Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to rescue a corrupt Menta file

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to rescue a corrupt Menta file
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1743 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to rescue a corrupt Menta file

Picard Product_Support
‎2018-09-06 12:19 PM

Issue

Menta file Simulates (F12) and Generates OK and even downloads from Vista apparently OK, but monitored values shown the message 'Failed to read signal'.

Connecting to the controller with the serial lead and entering online simulation mode gives a 'PARSER ERROR'.

The Memory Usage stats show less free space than would be expected for a file of this complexity.

Environment

Vista

Menta

Xenta

Cause

The Menta file has some corruption that is not visible when viewing the Functional Block Diagram.

Resolution

Some files may be rescued by copying the FBD into a new empty Menta file:

  1. Create a new empty Menta file with the same Device and Program Specifications as the corrupted file.
  2. Open the corrupted file in a second instance of Menta.
  3. Drag a selection box around the entire visible FBD and enter Ctrl+C to copy.
  4. Switch to the new Menta file and enter Ctrl+V to paste the FBD.

Please note that this procedure will copy references to named constants across to the new file, but it will not copy the constant definitions. Selecting F12 will highlight the function blocks containing the references to the missing constant definitions.  Edit the block and press 'OK'.  A dialog box will pop up for each constant where you can fill in the value, unit and public parameters.  Repeat this procedure by selecting F12 until Menta enters simulation mode without errors.  You will also need to create the OP tree and any trend logs from scratch.

If you are lucky, the new file will download and run without errors.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7996
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of