Can the B&B Electronics Converter Model # 485OT9L be used to connect PSI 4.1 to a Network 8000 Microzone II?
  • Can the B&B Electronics Converter Model # 485OT9L be used to connect PSI 4.1 to a Network 8000 Microzone II?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 12:28 PM
Aside from the recommended models from B&B Electronics, can Model # 485OT9L be configured to work with PSI 4.1?
TAC IA Series
  • PSI 4.1
  • Network 8000 ASD devices (Microzone II, MicroFlo II)
On a jobsite and the only model available is the 485OT9L.
It can work by using the following settings for the on-board configuration switches:
  • Switches 1-4:  19200 baud (SW1=off, SW2=off, SW3=on, SW4=off)
  • Switch 5:  Echo off (SW5=off)
  • Switch 6:  Half-duplex (SW6=on)
  • Switch 7:  Half-duplex (SW7=on)
  • Switch 8:  Term Resistance (SW8=off)
  • Jumper 1:  JP1=SD
Note:  Model # 485OT9L was discontinued by B&B Electronics in Sept. 2011
  • TAC IA Series
  • 7695