MNB-1000
The MNB-1000 must be at firmware version 1.501 or newer in order to use the MNB-1000-15 module.
The first MNB-1000s can utilize the MNB-1000-15 expansion modules if its firmware is at version 1.501 or higher.
Also WorkPlace Tech version 5.7.1 or higher must be used to add the MNB-1000-15 modules.