Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,853
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 464
    • 465
    • 466
    • …
    • 509
  • Next »

STR800 thermistor accuracy.

Issue The STR800 sensor is a replacement for the TSMN-57011-850.  What is the thermistor's accuracy?  The datasheet (F-27739) does not provide this information. Environment Temperature sensors Cause Missing data in the spec sheet Resolution Sensing Element:  Thermistor resistance, 10,000 ohms at 77°F (25°C) shunted with an 11K ohms 0.1% resistor. Within operating temperature limits of 32 to 158°F (0 to 70°C): Error ±0.36°F (0.2°C) maximum Drift/Year 0.045°F (0.025°C) maximum Over Operating Temperature Limits: Error ±0.76°F (0.42°C) maximum Drift/Year 0.09°F (0.05°C) maximum
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • Field Devices
  • TAC IA Series
998 Views

Import/ Export functions of Tree Tech 3.2 on Windows XP SP3 were disabled by recent Microsoft update.

Issue Import/ Export functions of Tree Tech 3.2 on Windows XP SP3 were disabled by recent Microsoft update. No .GDF file exported, no error message displayed. Environment Tree Tech revision 3.2 installed on Windows XP SP3 computer Cause Believed to have been caused by a recent Microsoft update.  Resolution There are two work-around options: Run Tree Tech 3.2 on Windows 7 , 32-bit machine If the project database is backed up from the Windows XP computer, it can be reloaded on the Windows 7 computer. The project database path on the Windows XP computer is: c:\Documents and Settings\All Users\Schneider Electric\TreeTech\Jobs\Projects\  On a Windows 7 computer, the file path for the TreeTech database is c:\Program Data\Schneider Electric\TreeTech\Jobs\Projects\    Un-install Tree Tech 3.2, install Tree Tech 3.1 on Win XP SP3 machine if no Win 7 machine available. Tree Tech 3.1.exe is available on The Exchange Download Center Run the WIBs purchase, generate license request for IV-DEMO-CDE, send file to us to create a license. OK to export GCM database already uploaded in 3.2 
View full article
Picard Product_Support
‎2018-09-11 04:29 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1481 Views

Unable to Login into Webpage after java update 7_21 error unknown wbreq:wbapplet.class

Issue Unable to Login into Webpage after java update 7_21 Environment R2, G3 Cause Java's latest update  7_21 (and later) includes a new option to keep temporary internet files.  This is creating issues with the user login and with displaying some graphics. Resolution A.  Configure Java so that it does not cache the applet files. Go to Windows Control Panel (\via the Start menu Open Java Console General tab --  Temporary Internet Files Click [Settings] Uncheck "Keep temporary files on my computer" Click [Delete Files] Check  "Cached Applications and Applets" then click [OK] Close Java Console B. Clear the browser's cache. Clear the temporary internet files, cookies and history. NOTE: Each browser is cleared differently. Use the browser's help for information on clearing its cache. C.  Manually clear the cached application and applets for specific applications: Delete all the files in the 'wbapplet' cache. Windows, clicking Start > Run... and entering %userProfile% will open the local Windows user directory.  \niagara\wbapplet\modules   Delete everything in the 'Secondary Applet' cache, also located under the current %userProfile% folder. Windows 7: \AppData\LocalLow\Sun\Java\Deployment\cache Windows XP: \Application data\sun\java\deployment\cache        
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • TAC IA Series
1423 Views

CPU light on ACX7xx flash rapidly (at bout twice the normal speed)

Issue After an attempt to cold start the controller by removing AC power with the batteries disconnected, the unit started up with its CPU light flashing very rapidly (hard failure mode) Environment ACX780 ACX781 Cause Partly cleared memory. The random access memory  (RAM) on the ACX78x take a long time to erase. Resolution Remove the batteries Power down the unit Wait 5 minutes Power up the unit
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • Andover Continuum
969 Views

What Ethernet speed and duplex is supported by the MNB-1000?

Issue What Ethernet speed and duplex is supported by the MNB-1000? Environment MNB-1000 Cause Specifications for IT infrastructure Resolution The MNB-1000 controller has auto-sensing Ethernet port (10/100 MB, half / full duplex) capabilities and are dependent on the network / switch to which they are connected.  The MNB-1000 has the ability to auto negotiate with the Ethernet network on startup.
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • TAC IA Series
1270 Views

Does TAC Vista support the protocol ESPA 4.4.4?

Issue Does TAC Vista support the protocol ESPA 4.4.4? Environment TAC Vista 5.1.8 Cause Vista server supports: OPC Lon The Xenta 913 supports: Bacnet Modbus M-bus Clipsal C-Bus Resolution TAC Vista has no support for ESPA 4.4.4
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • TAC Vista
1251 Views

Can the I/A Series R2 ModbusAsync driver be configured to control minimum send time between Modbus messages to the bus?

Issue Can the I/A Series R2 ModbusAsync driver be configured to control minimum send time between Modbus messages to the bus? Environment I/A Series R2, Modbus Cause The Modbus device under control is unable to process messages at normal rates and requires a delay between messages received. Resolution The minimum send time between Modbus messages can be controlled by adding a parameter into the drivers.properties file. Note: Requires modbusAsync-2.302.514.v1 or higher. Open the UNC with the admin tool and go to the Installation tab. Edit the drivers.properties file. Add the property (shown below) on its own line within the file. Set the value the number of mSec of delay between messages. Save the file and reboot the station (remember to backup the station when requested). modbusAsync.minSendInterval=1000
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • TAC IA Series
928 Views

Error entering Input conversion in b3

Issue Attempting to enter a conversion that references an object (point, PE function etc) results in error.. "Could not validate conversion formula" Environment Automation Server BACnet interface b3 device. Cause By design in SBO a point conversion can not contain references to other objects in the server. Resolution Remove the reference and substitute a hard coded value EXAMPLE: sqrt(elecvalue) * kfactor In the conversion above, 'kfactor' is an analog value in the b3, the conversion can't be validated due to the reference to kfactor. The solution is to replace 'kfactor' with its actual value sqrt(elecvalue) * 10
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • EcoStruxure Building Operation
1371 Views

Binding between the "Associated value" of a BACnet output point and the "Requested value" of the digital output value, does not work.

Issue Bindings do not work. Environment Binding BACnet Output Digital Output Cause When the BACnet point changes in value, it does not change the value of the Digital output.   Resolution The StruxureWare Building Operation core architecture (as of version 1.3) allows cross server “read” references, but not cross server “write” references. This was the design from 1.0, and effects everyone – not just BACnet (ie. script programs would have the same behavior). What this means for the BACnet associated value is that inputs (which are “read” references) can be done cross server, while outputs (which are “write” references) can be only be within a single server.
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • EcoStruxure Building Operation
1491 Views

Camera will not move to preset PTZ on video alarm

Issue Camera will not move to preset PTZ on video alarm, from Video Monitor the camera can be moved to the preset in live video. Environment CyberStation Video Server Video Monitor Cause Issue with accVideoRecordingSrvc.exe at workstation that is logging the alarm. NOTE: The accVideoRecordingSrvc.exe problem could happen at any workstation not necessarily the workstation receiving the alarm. Resolution Check all workstations looking for any indication that there has been a problem with accVideoRecordingSvr.exe Shutdown then re-start Continuum on the workstation reporting issues with accVideoRecordingSvr.exe
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • Andover Continuum
1267 Views

Issues with BACnet alarm text.

Issue When receiving an alarm from a BACnet device, the alarm text display does not match the text entered in the SmartStruxure configuration of the alarm object. Also performing a 'Recheck' from the alarm viewer results in the alarm text fields going blank. Environment AS ES BACnet device Cause As of version 1.3 SmartStruxure uses BACnet protocol version 6, as a result of that SmartStruxure is not able to read or write the alarm text message from BACnet devices. If a device includes the text message with an alarm event SmartStruxure will use the message when displaying the alarm in the alarm viewer but on alarm re-check it will use the alarm messages in the SmartStruxure database as it’s not able to read that information from the device. When using messages from the device and performing an alarm ‘Recheck’ the alarm messages will be blank unless they are set on the SmartStruxure side. This issue will addressed by SmartStruxure In the future when BACnet protocol revision 13 is supported. Resolution To work around this issue do one of the following: Configure the BACnet device so that no text is sent with the alarm. or   Enter alarm text on the SmartStruxure side to match the text sent from the controller.
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • EcoStruxure Building Operation
1491 Views

Can an automation server be installed with a backup database without the need for Workstation?

Issue Can an automation server be installed with a backup database without the need for Workstation?  For example, can a backup database be installed on a USB stick that is programmed to 'auto-run' when it is plugged into the automation server? Environment StruxureWare for Building Operations (all versions) Cause Customer works in the industrial refrigeration industry and his field personnel are primarily mechanics with limited pc knowledge.  Wants to use a stand-alone AS to control the refrigeration system.  Sites are mostly remote (several hours by car and/or flights).  Wants to send programming changes, due to site installation changes, as a self-extracting and self-installing file on a USB stick. Trying to avoid supplying the necessary laptops and Workstation training to the mechanics. Resolution This feature is not available.  Workstation is required for database administration.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • EcoStruxure Building Operation
1104 Views

LMADMIN.exe - Application Error

Issue After the "Windows is shutting down" message, the Windows displays a non specific memory error as shown below: lmadmin.exe - Application Error The instruction at "0x00000000" referenced memory at "0x000000". The memory could not be read.   Environment SmartStruxure Windows XP SP3 Cause Flexera Software (Licensing software used within Building Operation) does not support Windows XP.  This is a known issue which will not be corrected. Resolution There is currently no known operational issues with this error and only occurs when shutting down the Windows XP machine.  Upgrading the Operating System will remove this error.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • EcoStruxure Building Operation
2828 Views

Sensor pockets for Kamstrup Heat / Flow meters

Issue Which pockets are included with the different size meters? Environment Kamstrup Heat meter Flow meter Cause Different applications requires different sensor pockets. Resolution 65mm pockets included up to DN20, 90mm pockets between DN25-DN80, 140mm pockets from DN100 and up.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • Field Devices
1290 Views

Linkage kits to be used with Satchwell ALE (s) , ALi, ALX (s), ALM (s) on Schneider Electric Venta V and VG Valve bodies

Issue Linkage kits to be used with Satchwell ALE (s) , ALi, ALX (s), ALM (s) on Schneider Electric Venta V and VG Valve bodies Environment Linkage Kits Cause Linkage kits to be used with Satchwell ALE (s) , ALi, ALX (s), ALM (s) on Schneider Electric Venta V and VG Valve bodies. Resolution Use the L8TV linkage kit part no. 914-1080-000 on V type valve bodies e.g. V211, V211T, V311, V311T, V231, V241, V212, V222, V232, V292, V341 Use the L9TVG linkage kit part no. 914-108-000 on VG type valve bodies e.g. VGS211F, VG221F, VG311F
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • Field Devices
935 Views

Sigma - Global communications, what happens to the controllers if the network fails?

Issue What happens to Sigma globals if the network fails? Environment Globals Communications Networks Cause Site is to have a planned network shutdown, how will the Sigma controllers react to this? Resolution The Sigma controller using the global update, will continue to operate normally, but will use the last value received, so any changes will not be responded to. If the Sigma controller controls critical plant then the loss of global communications should be taken into account when programming.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • Satchwell BAS & Sigma
871 Views

I/A Series G3 Software Drivers Returns

Issue I/A Series G3 Software Drivers Returns Environment I/A Series G3 software drivers Examples: ENC-DRV-MOD, ENC-DRV-MOD-T etc.  Cause The wrong software driver was purchased for an ENC-520 and the ENC-520 has been shipped to the customer.  Resolution There are no returns on software drivers. A purchase would have to be made for the software driver that is required.  The existing driver that was wrongly purchased can be re-license for use on another G3 device by purchasing an I/A Series license change (IA-LIC-CHG). 
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • TAC IA Series
1018 Views

Fan Conditioning on a Xenta 121

Issue Fan is activating though it is not commanded. Environment Zbuilder Xenta 121FC Xenta 121HP Cause Fan Conditioning is Active. Conditioning can be used to "stir" the air periodically, evening the temperature when the system is not commanded or forced off. Resolution Active fan Conditioning is determined by settings for Inactive time and Active time. (UCPTappOptions bit 8, Active=1) Inactive time - Maximum interval in minutes before the fan is activated, if not used during. Standstill time between Conditioning.(UCPTFanCondOffTime) Active time - Time in minutes that the fan runs at minimum speed during Conditioning.(UCPTFanCondOnTime) If the Fan Conditioning is active, the fan state will be monitored for activity during the specified Inactive time and turned on when Inactive time has passed. The fan will stay on for the specified Active time until reached then turn off, which begins the Inactive time monitoring again. If the fan is called for during the Inactive time before reaching the Inactive time, the Inactive time is started over when the fan is released.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • TAC Vista
993 Views

What's the best way to restore a full SIGNAL database from version 4.4.1 (Windows 95/98) to version 5.0.0 (Windows XP)?

Issue Customer did a full backup of a SIGNAL 4.4.1 installation.  A full backup is data, bitmaps, and executable files.  The computer hardware was replaced along with the operating system to Windows XP 32-bit.  The customer has SIGNAL version 5.0.0. Environment SIGNAL Cause Computer hardware replacement Resolution There are a couple of ways to restore the database.  Here is a simple method: - Install SIGNAL 5.0.0 - Restore the full backup from version 4.4.1 (this step overwrites all the executable files of 5.0.0) - Re-install SIGNAL 5.0.0 (this last step will update all the executables back to version 5.0.0) The license file, signal.dcf, may need to be checked to ensure it is for version 5.0.0.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • TAC IA Series
938 Views

Information on how the MNB-Vx determines damper position after a power cycle.

Issue Information on how the MNB-Vx determines damper position after a power cycle. Environment MNB-V1 and MNB-V2 Cause Understanding damper behavior after a power cycle Resolution After a power cycle, the damper does not know exactly where it is and it is NOT stored in non-volatile memory. So, it must drive open or drive closed to re-synch the hall effect sensors embedded in one of the gears that provides positional feedback. There are two Hall-Effect sensors that detect a magnet, embedded in one of the drive gears, as it spins. Each sensor sends a pulse to an internal counter each time it detects the passing magnet. The two Hall-Effect sensors help with identifying clockwise and counter-clockwise rotation. The accumulated pulse count and the gear ratio help in calculating the damper position. Right-click the VAV Actuator object in WorkPlace Tech and go to its Properties, there is a setting called 'Position Initialization Mode'. Select open or closed as the choice when initializing after a power cycle.  
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • TAC IA Series
1127 Views
  • « Previous
    • 1
    • …
    • 464
    • 465
    • 466
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of