Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Is there a way to output the average of logged values contained within the I/A Series G3 history records?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Is there a way to output the average of logged values contained within the I/A Series G3 history records?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • WaynePeters
    WaynePeters

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2440 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Is there a way to output the average of logged values contained within the I/A Series G3 history records?

Picard Product_Support
‎2018-09-10 09:03 PM

Issue

Is there a way to output the average of logged values contained within the I/A Series G3 history records?

Environment

I/A Series G3

Cause

I/A Series G3 history tables contain records of values logged by the associated trend objects.  A BQL query must be used to read records from the table and perform a calculation to average the values.

Resolution

A program object that contains a BQL query can be used to read the records from a history table and calculate minimum, maximum, average, etc. The AX community module contains a BQL object (Trend Dynamic Analyzer) that can be assigned to a history ord and configured to a particular timeframe. A new trend with a specific number of records (rolling) can be queried by this object which in turn calculates the Count, Min, Max, Average, and Sum.

The axCommunity module contains a library of useful objects for the Tridium Niagara AX platform created by AX programmers.  Download the axCommunity module from the following website - http://sourceforge.net/projects/niagaraaxcommun/.

Note: Schneider Electric does not maintain and is not responsible for the content within the axCommunity module. The user should test and utilize at their discretion and risk.

  1. Copy the axCommunity.jar file into the Workbench platform (modules folder).  Install into the target platform as needed.
  2. Open the axCommunity palette and add a TrendDynamicAnalyzer object into the station.
  3. View the TrendDynamicAnalyzer property sheet and then assign the History using the History Ord Chooser.
  4. Connect an Interval Trigger if a time based refresh of the values is required. You may want to limit the values at the output if the values trended by the history can get out of range (e.g. initialization, etc.).
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7794
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of