3 and the SMTP server responds with an error "Must issue a STARTTLS command first." Environment I/A Series G3 Cause The targeted SMTP server requires an SSL / TLS encrypted connection.  SSL (Secure Sockets Layer) allows for the encryption of HTTP traffic between an ENC/ENS and a remote client. Encryption of the Fox and Platform protocol is not supported.  This implementation is supported with G3 versions 3.3 and above.  SSL can also be used to connect to a SSL enabled SMTP mail server to protect email credentials and the email message being transmitted.  Using SSL with SMTP is supported on version 3.4.55, 3.5.5, 3.6.31 or later.  As always it is recommended to use the latest maintenance build for each version of Niagara G3. Resolution The I/A Series G3 platform currently supports SSL encryption only.  Requires purchase of the crypto feature IA-SSL that adds the following line to the base license. Contact Customer Care at 888-444-1311 to order (Part Number IA-SSL).  The Host ID for the ENC/ENS must be provided on the associated license form with the order.  The following feature will be added to the license. crypto ssl="true", parts="IA-SSL" Install Updated License - Once the updated license is received, install the license into the ENC / ENS using Workbench.  Do not reboot when asked, you will reboot after updating the Crypto module. Install Crypto module - Use the Software Manager in the Platform to install the crypto module.  Allow the ENC to reboot. Install Crypto Service - Add Crypto Service to Services folder. Configure Web Service (Only do this if you plan on using SSL with the Web Server).  Enable the Https Enabled property.  Change the Http Port to an unpublished port, such as 31876. This is required to prevent users from using HTTP logon.  Do not enable HTTPS Only.   This will cause the Fox Protocol not to function. Configure Outgoing Mail Server (Only if SSL is required for email).  Configure as normal, except use SSL port for the port number and enable the Use Ssl property.  Contact your email provider for proper hostname and port number for SSL.
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Labels:
  • TAC IA Series
1210 Views

Are the MNL controllers LonMark-certified to version 3.4?

Issue Are the MNL controllers LonMark-certified to version 3.4? Environment MNL controllers Cause Design specification requirements. Resolution Yes, they are.  Follow the link below to view their listings at lonmark.org. http://www.lonmark.org/products/search?manID=211 Click the "Next" link in the bottom right corner of the screen to scroll through all of them.  They are grouped together with other Schneider-Electric profiles.
View full article
Picard Product_Support
‎2018-09-10 11:16 AM

Labels:
  • TAC IA Series
974 Views
  • « Previous
    • 1
    • …
    • 71
    • 72
    • 73
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of