Is RS-485 node activation required on a 57xx series acx to connect the SCH-PIM400-485
  • Is RS-485 node activation required on a 57xx series acx to connect the SCH-PIM400-485
  • Alan_Wood
    Alan_Wood
‎2018-09-06 09:35 AM
Normally using RS-485 on an ACX 57xx requires nodes to be activated to work so ordering and price could be affected by this
ACX57xx
Schlage PIM 400-485
The Schlage PIM RS-485 unit uses RS485 for communication and it's important to know if node activation is required for the Schlage solution to work
The Schlage PIM RS-485 does use RS-485 for communication, but it doesn't require node activation on the comm port. The Schlage solution uses an XDriver instead in order to communicate RS-485 to the PIM
Tags (2)
  • 16137
  • pim-rs485