Issue
When using STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device.
Environment
TAC Xenta 121-FC
STR150
Cause
When using a STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device.
Resolution
In ZBuilder, it is possible to move the Occupancy Mode indication from the default location at Y1 to K1-4.
In this case you also need to have an external power supply with 5 Volt DC for the Occupancy Mode indicator.