Cannot get McQuay BACnet MSTP controller to come into the BACnet side
  • Cannot get McQuay BACnet MSTP controller to come into the BACnet side
  • BillNeville
    BillNeville
‎2018-09-06 10:22 AM
McQuay BACnet MSTP controller does not respond to the Who-Is request from CyberStation
MSTP bCX4040 McQuay
McQuay Tech Support has reported that the McQuay device has problems with Enhanced MSTP.
McQuay Tech Support has reported that the McQuay device has problems with Enhanced MSTP.  Once Enhanced MSTP was turned off the device was found and displayed on the BACnet side.