I/A Series G3 Enterprise Network Server (ENS) learned proxy point does not properly inherit the maximum override duration facet setting configured point or points at the ENC.
I/A Series G3 versions 3.5.xx and earlier
The mechanism within the core G3 software that controls the inheritance of the maxOverrideDuration facet for a learned proxy point was not added until 3.6.31.
Upgrade the I/A Series G3 Enterprise Network Server (ENS) and ENC to version 3.6.31 or higher.