Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 426
    • 427
    • 428
    • …
    • 509
  • Next »

Try to create new ContinuumDB with Database Initialization and receive Database creation failed error stating the database does not exist.

Issue On attempted creation of new database receive the below errors. Database creation failed. Installation Error! <[Microsoft][ODBC SQL Server Driver][SQL Server]The database 'ContinuumDB' does not exist. Supply a valid database name. To see available databases, use sys.databases. > Installation Error! <[Microsoft][ODBC SQL Server Driver]Invalid cursor state> Installation Error! <[Microsoft][ODBC SQL Server Driver]Invalid cursor state> Environment Continuum Cyberstation Cause The "DB File Location" in the Database Initialization dialog is not specified properly. Resolution Check where the "Data" folder resides on the SQL server A typical SQL Express install will have this located at "C:\Program Files\Microsoft SQL Server\MSSQL.1\MSSQL\Data" but depending on the type of SQL, Operating System, and if any other instances of SQL - this location could be different. The correct folder contains at least six files:  master.mdf mastlog.ldf model.mdf modellog.ldf tempdb.mdf templog.ldf Type this path location into the "DB File Location" field Re-attempt the Database creation.  
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • Andover Continuum
1943 Views

"The Site Name" folder is missing when logging onto Xenta Server's webpage.

Issue When logging onto Xenta Server's webpage (Xenta 701 and Xenta 721), "The Site Name" folder is missing. Xenta 701 and Xenta 721 cannot display a Value Page though the page has been created in the Xbuilder project. Environment Xenta 701, Xenta 721 XBuilder 5.1.X TAC Vista Workstation 5.1.X Cause Though Xbuilder allows the user to create a Value Page, it will not be displayed on the website. Xenta 701 and Xenta 721 only has "Service" level support of web services, therefore any web content ability is disabled. NOTE: Xenta 913 also only has "Service" level web services. However, Xenta 913 is a gateway; therefore, the Value Page feature is enabled in Xenta 913.  Resolution User can use other Xenta servers such as Xenta 731 or Xenta 913 to have Value Page feature. Or, viewing points values on TAC Vista Workstation.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • TAC Vista
1073 Views

Device Editor Modbus Data Type Define in a Xenta 5/7/9xx

Issue Vista Workstation displays a data point as a signed integer data type that reads from a modbus device, but the modbus point is defined as unsigned integer data type in Device Editor. When a modbus point's raw value is greater than 32768, Vista Workstation displays a negative value. Environment Xenta Servers Ver 5.1.4 or previous Xenta 511, 527, 555, 701, 711, 721, 731, 913 Device Editor Cause Xenta Servers will read Modbus data as 16-bit signed data, whether the modbus point is defined as 16bit SIGNED or 16bit UNSIGNED in the Device Template. Resolution Upgrade Xenta Servers firmware to 5.1.5 or above; Upgrade Vista software environment to 5.1.5 or above. include  Vista Server, Xbuilder, Device Template, Menta
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • TAC Vista
1542 Views

How to integrate an Xenta 913 in Vista?

Issue How do integrate an Xenta 913 in Vista? Do I need to give an IP address as well as a Neuron ID to integrate an Xenta 913 in Vista? Environment Vista 5.1.X Xenta Server 913 (applies to other models) Cause There may be some confusion as to whether an Xenta 913 is considered a LON device or IP gateway in Vista. Resolution If the device is being used as a Modbus\M-bus\C-bus\BACnet client only the IP address is required. In Vista workstation, right-click on the Server object and select New\Device\Xenta Server 913. Give the device a suitable name. Right-click on the device and select Properties. Set the IP address for the device. Right-click on the device and select edit. Configure the device in TAC XBuilder.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • TAC Vista
1540 Views

How to rescue a corrupt Menta file

Issue Menta file Simulates (F12) and Generates OK and even downloads from Vista apparently OK, but monitored values shown the message 'Failed to read signal'. Connecting to the controller with the serial lead and entering online simulation mode gives a 'PARSER ERROR'. The Memory Usage stats show less free space than would be expected for a file of this complexity. Environment Vista Menta Xenta Cause The Menta file has some corruption that is not visible when viewing the Functional Block Diagram. Resolution Some files may be rescued by copying the FBD into a new empty Menta file: Create a new empty Menta file with the same Device and Program Specifications as the corrupted file. Open the corrupted file in a second instance of Menta. Drag a selection box around the entire visible FBD and enter Ctrl+C to copy. Switch to the new Menta file and enter Ctrl+V to paste the FBD. Please note that this procedure will copy references to named constants across to the new file, but it will not copy the constant definitions. Selecting F12 will highlight the function blocks containing the references to the missing constant definitions.  Edit the block and press 'OK'.  A dialog box will pop up for each constant where you can fill in the value, unit and public parameters.  Repeat this procedure by selecting F12 until Menta enters simulation mode without errors.  You will also need to create the OP tree and any trend logs from scratch. If you are lucky, the new file will download and run without errors.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • TAC Vista
1741 Views

Butterfly valve VF208 with lugged flanges

Issue In our portfolio we currently only list VF208 series valves with elongated wafer type eyelets  Environment VF208L VF208W Cause Applications sometimes requires a valve with lugs instead. Resolution VF208 valves with lugged flanges are available on request. Please contact Product Management or Order Entry for information on ordering this option. The Specification sheet can be downloaded here.
View full article
Picard Product_Support
‎2018-09-10 07:49 AM

Labels:
  • Field Devices
1178 Views

Data not showing up in Seven Reports.

Issue Data not showing up in the consumption report. Environment All versions of I/Net. Cause The points that are trending data are not matching up with the new host, therefore it is not collecting any data. Resolution After restoring the database, open up the trends editor and create or match the trends on the new Host PC.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • TAC INET
1116 Views

Changing the IP Address in Cyberstation

Issue Site needs to change the IP address in Cyberstation Environment Continuum Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause There is a need to be able to change the IP address in Cyberstation Resolution Shut down Cyberstation Go to the PC's network/LAN/TCPIP connection properties and enter the new static IP address Verify the IP address change by going to Start>Run>Cmd (DOS Prompt) and type Ipconfig/all. The IP address will show under the network card similar to the following: Description . . . . . . . . . . . : Intel(R) 82577LM Gigabit Network Connection Dhcp Enabled. . . . . . . . . . . : No Physical Address. . . . . . . . . : 5C-26-0A-45-7C-D8 Autoconfiguration Enabled . . . . : No IP Address. . . . . . . . . . . . : 192.168.203.2 Subnet Mask . . . . . . . . . . . : 255.255.255.128 Default Gateway . . . . . . . . . : 192.168.203.1   Launch Cyberstation Open the Workstation object using Continuum Explorer (Right click>Edit) Click on the "Teach" button (Distributes the New IP address to the controllers)
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • Andover Continuum
1682 Views

Objects with a "." character at the end of the object name will not bind to other objects.

Issue Cannot bind an input with the name Intern.Temp. Environment StruxureWare Building Operation Binding Point Naming Cause While a "." may be used as a separating character within a point name, it is an illegal object name character when it appears as the last character. StruxureWare Building Operation will generate an Illegal Character error when you attempt to name an object with a trailing "." character. Resolution Rename the object without a "." at the end of the name string and rebind it to the object.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • EcoStruxure Building Operation
844 Views

Vista adding the user group "domain admin" to the administrator group.

Issue When running Vista in high security level Vista will add the NT group "Domain admin" as a user group in Vista at startup. Is it possible to avoid this? Environment Vista 5.1.7 Cause When running Vista in high security level Vista will add all users in the computers administrator group as users in Vista at the startup of the Vista server . This is not possible to prevent.  Resolution Either run Vista in low security level or take away the "Domain admin" group from the administrator group on the computer.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • TAC Vista
1188 Views

SHD100: Using 24V AC power supply and 4-20mA output signal

Issue The data sheet only lists AC power supply as an option when using the 0-10V output signal Environment SHD100 006902320 SHD100-T 006902330 Cause Sensor configuration options. Resolution For a transmitter the operating (normal) current is at once the measuring signal. If a rectified output is requested this means that DC voltage as supply voltage is required.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Field Devices
1407 Views

Xenta Server firmware installation takes several minutes before it starts up or never starts

Issue Xenta Server firmware installation takes several minutes before it starts up When launching an installation of the Xenta Server system software it takes several minutes before it starts Environment Xenta 7XX Xenta 5XX Xenta 9XX Cause This rare issue has been seen on some PCs with a huge amount of files in the Windows/temp folder. It could be various other programs conflicting, in one case it has been the process setpoint.exe that was conflicting. Resolution Delete all files in the users temp folder. Here is a sample of the path: "C:\Documents and Settings\user_name\Local Settings\temp" or "C:\Users\user_name\AppData\Local\Temp". Easiest way to access the temp folder is by entering %temp% in the path in explorer. If  setpoint.exe (Logitech) or KiesAirMessage.exe (Samsung) is an active process in task manager, end the process. It has also been seen that the process net.exe is blocking the installer. If the above steps does not work, try stopping that process.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • TAC Vista
1387 Views

Replacing M15C on brand X butterfly valve

Issue Since the M5/M15 series actuator is no longer available, a replacement actuator is requested.  Environment M15 M9B TRV mounting kit 8600991000 Cause Replacing obsolete actuator. Resolution M9B together with the TRV mounting kit should work.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Field Devices
1045 Views

Network security and SNMP

Issue Are SNMP communication packets affected by controller's network encryption? Environment CX9680 ACX5720 ACX5740 Cause Documentation Resolution Enabling network encryption does not have any effect on SNMP communications.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Andover Continuum
1456 Views

When tunnel through a UNC using an HTTP port other than 80 the Ax Serial Tunnel will not connect and locks up.

Issue When tunnel through a UNC using an HTTP port other than 80 the Ax Serial Tunnel will not connect and locks up. Environment R2, G3 I/A Series tunneling Cause Including the port number after the IP address when entering the Host address in the Ax serial tunnel window will cause it to lock up trying to connect with the port entered. Resolution Do not include the port number after the IP address when entering the Host address in the Ax serial tunnel window.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • TAC IA Series
885 Views

Encountered the error 'Start service: SnmpService [1272] SnmpService SnmpReceive: unable ... Address already in use: Cannot bind

Issue Encountered the following error when running the SNMP service: Start service: SnmpService [1272] SnmpService SnmpReceive: unable to create socketjava.net.BindException: Address already in use: Cannot bind Environment I/A Series R2 SNMP driver Windows Server 2008 Cause The SNMP ports are being used by another application / process. In this particular case, the SNMP Service (which is available in Windows Server 2008) has been enabled. Resolution The I/A Series R2 default ports for SNMP are 161 (receive SNMP requests) and 162 (receive SNMP trap messages). Check if the SNMP Service in Windows Server 2008 is enabled. If it is enabled and not in use: Disable it by stopping the service and setting it to 'Manual' so that it does not start whenever the computer reboot and starts. Uninstall it using Windows 'Add or Remove Programs'   Alternatively, you can change the SNMP ports in I/A Series R2. To do this,  in your station, go to the SnmpService properties, 'General' > 'Config' tab.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • TAC IA Series
1120 Views

How to automatically disable access for Personnel who's expiry date has passed?

Issue How to automatically disable access for Personnel who's expiry date has passed? Environment Continuum Access Control Cause Want to automatically disable Personnel who's cards have gone beyond the expiry date. Resolution The below code sample can be used as a basis to provide this feature. It is a fallthru Workstation Program that can be triggered from one of the time related SystemVariables such as Hour or Minute. It uses the OpenList function to go through all Personnel in a specific folder and compare their expiry dates to the current Date and then disables them if required.   ========================================== 'Fall thru program that will search through the Personnel class for ' an expiration date that is less than today’s date. Object oAPerson Numeric nResult Line 1   nResult = OpenList("Personnel", oAPerson, Root\CardHolders) 'specify CH path Line 2   If nResult = Success then     While GetObject(oAPerson) = Success       'The next line will fail when the Expiration Date attribute is greater than 12/31/2037 (12/31/2099, by default)       If (Date > oAPerson ExpirationDate) then         Set oAPerson State = Disabled       Else         Set oAPerson State = Enabled       Endif     Print oAPerson Name, " is ", oAPerson State 'prints to message window for testing     Endwhile   Endif ==========================================
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Andover Continuum
1545 Views

Pelco Control Point Software cannot run on the same PC as I/NET Seven Software

Issue Can Pelco's Control Point Software run on the same PC as I/NET Seven Software? Product Line Pelco, TAC INET Environment All Windows OS I/NET Seven Software Pelco Control Point Software Cause The two software packages are not compatible with each other. Resolution Pelco's client software cannot be installed on the same PC that is running TAC I/NET Seven. See TCON 301 - Chapter 6.
View full article
Picard Product_Support
‎2018-09-10 11:02 PM

Labels:
  • CCTV
  • TAC INET
1283 Views

On a Windows 7 PC, when right-clicking on an object, both its "override" and "set" pop-up boxes do not fully open in Niagara G3 versions 3.5.x and older.

Issue An object’s override and set pop-up boxes do not fully open in Niagara G3. You have to grab and pull the corner of the pop-up to open it completely. Niagara version 3.5.x is installed on a Windows 7 PC. Environment Niagara G3 Version 3.5.x and older Cause Versions of WorkBench prior to 3.6.31 have not been officially certified with Windows 7. Resolution The issue is more of a nuisance, but does not affect functionality in any way. There are a couple of options you can try to try and correct the issue. The first option is to try to reduce the font size in Windows 7. - Click on the Start button and open the Control Panel - Open the Fonts folder and select Change font size. - Select smaller fro the font size and click apply The other option is to change the screen resolution slightly. Note: Since Niagara versions prior to 3.6.31 have not been certified for the Windows 7 operating environment, the above my not correct the issue.  
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • TAC IA Series
1209 Views

LinePrinterRecipient 'Load Printer List' does not bring up a list of the available printers

Issue LinePrinterRecipient 'Load Printer List' does not bring up a list of the available printers Environment I/A Series G3 Enterprise Network Server (ENS) or Enterprise Network Controller (ENC). Cause At this stage the reason that this occurs is unknown but the following resolution is the current workaround. Resolution Since you are not able to find the printer using the 'Load Printer List' button, you should just type in the name of the printer in the LinePrinter Recipient's properties 'Printer' field. To make sure you get the name correct, go to Windows Control Panel and go to 'Printers and Faxes'. Find the line printer and right-click on it to the properties. Copy the name of the printer. Go to Workbench and paste the name of the printer in the LinePrinter Recipient as per described above.  
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • TAC IA Series
1445 Views
  • « Previous
    • 1
    • …
    • 426
    • 427
    • 428
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of