What are the expected voltages on the RS485 IO Module bus?
Andover Continuum
  • Netcontroller IO Modules
  • IOU Modules
Require typical values for troubleshooting first steps.
Although the IO Module bus uses RS485 comms similar to Infinet or BACnet MSTP, the typical bus voltages when measured with a voltmeter are usually lower.
Exact voltages will vary from system to system and depend on the amount of bus activity at the time, but the following will allow general troubleshooting:
  • Typical DC voltage measured across the bus + to - = 0.7 to 0.8VDC but working systems may read as low as 0.4VDC
  • Typical DC voltage measured Screen (shield) to + = 0.6 VDC
  • Typical DC voltage measured Screen (shield) to - = 1.3VDC
Note: If using Free Topology (FTT-10A) controller and modules, these use transformer bus coupling and will measure 0VDC across the bus.