How to automatically disable access for Personnel who's expiry date has passed?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to automatically disable access for Personnel who's expiry date has passed?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1546 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to automatically disable access for Personnel who's expiry date has passed?

Picard Product_Support
‎2018-09-06 12:18 PM

Issue

How to automatically disable access for Personnel who's expiry date has passed?

Environment

Continuum Access Control

Cause

Want to automatically disable Personnel who's cards have gone beyond the expiry date.

Resolution

The below code sample can be used as a basis to provide this feature.

It is a fallthru Workstation Program that can be triggered from one of the time related SystemVariables such as Hour or Minute.

It uses the OpenList function to go through all Personnel in a specific folder and compare their expiry dates to the current Date and then disables them if required.

 

==========================================

'Fall thru program that will search through the Personnel class for
' an expiration date that is less than today’s date.

Object oAPerson
Numeric nResult

Line 1
  nResult = OpenList("Personnel", oAPerson, Root\CardHolders) 'specify CH path

Line 2
  If nResult = Success then
    While GetObject(oAPerson) = Success
      'The next line will fail when the Expiration Date attribute is greater than 12/31/2037 (12/31/2099, by default)
      If (Date > oAPerson ExpirationDate) then
        Set oAPerson State = Disabled
      Else
        Set oAPerson State = Enabled
      Endif

    Print oAPerson Name, " is ", oAPerson State 'prints to message window for testing

    Endwhile

  Endif

==========================================

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 8016
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of