Is it possible to use the analog output on the TAC Xenta 121-FC even if I want to have the Occupancy mode indicator on a STR150?
  • Is it possible to use the analog output on the TAC Xenta 121-FC even if I want to have the Occupancy mode indicator on a STR1...
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 09:35 AM
When using STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device.
TAC Xenta 121-FC
STR150
When using a STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device.
In ZBuilder, it is possible to move the Occupancy Mode indication from the default location at Y1 to K1-4.
In this case you also need to have an external power supply with 5 Volt DC for the Occupancy Mode indicator.
  • 16143