Sigma - Global communications, what happens to the controllers if the network fails?
  • Sigma - Global communications, what happens to the controllers if the network fails?
  • sesa139513
    sesa139513
  • Gary
    Gary
  • sesa125819
    sesa125819
‎2018-09-06 10:23 AM
What happens to Sigma globals if the network fails?
Globals
Communications
Networks
Site is to have a planned network shutdown, how will the Sigma controllers react to this?
The Sigma controller using the global update, will continue to operate normally, but will use the last value received, so any changes will not be responded to.
If the Sigma controller controls critical plant then the loss of global communications should be taken into account when programming.
  • Satchwell BAS & Sigma