Setting up an Alarm Notification class separate from the default Notification Class 0.
  • Setting up an Alarm Notification class separate from the default Notification Class 0.
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 12:28 PM
Niagara R2, Enterprise Server, UNC-410, UNC-520
Do not want to send all alarms to Email Recipient.
- Setup a new Notification class and assign it to the alarms you want emailed.
- Link the output of the Notification class to the input of the MailRecipient.
- Go to the Alarm Setup tab of the objects you want emailed and set its notificationClass property to that of the Notification class you just added. .
Only the alarm associated with the added Notification Class will be emailed.
  • TAC IA Series