Binding between the "Associated value" of a BACnet output point and the "Requested value" of the digital output value, does not work.
  • Binding between the "Associated value" of a BACnet output point and the "Requested value" of the digital output value, does n...
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
‎2018-09-06 10:24 AM
Bindings do not work.
Binding
BACnet Output
Digital Output
When the BACnet point changes in value, it does not change the value of the Digital output.
The StruxureWare Building Operation core architecture (as of version 1.3) allows cross server “read” references, but not cross server “write” references. This was the design from 1.0, and effects everyone – not just BACnet (ie. script programs would have the same behavior).
What this means for the BACnet associated value is that inputs (which are “read” references) can be done cross server, while outputs (which are “write” references) can be only be within a single server.