Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,839
  • TAC IA Series 1,822
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 328
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 487
    • 488
    • 489
    • …
    • 507
  • Next »

Is it possible to access the value of a doors ADA output for programming or reporting via graphics, listviews or reports?

Issue Is there a way to display the value of a doors ADA output or to use this value in a Plain English program? Environment ADA output Door attributes Cause Need to display and track the value of a doors ADA output. Resolution There is no sanctioned way to access or use the value of a doors ADA output.  While in some cases it may be possible to create a separate output object with the same channel number to track this value, this kind of configuration is known to have issues and it is not recommended.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
989 Views

License Setup changes without user interaction and reverts to previous configuration

Issue The configuration in "License Setup" changes autonomously meaning that you open "License Setup", make a change, close "License Setup", open "License Setup" and the configuration has reverted to what is was before the change was made. It reverts back to what it was before making the change. Environment TAC Vista 5.1.9 Cause The cause of this is unknown. TAC Vista Server is supposed to set some values in the registry while running also regarding licensing, but not like described here. Resolution Make sure TAC Vista Server is stopped while changing the license setup: Stop TAC Vista Server Change the license setup Start TAC Vista Server
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • TAC Vista
1063 Views

Windows reports that RAM services do not start or stop in a timely manner

Issue Windows reports that RAM services do not start or stop in a timely manner Environment RAM 2.1.025 Cause Windows reports that RAM services do not start or stop in a timely manner. Re-installing RAM does not resolve the issue Resolution The issue may be with the RAM configuration file (setup.mdb). Note: If possible, record the RAM setup by opening the RAM console. Uninstall RAM and locate and delete or save the Remote Alarm Manager folder to a different location. Reinstall RAM. RAM will need to be re-configured with the site setup.
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • Satchwell BAS & Sigma
  • TAC Vista
1011 Views

Can the LON card for MULTICAL 601/602 be mounted on an older MULTICAL 66 type?

Issue On a MULTICAL 66, the Lon card is broken and needs to be replaced. Does the MALON BASE card fit the older heat meters? Environment MELON BASE MULTICAL Cause Unfortunately the LON card we have today for the newer MULTICAL 601/602 will not function with the old MULTICAL 66 meter types. Resolution Please contact local Kamstrup Service channel.
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • Field Devices
1034 Views

I/A Series G3 Enterprise Network Server output window displays the following error: java.io.IOException: Negative seek offset.

Issue I/A Series G3 Enterprise Network Server output window displays the following error: java.io.IOException: Negative seek offset. java.io.IOException: Negative seek offset at java.io.RandomAccessFile.seek(Native Method) at com.tridium.history.io.FileRandomAccess.seek(FileRandomAccess.java:118) at com.tridium.history.file.recstore.RecordStore.writePage(RecordStore.java:561) at com.tridium.history.file.recstore.RecordStore.newLastPage(RecordStore.java:631) at com.tridium.history.file.recstore.RecordStore.getWritePage(RecordStore.java:606) at com.tridium.history.file.recstore.RecordStore.append(RecordStore.java:222) at com.tridium.history.file.recstore.BRecordStoreHistoryTable.doAppend(BRecordStoreHistoryTable.java:175) at com.tridium.history.file.BFileHistoryTable.append(BFileHistoryTable.java:803) at com.tridium.history.db.TableHandle.append(TableHandle.java:203) at com.tridium.history.db.BLocalDbHistory.append(BLocalDbHistory.java:393) at com.tridium.driver.file.history.BDelimitedFileImport.appendToHistory(BDelimitedFileImport.java:796) at com.tridium.driver.file.history.BCsvFileImport.executeFileImport(BCsvFileImport.java:212) at javax.baja.driver.file.history.BFileHistoryImport.doExecute(BFileHistoryImport.java:90) at auto.com_tridium_driver_file_history_BExcelCsvFileImport.invoke(AutoGenerated) at com.tridium.sys.schema.ComponentSlotMap.invoke(ComponentSlotMap.java:1217) at com.tridium.sys.engine.EngineUtil.doInvoke(EngineUtil.java:49) at javax.baja.sys.BComponent.doInvoke(BComponent.java:1046) at javax.baja.util.Invocation.run(Invocation.java:46) at javax.baja.util.Worker.process(Worker.java:161) at javax.baja.util.Worker$Processor.run(Worker.java:134) at java.lang.Thread.run(Thread.java:619) Environment I/A Series G3 Enterprise Network Server (versions prior to 3.4.54) Cause The error indicates that a history has become too large where the source .hdb file has exceeded 2GB making the history become inaccessible.  Versions prior to 3.4.54 used a Java integer as the offset into the page file of a history and the negative seek offset error is caused by a math rollover calculating a negative number. Resolution Two options to correct: Review the current size of the audit histories, log histories and any string logs to see which one is at the 2GB limit and perform some history database maintenance to trim the size down. Upgrade to the latest maintenance build of I/A Series G3 (3.4.54 or higher) where Java long calculations are used for the offset.
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • TAC IA Series
1343 Views

When attempting to fax a WorkPlace Tech license request, the fax number is reported as no longer in service.

Issue The paper version of the WorkPlace Tech Tool license request form includes the 815-637-5331 fax number.  This number has been disconnected and is no longer in service. The Schneider Electric Park Plant Customer Care Center has been relocated and the 815-637-xxxx series phone numbers have been disconnected. Environment WorkPlace Tech License Request Fax and email information Cause Incoming faxes to the Schneider Electric Buildings Customer Care Center are now handled electronically. Resolution Use of email is the preferred method for submitting a WorkPlace Tech Tool license request form although a fax number is still available. The preferred email address is IASeries.License@schneider-electric.com If it is necessary to fax the license request please use +1 888-560-3636.
View full article
Picard Product_Support
‎2018-09-11 02:50 PM

Labels:
  • TAC IA Series
1094 Views

Sigma - When backing up User Names and Passwords, what files / folders need to be copied?

Issue When backing up user names and passwords, what files / folders need to be copied? Environment User Names Passwords Cause Replacing the Sigma server PC and upgrading at the same time, what files should be copied? Resolution The Passwords / User names are stored in two locations in the Sigma/Data folder.   The following files / folders should be copied; All files located in the User folder. GenCNF.rec
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • Satchwell BAS & Sigma
1099 Views

Schedule not work properly, especially the holiday events

Issue The customer reported the schedule not work properly randomly, especially the holiday events not executing correctly. One item of error log 1465 was logged every 10 minutes. Environment CX9900/9940 i2 controller with version 3.2x Cause Some controllers with special version contribute to error log 1465 significantly, possibly impacting on the schedule event downloading Some i2 controllers with lower version firmware cause the schedule not to work correctly. Resolution Upgrade the CX controller to the latest version firmware. Upgrade all the i2 field controller to the late version firmware 3.300008
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • Andover Continuum
1094 Views

What is the input power supply range for the ACX57xx controllers?

Issue The ACX57xx controller datasheet does not specify the AC power voltage range/ tolerance. Environment ACX ACX5740 ACX5720 Cause The DC power input specifies the voltage range on the datasheet. No documents specify the AC voltage range. Resolution You can power the ACX57xx controllers from either AC or DC power. The DC range is 12VDC - 28VDC. Max' power consumption = 50W. The AC voltage is 24VAC +10% -15% 50/60Hz. Max' power consumption = 90VA Giving an AC voltage range of  20.4VAC - 26.4VAC.
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • Andover Continuum
950 Views

Graphic pipes are missing from Px pages when viewed via a Web Browser.

Issue Graphic pipes are missing from Px pages when viewed via a Web Browser, however pipes are displayed when viewed via WorkBench. Environment Niagara G3, ENC-520 Cause The needed kitPxHvac module was missing from the ENC-520. It seems the kitPxHvac module was not installed to the ENC. Usually all required modules are automatically installed to the ENC at the time of a station install, but for some reason the kitPxHvac module was not installed. Resolution Manually install the kitPxHvac module to the ENC - Open the Application Director window for the ENC hosting the graphics - Double-click on Software Manager - Select the kitPxHvac module from list and click the “Install” button at the bottom of the screen. - Click the “Commit” button to install the kitPxHvac module to the ENC A reboot of the ENC should not be required. Open a new Windows Browser and browse to the ENC. The pipes should now display correctly in the graphics.
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • TAC IA Series
1301 Views

Automation Server stuck in Reboot Cycle

Issue Automation Server stuck in Reboot Cycle Environment Automation Server Cause This experience is not typical so below is a list of solutions that have worked in the past. Resolution ES - AS Communication Issue - This fix works when the boot cycle only occurs while the ES is online. You can prove this is the case by stopping the Enterprise Server through software administrator, then attempting to log into the AS Log into the Enterprise Server Click on the Root Server Object in the System Tree Pane Click on the Communications tab Verify that the listed IP address for the Enterprise Server matches the IP address of the machine In the System Tree Pane, expand the Servers folder Delete the Affected Automation Server. NOTE: This will break all binds to/from this server. Log out of the Enterprise Server and Log into the Automation Server to verify that it is stable. Log out of the Automation Server and back into the Enterprise Server Re-add the Automation Server to the Enterprise Server
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • EcoStruxure Building Operation
1583 Views

Schneider Electric MTN881001 or the SVEA LON I/O Module DR-N 3DIM 1-10V. Output values are not as expected.

Issue Schneider Electric MTN881001 or the SVEA LON I/O Module DR-N 3DIM 1-10V. Changing the SNVT nviLALampValue_? does not give the expected output. Environment MTN881001 SVEA 36237-552 Cause Changing the SNVT nviLALampValue[i] to the following values, shows the following VDC volt on the analog output: nviLALampValue Analog output 100.0 1 -  9,94 VDC 80.0 1 -  7.65 VDC 60.0 1 -  6,75 VDC 50.0 1 -  6.25 VDC 20.0 1 -  4.86 VDC 1.0 1 -  3.97 VDC When nviLALampValue is 50.0 1, the analog output is 6.25 VDC (not proportional) and the minimum analog output value is 3.97 VDC, which does not make sense.   Resolution The module is using a logarithmic behaviour for the 1-10V output as default. This is because the device is mostly used for fluorescent lamps. You can change the behaviour by using the UCPTadaptationTable in the lamp Actuator object. UCPTadaptationTable consists of 21 values representing the digits (from 0 to 255) for the output value in steps of 5%. This means:   first value: 0% second value: 5% third value: 10% ... 21st value: 100% To get a linear behaviour you should set as follows: first value: 0 second value: 13 third value: 26 ... 21st value: 255
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC Vista
1243 Views

Wrong SQL database schema version after upgrade

Issue After upgrading a TAC Vista system on a site with high IT security you can end up with a wrong schema version in the SQL database causing issues such as failure to insert trend log data. Environment TAC Vista SQL Cause In some versions of TAC Vista, the SQL database upgrade carried out during the installation of TAC Vista doesn't upgrade the SQL database to the newest version. The first time you start TAC Vista Server, the server (TACOS) carries out the remaining upgrade steps. On a site with very high security standards, TAC Vista Server is however not able to apply the last SQL database upgrade scripts as those can only be carried out by the IT department directly on the SQL server, and as a result the SQL database is not fully upgraded. Resolution   1.      Note exactly what schema version the SQL database currently has This can be checked through SQL management studio with this query USE taclogdata; SELECT dbo.DSS_SchemaVersion() AS Db_SchemaVersion 2.      Note exactly what version of TAC Vista you have upgraded to 3.      Contact PSS to get a SQL upgrade script specific for the site and run that on the SQL database
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • TAC Vista
2316 Views

Create or Modify Custom Standby Image on SE8000 Series Room Controller

Issue How to change the Standby image on a SE8000 controller to something other than standard factory image Product Line EcoStruxure Building Expert, Field Devices Environment SE8xxx range Cause The standard standby image for the SE8300 does not meet the customer requirements Resolution See the link below to the Exchange for the software and instructions on how to perform this process. Reference page 4 of the Uploader Tool - SE8000 Series Room Controllers.
View full article
Picard Product_Support
‎2018-09-11 02:52 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
2705 Views

Webreport - Reportserver does not delete the trend data when extended trendlog is deleted in StruxureWare Building Operation

Issue Reportserver does not delete the trend data when an extended trendlog is deleted in StruxureWare Building Operation. Environment StruxureWare Building Operation Webreport SQL Cause When an extended trendlog is deleted in StruxureWare Building Operation, its corresponding data in webreport server are not deleted. This means that when you want to look at a trend in the reportserver you will still see the deleted trendlog. No new data are collected but the previously collected data will be there. Resolution This is by design. The historical data are not deleted from SQL; however,  a side effect of this is that the webreport interface will still show the extended trendlog after it has been deleted in Workstation.
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Labels:
  • EcoStruxure Building Operation
1252 Views

Tunneling with the LCM driver

Issue Does the LCM driver support tunneling? Product Line TAC IA Series Environment R2 UNC with LCM driver Cause Tunneling is needed to make programming changes to the LCM's. Resolution It is possible to tunnel through the UNC to the LCM's, but it requires an RS-232 connection from the UNC to one of the LCM's.  See the LCM Integration Guide F-27422-2 for details.
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Labels:
  • TAC IA Series
1274 Views

Does the bCX1-CR-INF (bCX9640) have any BACnet objects or functionality at all?

Issue Need to use a controller that has no BACnet functionality due to network security limitations on site. Environment Continuum bCX1-CR-INF (bCX9640) Cause A customer has a site with restrictive network security requirements and BACnet devices (or any other open protocol) are not allowed. Resolution The bCX9640 is an Infinet protocol controller only. This version of the bCX firmware does not have the BACnet stack installed, and there are no BACnet points able to be created in this controller. You will be fine to use this controller where BACnet support is not required or allowed.
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Labels:
  • Andover Continuum
1690 Views

Web based email should not be used to deliver Keyless Licensing information files (c2v) or activation files (v2c)

Issue One of the following errors is thrown by the Hasp Key Utility when attempting to update the Continuum License key using the V2C file received from Schneider Electric. Invalid Parameter Update failed: KeyIdNotFound Product Line Andover Continuum Environment Continuum 2.0 Hasp Key Utility License Cause The V2C file that was emailed to the customer is corrupted. When Web based email is used to receive the v2c file from Schneider there have been cases where the file is not received in its original form.  When this happens the file size of the attachment appears to be correct.  When the c2v file is save to a folder on the workstation PC however, the file size reported is 0kb.  Resolution The solution to this is to use a non-web-based email application like Outlook or Outlook Express. 
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Labels:
  • Andover Continuum
1589 Views

Troubleshooting "4417 DEVICE_ERR_NOADDR_I2C" errors seen in Controller's Error Log.

Issue Troubleshooting 4417 DEVICE_ERR_NOADDR_I2C errors seen in Controller's Error Log. Environment Continuum Controllers Cause 0x00004417 0x00002100 0x021046e2 0x00080002 0x000000200x00004417 0x00002100 0x021046e2 0x00080002 0x00000020 "DEVICE_ERR_NOADDR_I2C" errors are related to the internal bus to the peripherals and RealTimeClock.   DEVICE_ERR_NOADDR_I2C       (no address response)      “DEVICE_ERR_NOADDR_I2C” errors are not I2 errors they are I2C errors. These errors are related to the internal bus to the peripherals (like an onboard RealTimeClock or the expansion bus (modules)).   There may have been an expansion module installed that has been removed while a PE program is still accessing an I/O on the module. Resolution Possible causes can be:   1. A defect with the onboard RealTimeClock. Check for 4417 errors followed by TimeSync errors and/or indications that the time clock is not stable similar to the following error lines.   01/01/1989 00:00:00.00 0x00004417 DEVICE_ERR_NOADDR_I2C (no address response) 01/01/1989 00:00:00.00 0x00010000 Clock change   2. An issue with the expansion bus modules. There may have been an expansion module installed that has been removed while a PE program is still accessing an I/O on the module.
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Labels:
  • Andover Continuum
1690 Views

Discontinuation of HID SmartTOUCH Fingerprint readers

Issue HID Biometric reader product obsolescence. Environment HID Desfire and Mifare Smart card and Fingerprint readers. As used on Continuum and I/Net Access Control. Cause HID have discontinued these readers. Resolution HID have discontinued production of their SmartTOUCH SB10 and SBK10 Desfire and Mifare fingerprint readers. Part numbers affected are: HID Ref: 800-8052, SE P/N 654 1903 000 - SB10 Desfire Fingerprint reader. HID Ref: 800-8057, SE P/N 654 1904 000 - SBK10 Desfire Fingerprint reader with keypad. HID Ref: 800-8050, SE P/N 654 1901 000 - SB10 Mifare Fingerprint reader. HID Ref: 800-8055, SE P/N 654 1902 000 - SBK10 Mifare Fingerprint reader with keypad.
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Labels:
  • Andover Continuum
  • Field Devices
  • TAC INET
1067 Views
  • « Previous
    • 1
    • …
    • 487
    • 488
    • 489
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of