Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,853
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 465
    • 466
    • 467
    • …
    • 509
  • Next »

A newly added Microzone II does not appear in the Node List in PSI.

Issue A newly added Microzone II does not appear in the Node List in PSI.  The ASD trunk contains existing controllers connected to a UNC-520.  All existing ASD controllers appear in the Node List.  Environment Niagara R2 ASD Cause The new ASD controller must be 'learned' into the R2 station in order for it to appear in the Node List in PSI. Resolution Access the R2 station and use Device Manager to find and learn the new controller into the station. 
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • TAC IA Series
996 Views

Are MA-223 Fire and Smoke Damper Actuators still available?

Issue Do we have a replacement for the Fire Rated Damper Actuator: Make: Siebe Environmental Controls Part No: MA – 223   Environment Fire Rated Smoke actuators MA-223-0-2 Cause Siebe Fire/ Smoke rated damper actuators are all obsolete. Resolution Schneider Electric no longer manufacture any fire and smoke actuators so the MA-223 range are obsolete with no replacement. The only suggestion we can offer is for the customer to contact the damper manufacturer that this actuator is mounted on and see what they would use to replace the actuator. We only sold these fire/smoke rated actuators directly to the damper manufacturers.  
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • Field Devices
1427 Views

European Intrusion Certification

Issue Intrusion Alarm System for TAC I/NET Building Automation Systems Environment I/NET Site using Intrusion Alarm System for TAC I/NET Building Automation Systems Cause Certification Requests Certification Requests including Grade 3 Resolution The I/NET Access Control security products are certified and Listed under Underwriters Laboratories standard UL294. We do not have certification with NSI or SSAIB. Reference to NSI and SSAIB suggest a probable European security application. If that is the case, the application may be a candidate for our recently released TAC I/NET security products listed below - ICPB - Intrusion Control Panel Base ICPE - Intrusion Control Panel Expander ICPD - Intrusion Control Panel Distributed OP5 - Operator Terminal The above system panels were certified to the European Security System Standard EN50131 and the Swedish standard SSF1014 by - SP Sveriges Tekniska Forskningsinstitut SP Technical Research Institute of Sweden Box 857, SE-501 15 Borås, Sweden Tel: +46 (0)10 516 50 00 Telefax: +46 (0)33 12 50 38 Internet: www.sp.se The Security system panels and their functional performance were tested and certified to the following standards - EN50131-3:2009 Alarm systems - Intrusion and hold-up systems - Part 3: Control and indicating equipment EN50131-6:2008 Alarm systems - Intrusion and hold-up systems - Part 6: Power supplies The above two standards are used to test/evaluate intrusion systems for compliance with EN50131-1 SSF1014:2005 System components – Intruder Alarm Systems Requirements and test methods EN60950-1:2001+A11:2004 Information technology equipment - Safety EN61000-6-3:20007 Electromagnetic compatibility (EMC) - Generic Standards - Emission standard EN50130-4:1996/A1:1998/A2:2003 - Electromagnetic Compatibility - Product family standard: Immunity requirements for components of fire, intruder and social alarm systems. The TAC I/NET EN50131 compliant system is documented in TCON314 Installation Manual and TCON315 operators Manual. The security system detailed above was certified and registered with the organization - SBSC SBSC is Sweden’s leading organization for certifying companies, products, management processes and personnel within fire protection and crime prevention. This is covered under SBSC Certificate number 10-523 (copy available at link provided) PA-00148 Vista Security Intrusion Certification.
View full article
Picard Product_Support
‎2018-09-11 04:33 AM

Labels:
  • TAC INET
1407 Views

Import/Export data from Microsoft Excel into StruxureWare Building Operation spreadsheet view

Issue Is it possible to Import / Export data from Excel into the StruxureWare Building Operation Spreadsheet view? Product Line EcoStruxure Building Operation Environment SmartStruxure Spreadsheet View Microsoft Excel Cause Engineer must complete a survey of the existing plant before starting the upgrade and wished to export the StruxureWare Building Operation data into Excel. Resolution Importing and Exporting to Excel at release 1.3 is not possible, using copy and paste are the only options. These functions are described in StruxureWare Building Operation "Help" under "How To". Copying from MS Excel to Spreadsheet View Copying from Spreadsheet View to MS Excel
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • EcoStruxure Building Operation
3168 Views

LD-1 display program stopped working.

Issue LD-1 program was working, then suddenly stopped. Environment LD-1 Display Module Cause Corrupted InfinityString points. Resolution Deleted and recreated corrupted InfinityString points.
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • Andover Continuum
905 Views

Cannot get McQuay BACnet MSTP controller to come into the BACnet side

Issue McQuay BACnet MSTP controller does not respond to the Who-Is request from CyberStation   Environment MSTP bCX4040 McQuay Cause McQuay Tech Support has reported that the McQuay device has problems with Enhanced MSTP.  Resolution McQuay Tech Support has reported that the McQuay device has problems with Enhanced MSTP.  Once Enhanced MSTP was turned off the device was found and displayed on the BACnet side. 
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • Andover Continuum
1102 Views

After copying sections of logic from one application to another the ability to connect pointers stopped working.

Issue After copying sections of logic from one application to another the pointers from that logic won't connect to other objects and therefore show up as red lines. Environment WorkPlace Tech Cause Copying sections of logic from an older application has been known to cause this. Resolution To recover the application remove all objects and reference tags that exhibit the connection issue, compile the application and then re-create the deleted logic by pulling objects from the Shapes window.
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • TAC IA Series
872 Views

What is the difference between the MNL-V3RV3 and the MNL-V3RV3-A?

Issue What is the difference between the MNL-V3RV3 and the MNL-V3RV3-A? Environment  MNL-V3RV3 MNL-V3RV3-A Cause MNL-V3RV3-A is a new part number, and it isn't clear how it differs from the existing  MNL-V3RV3. Resolution The MNL-V3RV3-A meets the requirements of the Buy American Act (BAA).
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • TAC IA Series
1050 Views

Netcontroller IO Module Bus Voltages

Issue What are the expected voltages on the RS485 IO Module bus? Product Line Andover Continuum Environment Netcontroller IO Modules IOU Modules Cause Require typical values for troubleshooting first steps. Resolution Although the IO Module bus uses RS485 comms similar to Infinet or BACnet MSTP, the typical bus voltages when measured with a voltmeter are usually lower. Exact voltages will vary from system to system and depend on the amount of bus activity at the time, but the following will allow general troubleshooting: Typical DC voltage measured across the bus + to - = 0.7 to 0.8VDC but working systems may read as low as 0.4VDC Typical DC voltage measured Screen (shield) to + = 0.6 VDC Typical DC voltage measured Screen (shield) to - = 1.3VDC Note: If using Free Topology (FTT-10A) controller and modules, these use transformer bus coupling and will measure 0VDC across the bus.
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • Andover Continuum
1205 Views

Sigma - Can the Alarm Manager on a Remote client be configured differently, to the Local client.

Issue Alarm Manager configuration. Environment Alarm Manager Configuration Cause A different configuration of alarms is required on a Remote Sigma client. Resolution The Alarm Manager is shared by both the local and remote Sigma clients, therefore any changes in configuration effect both clients. If there is a requirement to send different alarms to the local and remote Sigma clients, then this is achieved using Routesets, which are allocated to the individual object alarms.
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • Satchwell BAS & Sigma
1004 Views

XIF parser fails due to "-sign.

Issue The XIF parser could fail if there is a "-sign in a commented row in the XIF default field. Environment TAC Vista Cause The XIF parser could fail if there is a "-sign in a commented row in the XIF default data field. Example: # ----------------------------------------------------- # ----------------------------------------------------- FILE value 1 1 ##dde1  "1,2,3\x00,1,2;"         // UCPTdownDriveTime                SNVT_time_sec 0x66,0x66 ##dde3 "1,2,23x00,2,2;"         // UCPTupDriveTime                     SNVT_time_sec   Resolution Just removing the "-sign will work: # ----------------------------------------------------- # ----------------------------------------------------- FILE value 1 1 ##dde1 1,2,3\x00,1,2;           // UCPTdownDriveTime             SNVT_time_sec 0x66,0x66 ##dde3 1,2,23x00,2,2;         // UCPTupDriveTime                   SNVT_time_sec
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • TAC Vista
1084 Views

Can multiple TCP/IP XDrivers be installed on a single 2nd Generation Controller?

Issue Will a single 2nd generation Controller  (NC2, bCX) support two IP XDrivers on two different comm ports?    Environment XDriver NC2 (CX9680) bCX4040 Cause Want to enable two IP XDrivers on different comm ports of the same Controller. Resolution You can only enable one IP XDriver per Controller. (Example: You can not enable a BACnet IP XDriver on one comm port and a Modbus IP XDriver on another, you would need two Controllers for this - one IP XDriver on each.)
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Andover Continuum
1295 Views

Programmable controller does not get added. Progress window never closes

Issue Programmable controller does not get added. Progress window never closes Can not add programmable controller. Environment StruxureWare Building Operation 1.3 SP Function block editor TAC Xenta 301, TAC Xenta 302, TAC Xenta 401, TAC Xenta 281, TAC Xenta 282, TAC Xenta 283 Cause Check if there are any blocks named "version". This is a reserved word that is not allowed as a name Resolution Open Function block editor and search your application (F7) for the word version. Change version to something else
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • EcoStruxure Building Operation
1144 Views

Sigma Logging - If an object has been logged for some time, and then the object name is changed, what name will be used in the log?

Issue Changing the name of an object that is being logged. Environment Logging Object name Cause A system has been logging for several years, but now the customer needs to change an object name. When using Dataview to review the logged data, which name will be shown for the existing data? Resolution If an object name is changed and that object is being logged, then the new name is passed to the logging setup. From this point on it is this name that will be used in any log reviews containing this object. This applies to both new logged data and any archived data.
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Satchwell BAS & Sigma
894 Views

What is the part number & price for a SmartStruxure/IA Series R2, SmartStruxure/Network 8000 or SmartStruxure/Signal?

Issue What is the part number & price for a SmartStruxure/Network 8000 driver or a SmartStruxure/Signal driver? Environment SmartStruxure Network 8000 Signal Cause Job estimating Resolution There is no Network 8000 driver or Signal as there is with I/A Series Niagara. The conversion process is performed at no cost when converting an I/A Series R2 database,  Network 8000 GCM or Signal to SmartStruxure via the "TAC I/A Series Conversions Projects" link on the iPortal2 web site.
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
915 Views

Unable retrieve objects from a third party device that has been added to Continuum.

Issue Continuum found and added both third party chiller controllers, RLE LD5200.  When a send to database is executed however, no objects are added to the Continuum database. Environment BACNet RLE LD5200 Cause Some BAS systems use a 16 bit identifier while Continuum uses 32 bits. Resolution Problem resolved updating the third party controller firmware..
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Andover Continuum
1035 Views

TAC License server can't be started

Issue TAC License server can't be started. TAC license server crashes Environment TAC Vista 5.1.8 Cause The license server can't start if there is a DEMO license in the same folder as the "real" license. Note that in 5.1.8 the default path to the license files have changed to: C:\Program Files\Schneider Electric\License Server\TacLic\Licenses Any license files that are in the old directory will be moved to the new one when upgrading. If you need to use DEMO licenses for a site you can add them to a separate directory and add that directory in the license setup.   Resolution Delete any DEMO licenses in: C:\Program Files\Schneider Electric\License Server\TacLic\Licenses Go to services and start TACLicenseServer  
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • TAC Vista
1465 Views

What causes "?_1" to be displayed in a Plain English program?

Issue When editing a PE program it displays "?_1" Environment Plain English Cause An object that the program is referencing has been deleted. If multiple objects have been deleted then the integer after the ?_ will increment. Resolution An object that the program is referencing has been deleted.  Recreate the missing object, enter it into the program and save the program.
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Andover Continuum
1300 Views

Schedule editor crashes with ACCDataServices error when creating a new or modifying an existing Schedule.

Issue Schedule editor crashes with ACCDataServices error when creating a new or modifying an existing Schedule. Environment Continuum v1.94 Schedule object Cause Known issue with Schedules when editing or creating exception events. The Schedule editor will crash with an error. Resolution CyberStation v1.94 SP1 has a fix in it that corrects the issue with the editor crashing when editing or creating a schedule with exceptions.
View full article
Picard Product_Support
‎2018-09-11 04:47 AM

Labels:
  • Andover Continuum
1454 Views

What modems are supported for Xenta 901 dial -up to TAC Vista?

Issue What modems are supported for Xenta 901 dial -up to TAC Vista? Environment TAC Vista TAC Xenta 901 Cause Want to use a dial-up to TAC Vista. The support for dial-up in TAC Vista is mainly for upgrading of older systems. We have not added any new modems to the list in many years Resolution These modems are supported Us Robotics,3Com 56k Sportster(V92) D-Link DFM-560E+ Siemens MC-35 (GSM modem) Siemens M-20 (GSM modem) SRT (GSM modem) Wawecom (GSM modem) SRT DIN 35 (Leased line) SRT DIN (Dial up)
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • TAC Vista
1145 Views
  • « Previous
    • 1
    • …
    • 465
    • 466
    • 467
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of